I’m studying for the National Home Inspector exam and came across a test prep question: “Should a breaker be in sight of a 240v appliance?” with the answer being “ a breaker not in sight of the appliance.” I rarely see 240v appliance (dryer, electric oven) with a breaker in sight. Can someone please help explain this rule?
Sure. The question is asking about the required disconnecting means for the appliance so that it can be denergized for servicing. If the appliance has a cord and plug that can be serve as the disconnecting means. If the appliance is hard wired then the disconnecting means can be a circuit breaker in the panel if it’s within sight of the appliance and within 50’. There are other options such as a local disconnecting means adjacent to the appliance or breaker lockouts depending on the appliance type.
Correct. Remember that the code requirement is for the appliance to have a means of disconnect so that it can be worked on in a de-energized state. There are several code compliant ways to accomplish this requirement. A cord and plug is one means of disconnect. A circuit breaker within sight of the appliance is another. So either would meet the requirement.
For electric ranges there is also a requirement for the cord and plug disconnecting means to be accessible by removing the bottom drawer of the range. If the cord and plug is not accessible by removing the drawer then it does not qualify as a means of disconnect.