Originally Posted By: jpeck
Yes.
NM cable is an example.
Comes manufactured as an assembly, which is why the white is allowed to be re-identified.
Individual conductors need to be pulled in being the correct color - don't pull in white, then expect to be able to say 'no, that one is black'. You can go the other way, pull in all black (for larger than #6 AWG) and then identify the black to white with tape.
B) Sizes Larger Than 6 AWG. An insulated grounded conductor larger than 6 AWG shall be identified either by a continuous white or gray outer finish or by three continuous white stripes on other than green insulation along its entire length
or at the time of installation by a distinctive white marking at its terminations. This marking shall encircle the conductor or insulation.
But not conductors #6 AWG and smaller.
(A) Sizes 6 AWG or Smaller. An insulated grounded conductor of 6 AWG or smaller
shall be identified by a continuous white or gray outer finish or by three continuous white stripes on other than green insulation along its entire length. Wires that have their outer covering finished to show a white or gray color but have colored tracer threads in the braid identifying the source of manufacture shall be considered as meeting the provisions of this section. Insulated grounded conductors shall also be permitted to be identified as follows:
(1) The grounded conductor of a mineral-insulated, metal-sheathed cable shall be identified at the time of installation by distinctive marking at its terminations.
(2) A single-conductor, sunlight-resistant, outdoor-rated cable used as a grounded conductor in photovoltaic power systems as permitted by 690.31 shall be identified at the time of installation by distinctive white marking at all terminations.
(3) Fixture wire shall comply with the requirements for grounded conductor identification as specified in 402.8
(4) For aerial cable, the identification shall be as above, or by means of a ridge located on the exterior of the cable so as to identify it.
Jerry Peck
South Florida