# sink drain/traps

**URL:** <https://forum.nachi.org/t/sink-drain-traps/69902>\
**Category:** Plumbing Inspections\
**Created:** [June 15, 2012, 7:24pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902 "2012-06-15T19:24:09Z")\
**Posts on this page:** 17\
**Page:** 1

<div class="post-metadata">

**Author:** ![dokeefe](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dokeefe/32/171355_2.png) [@dokeefe](https://forum.nachi.org/u/dokeefe)\
**Post date:** [June 15, 2012, 7:24pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/1 "2012-06-15T19:24:09Z")

</div>

A little help here would be appreciated. This is new construction, under the kitchen sink. I’m not sure if this is OK. It looks a little hap hazard, not neat, (two traps?) especially for new construction. anytime I see work like this I start to question it. Thanks for any help.

 ![033.jpg](https://global.discourse-cdn.com/internachi/original/3X/7/1/710cbdbc98a6c8723f3c23a7cd0e6aec9449a8d8.jpeg)

 ![032.jpg](https://global.discourse-cdn.com/internachi/original/3X/9/d/9dbbe4c3c93d13bb307b9fdc0bce897061b6d39f.jpeg)

---

<div class="post-metadata">

**Author:** ![dokeefe](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dokeefe/32/171355_2.png) [@dokeefe](https://forum.nachi.org/u/dokeefe)\
**Post date:** [June 15, 2012, 7:28pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/2 "2012-06-15T19:28:09Z")

</div>

I was thinking this is some type of temporary setup. that adding a disposal would clean this up. any thoughts?

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [June 15, 2012, 7:52pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/3 "2012-06-15T19:52:09Z")

</div>

Not allowed… Only one P-trap allowed for each horizontal run of drain to the stack.

Also… the high loop needs to be properly secured in the proper position.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [June 15, 2012, 7:53pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/4 "2012-06-15T19:53:11Z")

</div>

> [@dokeefe](#):
>
> I was thinking this is some type of temporary setup. that adding a disposal would clean this up. any thoughts?

Depends how the disposal is installed.

---

<div class="post-metadata">

**Author:** ![dmacy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dmacy/32/1466_2.png) [@dmacy](https://forum.nachi.org/u/dmacy)\
**Post date:** [June 15, 2012, 8:33pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/5 "2012-06-15T20:33:41Z")

</div>

improper double trap noted. Fixtures must not be double-trapped because of the unnecessary additional restriction of flow and the increased potential for stoppages. Double-trapping can cause air to be trapped between the two trap seals, and the “air-bound” drain will block flow.

---

<div class="post-metadata">

**Author:** ![dokeefe](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dokeefe/32/171355_2.png) [@dokeefe](https://forum.nachi.org/u/dokeefe)\
**Post date:** [June 15, 2012, 8:41pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/6 "2012-06-15T20:41:39Z")

</div>

> [@jjonas](#):
>
> Depends how the disposal is installed.

I was thinking installing a disposal would eliminate one of the traps.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [June 15, 2012, 8:44pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/7 "2012-06-15T20:44:34Z")

</div>

> [@dokeefe](#):
>
> I was thinking installing a disposal would eliminate one of the traps.

Only if they plumbed it correctly while installing the disposal, which would mean re-doing everything already in place. I have seen many that were not.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [June 15, 2012, 8:46pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/8 "2012-06-15T20:46:10Z")

</div>

I don’t see that as a problem. Here is a similar thread: [http://www.nachi.org/forum/f22/double-trapped-22365/](http://www.nachi.org/forum/f22/double-trapped-22365/)

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [June 15, 2012, 8:47pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/9 "2012-06-15T20:47:30Z")

</div>

> [@dmacy](#):
>
> improper double trap noted. Fixtures must not be double-trapped because of the unnecessary additional restriction of flow and the increased potential for stoppages. Double-trapping can cause air to be trapped between the two trap seals, and the “air-bound” drain will block flow.

Actually… double trapping can cause one of the traps to siphon out and break the seal, leaving it unsealed.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [June 15, 2012, 8:49pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/10 "2012-06-15T20:49:19Z")

</div>

> [@jfunderburk](#):
>
> I don’t see that as a problem. Here is a similar thread: [Double Trapped? - Plumbing Inspections - InterNACHI®️ Forum](http://www.nachi.org/forum/f22/double-trapped-22365/)

[http://www.nachi.org/forum/attachments/f22/15899d1194620507t-double-trapped-pa270034.jpg](http://www.nachi.org/forum/attachments/f22/15899d1194620507-double-trapped-pa270034.jpg)  
Flow from the disposal drain can cause a siphon in the sink trap, emptying the trap and breaking the seal… or vice-versa. (Especially with the dishwasher discharge flow rate & duration).

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [June 15, 2012, 8:50pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/11 "2012-06-15T20:50:59Z")

</div>

Here’s a double trap:

> **[InterNACHI®️ Forum](https://forum.nachi.org/)**
>
> The InterNACHI®️ forum is a place for home inspectors and InterNACHI®️ members to discuss everything and anything related to the home inspection industry.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [June 15, 2012, 8:52pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/12 "2012-06-15T20:52:41Z")

</div>

Same principle, different hook-up.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [June 15, 2012, 8:55pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/13 "2012-06-15T20:55:17Z")

</div>

Not allowed by UPC standards. What code does your jurisdiction follow?

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [June 15, 2012, 8:57pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/14 "2012-06-15T20:57:55Z")

</div>

> [@jjonas](#):
>
> Flow from the disposal drain can cause a siphon in the sink trap, emptying the trap and breaking the seal… or vice-versa. (Especially with the dishwasher discharge flow rate & duration).

An S-trap has the siphoning problems you mention.

The problem with a double-trap is that air gets trapped \*between \*the two traps and will cause a stoppage of flow or blockage. I don’t see any way air can be trapped between the two traps in the OP’s picture.

---

<div class="post-metadata">

**Author:** ![dokeefe](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dokeefe/32/171355_2.png) [@dokeefe](https://forum.nachi.org/u/dokeefe)\
**Post date:** [June 15, 2012, 9:25pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/15 "2012-06-15T21:25:12Z")

</div>

> [@jpope](#):
>
> Not allowed by UPC standards. What code does your jurisdiction follow?

We follow the IRC

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [June 15, 2012, 9:30pm UTC](https://forum.nachi.org/t/sink-drain-traps/69902/16 "2012-06-15T21:30:36Z")

</div>

> [@dokeefe](#):
>
> We follow the IRC

And this is where you need to decide which road your company will take. If there is a potential risk for anything to go wrong, that is the road I will take. My clients health/safety is at risk. I will not ever knowingly place a client at risk, no matter how irrelevent it may seem to others. My clients, my company, my decision!

---

<div class="post-metadata">

**Author:** ![dokeefe](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dokeefe/32/171355_2.png) [@dokeefe](https://forum.nachi.org/u/dokeefe)\
**Post date:** [June 16, 2012, 11:59am UTC](https://forum.nachi.org/t/sink-drain-traps/69902/17 "2012-06-16T11:59:22Z")

</div>

Thanks for your help. I added it to the report.