# Single or duplex outlet

**URL:** <https://forum.nachi.org/t/single-or-duplex-outlet/159933>\
**Category:** Electrical Inspections\
**Created:** [January 11, 2020, 2:15pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933 "2020-01-11T14:15:32Z")\
**Posts on this page:** 20\
**Page:** 2

<div class="post-metadata">

**Author:** ![ggilbert](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ggilbert/32/184784_2.png) [@ggilbert](https://forum.nachi.org/u/ggilbert)\
**Post date:** [January 11, 2020, 9:43pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/23 "2020-01-11T21:43:20Z")

</div>

Correct, I fallowed the12 gauge wire back to the panel and it had no other junction boxes. 20ft of wire from electrical box to breaker.

---

<div class="post-metadata">

**Author:** ![ggilbert](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ggilbert/32/184784_2.png) [@ggilbert](https://forum.nachi.org/u/ggilbert)\
**Post date:** [January 11, 2020, 9:46pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/24 "2020-01-11T21:46:34Z")

</div>

You are right because I can’t center the outlet and drill a hole in a blank cover plate because I will not have the screw in points for the outlet on the the electrical box

---

<div class="post-metadata">

**Author:** ![rweed2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rweed2/32/180964_2.png) [@rweed2](https://forum.nachi.org/u/rweed2)\
**Post date:** [January 11, 2020, 9:49pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/25 "2020-01-11T21:49:03Z")

</div>

K, if you abandon the rest in line, dedicated it is. You could also buy a split duplex receptacle, power one side fill the box with another duplex dummy (not connected) kinda backwoods but so is modifying a cover plate.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [January 11, 2020, 11:22pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/26 "2020-01-11T23:22:56Z")

</div>

> [@dwigger](#):
>
> Or, simply tell her that tanning beds cause skin cancer and shouldn’t be used. 😃

I vote best answer.

---

<div class="post-metadata">

**Author:** ![lmorrison](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lmorrison/32/58376_2.png) [@lmorrison](https://forum.nachi.org/u/lmorrison)\
**Post date:** [January 12, 2020, 3:19pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/27 "2020-01-12T15:19:20Z")

</div>

And they are in Stock…[https://www.kyleswitchplates.com/combo-duplex-outlet-single-1-62-20a-round-receptacle-cover-plate/](https://www.kyleswitchplates.com/combo-duplex-outlet-single-1-62-20a-round-receptacle-cover-plate/) If you have seperate circuits, one for the duplex and another for the single, this would be the way to go and still have use of the duplex receptacle. ![image](https://global.discourse-cdn.com/internachi/original/3X/f/b/fb37dd6b98565d2173fdcf4da3ce83fc4327ff6d.png)

---

<div class="post-metadata">

**Author:** ![jdepiero](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jdepiero/32/356888_2.png) [@jdepiero](https://forum.nachi.org/u/jdepiero)\
**Post date:** [January 12, 2020, 4:51pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/28 "2020-01-12T16:51:10Z")

</div>

Good source to know about. Thanks for posting Larry.

---

<div class="post-metadata">

**Author:** ![ggilbert](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ggilbert/32/184784_2.png) [@ggilbert](https://forum.nachi.org/u/ggilbert)\
**Post date:** [January 12, 2020, 6:53pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/29 "2020-01-12T18:53:33Z")

</div>

Yes, definitely. Good find Larry

---

<div class="post-metadata">

**Author:** ![mcyr](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mcyr/32/173319_2.png) [@mcyr](https://forum.nachi.org/u/mcyr)\
**Post date:** [January 12, 2020, 7:32pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/30 "2020-01-12T19:32:25Z")

</div>

What is wrong with a single gang plate?  
[https://www.amazon.com/Leviton-84004-40-1-406-Inch-Receptacle-Wallplate/dp/B000FKDMDM/ref=pd\_cp\_60\_4/137-9998017-1167435?\_encoding=UTF8&pd\_rd\_i=B000FKDMDM&pd\_rd\_r=bc3be738-8e2c-4b96-97f2-035bef2837c7&pd\_rd\_w=TJoMS&pd\_rd\_wg=3PqdG&pf\_rd\_p=d534d65f-a237-49e4-9070-a58a3a6b8ba4&pf\_rd\_r=C4STXMNNVETX2M1M76HE&psc=1&refRID=C4STXMNNVETX2M1M76HE](https://www.amazon.com/Leviton-84004-40-1-406-Inch-Receptacle-Wallplate/dp/B000FKDMDM/ref=pd_cp_60_4/137-9998017-1167435?tag=nachi02-20)

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [January 12, 2020, 7:38pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/31 "2020-01-12T19:38:44Z")

</div>

> [@mcyr](#):
>
> What is wrong with a single gang plate?

Greg has a 2-gang box in the wall, from what I understand.

---

<div class="post-metadata">

**Author:** ![mcyr](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mcyr/32/173319_2.png) [@mcyr](https://forum.nachi.org/u/mcyr)\
**Post date:** [January 12, 2020, 8:25pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/32 "2020-01-12T20:25:54Z")

</div>

I thought it was the other way around. Then what Larry M. posted would be the way to go.

---

<div class="post-metadata">

**Author:** ![ggilbert](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ggilbert/32/184784_2.png) [@ggilbert](https://forum.nachi.org/u/ggilbert)\
**Post date:** [January 12, 2020, 9:14pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/33 "2020-01-12T21:14:56Z")

</div>

I appreciate the guidance from everyone, very helpful.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [January 12, 2020, 11:50pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/34 "2020-01-12T23:50:47Z")

</div>

> [@mcyr](#):
>
> …what Larry M. posted would be the way to go.

Yup, that would be the way to go, if he leaves the duplex receptacle dead.

Otherwise, what Rob posted is for the real dedicated circuit, with what Greg has existing:

 ![image](https://global.discourse-cdn.com/internachi/original/3X/a/7/a7e9c103c184a07b70448f086db356a9a09bd10d.jpeg)

---

<div class="post-metadata">

**Author:** ![ggilbert](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ggilbert/32/184784_2.png) [@ggilbert](https://forum.nachi.org/u/ggilbert)\
**Post date:** [January 13, 2020, 1:53am UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/35 "2020-01-13T01:53:32Z")

</div>

You are correct! What Rob posted is actually what I need, the picture Larry posted could be used but only if I leave the outlet dead! That is correct thank you

---

<div class="post-metadata">

**Author:** ![cevans](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/cevans/32/244194_2.png) [@cevans](https://forum.nachi.org/u/cevans)\
**Post date:** [January 13, 2020, 2:15am UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/36 "2020-01-13T02:15:16Z")

</div>

Remember that if you are using an existing circuit, you would need to disconnect all of the upstream and downstream receptacles to meet the manufacturer’s requirement of a dedicated receptacle. This could leave a lot of non-functional receptacles leftover from the old circuit depending on how many receptacles currently share the circuit.

---

<div class="post-metadata">

**Author:** ![ggilbert](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ggilbert/32/184784_2.png) [@ggilbert](https://forum.nachi.org/u/ggilbert)\
**Post date:** [January 13, 2020, 11:33am UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/37 "2020-01-13T11:33:38Z")

</div>

Yes you are right, This box I am working on is all that came off of the circuit breaker. I fallowed the wire from the breaker to the electrical box and there were no other junction boxes and the wire dead ends into the box I am going to install the 20 amp receptacle. It is weird that it was the only outlet coming off of this breaker, but that was the case.

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [January 19, 2020, 11:42pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/38 "2020-01-19T23:42:30Z")

</div>

Do not know how you followed a cable in a wall assembly but so be it.  
It, the circuit, would be traced to first point of termination upstream.  
Manufacturers requires a dedicated circuit and disconnect. Tanning bed.  
Long string for this type of question.

---

<div class="post-metadata">

**Author:** ![ggilbert](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ggilbert/32/184784_2.png) [@ggilbert](https://forum.nachi.org/u/ggilbert)\
**Post date:** [January 20, 2020, 12:00am UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/39 "2020-01-20T00:00:17Z")

</div>

I fallowed the wire down a floor joist then it dropped into a hallow core of cinder block, it was actually very simple to fallow, yes I got lucky with this one

---

<div class="post-metadata">

**Author:** ![jmontgomery9](https://avatars.discourse-cdn.com/v4/letter/j/77aa72/32.png) [@jmontgomery9](https://forum.nachi.org/u/jmontgomery9)\
**Post date:** [January 21, 2020, 3:25am UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/40 "2020-01-21T03:25:11Z")

</div>

Yeah you’ll need a Double gang and a single receptacle plate.

---

<div class="post-metadata">

**Author:** ![mparks2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks2/32/172915_2.png) [@mparks2](https://forum.nachi.org/u/mparks2)\
**Post date:** [January 25, 2020, 11:32pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/41 "2020-01-25T23:32:44Z")

</div>

> [@rmeier2](#):
>
> All of these would be code compliant for a 20 amp branch circuit:  
> 20 amp circuit with a single 20 amp receptacle.  
> 20 amp circuit with a 20 amp duplex receptacle.  
> 20 amp circuit with a 15 amp duplex receptacle.

Assuming an individual branch circuit.

You can install a single 15 on:  
Branch Circuit, General-Purpose. A branch circuit that  
supplies two or more receptacles or outlets for lighting and  
appliances.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [January 26, 2020, 1:19pm UTC](https://forum.nachi.org/t/single-or-duplex-outlet/159933/42 "2020-01-26T13:19:21Z")

</div>

> [@mparks2](#):
>
> Assuming an individual branch circuit.
> 
> You can install a single 15 on:  
> Branch Circuit, General-Purpose. A branch circuit that  
> supplies two or more receptacles or outlets for lighting and  
> appliances.

Mike what am I missing? The last two on my list could be general purpose branch circuits.