This was on an inspection today and I could use help explaining it. Specifically, service to a shed is tapped from the 2 lugs at the top of this panel. From the top of the panel the wires go through a mast head, then 15 feet to the shed where they go into the shed via another masthead.
The main disconnect is a 125 amp breaker at the top right. There was also a 50 amp breaker labeled shed and those wires go into the house with all of the other wires. In the report I stated that the shed was serviced directly from the lugs without passing through a circuit breaker and recommended further evaluation by a licensed electrician.
Any thoughts would be appreciated. I explained this to the client, told her I’d never seen this before and that I might have to revise and send another report tomorrow.
That narrative is fine. There can be an overcurrent breaker at either end, depending on specific rules. I believe it is only allowed on the shed end if the conductors are underground, but protected inside conduit may be ok as well..(not sure)
But either way, your narrative is sufficient. And, good catch!
not necessarily. I know with service feeders, they are allowed to travel from the meter to the service panel without protection, as long as they are underground. Not sure if that also applies to a detached structure.
There’s generally nothing wrong with the installation provided the conductors terminate at an overcurrent protective device at the remote end. Some jurisdictions do not allow overhead feeders to remote buildings, so you should verify that overhead feeders are permitted in your area.
They are protected. The conductors terminate in an overcurrent protective device. The current is the same at any point in a closed loop so the conductors are protected regardless of where the overcurrent protection is placed.
The white and black conductors going into the lugs at the top are the ones that didn’t make sense to me but I was hoping to get your take on it. I’ll likely be delayed in responding though, I’m getting ready to leave for work soon.
I agree with Richard here, (Both are marked “White” as Neutrals) I think one of those Neutrals (taped white is my guess) are from another source To this panel and possibly the other going to the shed. And then load to the shed is probably from one of the breakers (my guess would be the Red and Black conductors from the GE 240V breaker on the left, along with a bare ground and The White conductor…All exiting at the Top. What I would probably be mentioning (reporting) is the Backfed Breaker supplying power to this panel without a hold down clip or screw on the right, along with the relatively new, clean looking panel with what looks to be a mismatch of Old breakers (I count at least 4 different brands) ….That I’m guessing came out of Red Green’s personal stash he keeps in the back of the Opossum Van.