# Shouldn't these floor joists be supported on the foundation?

**URL:** <https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447>\
**Category:** Structural Inspections\
**Created:** [March 2, 2026, 4:50pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447 "2026-03-02T16:50:23Z")\
**Posts on this page:** 18\
**Page:** 1

<div class="post-metadata">

**Author:** ![jgriffith11](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgriffith11/32/416805_2.png) [@jgriffith11](https://forum.nachi.org/u/jgriffith11)\
**Post date:** [March 2, 2026, 4:50pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/1 "2026-03-02T16:50:23Z")

</div>

I came across this design in a new build. It appears that the beam is the load bearing member for the floor joists and that the beam is only supported by nailing into a wood post between the block foundation (picture 2). Can’t be sure that the joists aren’t additionally resting on the sill plate and block with all of the spray foam, but not thinking so. I’m not comfortable telling my client that the support is sufficient. Thoughts?

 ![IMG_5185](https://global.discourse-cdn.com/internachi/original/4X/0/c/b/0cba20d7ceef96b0e32eff59623188ad8a4af699.jpeg)

Thoughts?

 ![IMG_5183](https://global.discourse-cdn.com/internachi/original/4X/d/9/5/d95cd1e8fb6f22002c3cddf18382f5a381206bc1.jpeg)

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [March 2, 2026, 5:13pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/2 "2026-03-02T17:13:40Z")

</div>

> [@jgriffith11](#):
>
> I’m not comfortable telling my client that the support is sufficient. Thoughts?

Then don’t!  
Do you also report other systems that are performing as intended?  
FYI… I don’t see any issue from here in Minnesota.

---

<div class="post-metadata">

**Author:** ![spatterson5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/spatterson5/32/195461_2.png) [@spatterson5](https://forum.nachi.org/u/spatterson5)\
**Post date:** [March 2, 2026, 5:17pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/3 "2026-03-02T17:17:01Z")

</div>

Just report what you can see. When we come across foundations that have spray foam and we can’t see much, we report as such and instruct our client to gain assurance from the builder/owner that X is installed properly.

FYI, chances are those joists are partly on the sill plate, and the beam/ledger was added for additional support. But, we do not know this…. So do not put that in the report!

---

<div class="post-metadata">

**Author:** ![jgriffith11](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgriffith11/32/416805_2.png) [@jgriffith11](https://forum.nachi.org/u/jgriffith11)\
**Post date:** [March 2, 2026, 5:32pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/4 "2026-03-02T17:32:40Z")

</div>

Thanks Scott. I hope you are correct that the beam is acting as additional support. I did disclaim what I couldn’t see in my report as follows. “The condition of the foundation was not visible from the exterior due to high soil conditions or from under the crawlspace because of the foam insulation and could not be properly assessed.” The appraiser has requested an additional letter describing the type of foundation and determining whether it is adequate. I’ll refer my client to the builder to ensure it was proper installed. Appreciate your help!

---

<div class="post-metadata">

**Author:** ![mdurante](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mdurante/32/289617_2.png) [@mdurante](https://forum.nachi.org/u/mdurante)\
**Post date:** [March 2, 2026, 8:22pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/5 "2026-03-02T20:22:28Z")

</div>

> [@jgriffith11](#):
>
> Thoughts?

Must have been amateur hour when the spray foam guys were there…. Yikes….

As far as the floor structure is concerned, you cannot report on what you cannot see….

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 2, 2026, 10:41pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/6 "2026-03-02T22:41:30Z")

</div>

> [@jgriffith11](#):
>
> Can’t be sure that the joists aren’t additionally resting on the sill plate and block with all of the spray foam, but not thinking so. I’m not comfortable telling my client that the support is sufficient. Thoughts?

> [@jjonas](#):
>
> FYI… I don’t see any issue from here in Minnesota.

Agree.

I used to carry a knitting needle for spay foam stuff… checking thickness, things like this bearing issue too. YMMV

P.S. Is that white wood against the blocks?

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [March 2, 2026, 11:16pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/7 "2026-03-02T23:16:38Z")

</div>

> [@jgriffith11](#):
>
> I came across this design in a new build. It appears that the beam is the load bearing member for the floor joists and that the beam is only supported by nailing into a wood post between the block foundation (picture 2).

Load Bearing is 1.5". The structural lumber thickness, being ~x 8" is at least that 1.5" inches required.  
Span is another equation.  
Did the floor dip or sag in the centers?

---

<div class="post-metadata">

**Author:** ![mgratton](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgratton/32/58251_2.png) [@mgratton](https://forum.nachi.org/u/mgratton)\
**Post date:** [March 3, 2026, 12:08am UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/8 "2026-03-03T00:08:45Z")

</div>

How high was the soil against the foundation, higher than the top of foundation?

---

<div class="post-metadata">

**Author:** ![jgriffith11](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgriffith11/32/416805_2.png) [@jgriffith11](https://forum.nachi.org/u/jgriffith11)\
**Post date:** [March 3, 2026, 12:16am UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/9 "2026-03-03T00:16:46Z")

</div>

Best I could tell, it’s block foundation all around with exception to wood posts where the supports meet. Guessing the floor joists are abutting the rim joist and not block?

---

<div class="post-metadata">

**Author:** ![mdurante](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mdurante/32/289617_2.png) [@mdurante](https://forum.nachi.org/u/mdurante)\
**Post date:** [March 3, 2026, 12:21am UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/10 "2026-03-03T00:21:26Z")

</div>

BTW @jgriffith11 fill out your signature on your profile so we all know where you are located.

> [@NEW MEMBERS, Filling Out Your Profile & Signature](https://forum.nachi.org/t/new-members-filling-out-your-profile-signature/265380):
>
> If you are new to this MB, I’d like to say WELCOME. Visit often. There is a ton of great information in here to help new and seasoned inspectors learn and share, so there’s no lack of reading material. Remember, the only stupid questions are the ones that aren’t asked, especially when starting out. Use the “Search” function on the header if you can’t find specific info that you may be looking for. Since it gets repeated regularly in this MB, I thought I’d just put up a thread that everyone can …

---

<div class="post-metadata">

**Author:** ![jgriffith11](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgriffith11/32/416805_2.png) [@jgriffith11](https://forum.nachi.org/u/jgriffith11)\
**Post date:** [March 3, 2026, 12:34am UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/11 "2026-03-03T00:34:53Z")

</div>

no sag observed. Other than the obvious lack of ventilation, a couple of small leaks in the supply and drain lines observed, and the need to install a vapor retarder, the crawlspace looked pretty good. Surprisingly, no mildew or moisture on the boards.

---

<div class="post-metadata">

**Author:** ![jgriffith11](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgriffith11/32/416805_2.png) [@jgriffith11](https://forum.nachi.org/u/jgriffith11)\
**Post date:** [March 3, 2026, 12:41am UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/12 "2026-03-03T00:41:06Z")

</div>

The soil was up to the sill plate pretty well all around the perimeter of the house. I showed that to my client and called it out in the report. Definitely a WDO and moisture issue as it is. The crawlspace is actually subsurface on 3 sides from what I can tell. The exception is on the garage side where the access is.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 3, 2026, 12:52am UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/13 "2026-03-03T00:52:26Z")

</div>

> [@lkage](#):
>
> P.S. Is that white wood against the blocks?

> [@jgriffith11](#):
>
> Best I could tell, it’s block foundation all around with exception to wood posts where the supports meet. Guessing the floor joists are abutting the rim joist and not block?.

So, was it white wood against the block wall, then? …instead of treated?

---

<div class="post-metadata">

**Author:** ![jgriffith11](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgriffith11/32/416805_2.png) [@jgriffith11](https://forum.nachi.org/u/jgriffith11)\
**Post date:** [March 3, 2026, 1:21am UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/14 "2026-03-03T01:21:57Z")

</div>

Yes, didn’t appear to be pressure treated.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 3, 2026, 1:26am UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/15 "2026-03-03T01:26:04Z")

</div>

> [@lkage](#):
>
> So, was it white wood against the block wall, then? …instead of treated?.

> [@jgriffith11](#):
>
> The soil was up to the sill plate pretty well all around the perimeter of the house

> [@jgriffith11](#):
>
> Yes, didn’t appear to be pressure treated

Uh, oh.

…

…

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [March 3, 2026, 2:35am UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/16 "2026-03-03T02:35:57Z")

</div>

> [@jgriffith11](#):
>
> no sag observed. Other than the obvious lack of ventilation

No conditioning?

---

<div class="post-metadata">

**Author:** ![jgriffith11](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgriffith11/32/416805_2.png) [@jgriffith11](https://forum.nachi.org/u/jgriffith11)\
**Post date:** [March 3, 2026, 4:23pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/17 "2026-03-03T16:23:05Z")

</div>

No. No natural ventilation of any sort or space conditioning. The current owner bought the place with the foundation already constructed and had the home built. I’m guessing that the spray foam was a poor attempt to compensate for lack of ventilation/conditioning.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [March 3, 2026, 4:34pm UTC](https://forum.nachi.org/t/shouldnt-these-floor-joists-be-supported-on-the-foundation/265447/18 "2026-03-03T16:34:53Z")

</div>

> [@jgriffith11](#):
>
> I’m guessing that the spray foam was a poor attempt to compensate for lack of ventilation/conditioning.

Maybe. Spray foam, encapsulation, or any other barrier, for that matter, would not compensate for the lack of ventilation or conditioning.

> [@jgriffith11](#):
>
> Best I could tell, it’s block foundation all around with exception to wood posts where the supports meet.

The difficulty here is determining the load-bearing components. Could be wood, could be block, could be a combination. Some homes have pier support, and the block wall around the perimeter is nothing more than a skirt.

I would definitely call out the lack of ventilation. Anything else is likely speculation.
