# Squared D secondary surge protector tapped into main

**URL:** <https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597>\
**Category:** Electrical Inspections\
**Created:** [March 12, 2020, 2:11am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597 "2020-03-12T02:11:39Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [March 12, 2020, 2:11am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/1 "2020-03-12T02:11:39Z")

</div>

Came across this today says it’s a secondary surge protector. Its tapped into the main breaker. Is this supposed to just go to it’s own breaker not sure how these work, just want to make sure. Thanks for any help with this

 ![20200311_180808](https://global.discourse-cdn.com/internachi/original/3X/8/5/852d8ad520f74672c4a9e8d2048a3068882226a5.jpeg) ![20200311_180818](https://global.discourse-cdn.com/internachi/original/3X/6/8/6875212fde178ea4952fbff713550589063aaac6.jpeg)

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 12, 2020, 2:17am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/2 "2020-03-12T02:17:39Z")

</div>

> [@dvandermeulen](#):
>
> Came across this today says it’s a secondary surge protector. Its tapped into the main breaker. This looks wrong to me ! just want to make sure. Bunch of other problems with this panel also. Just was wondering about this setup. Thanks for any help with this.

Pretty bad picture but from you verbiage, it is not correct. The main breaker in not listed for that type of termination. 😄

---

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [March 12, 2020, 2:18am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/3 "2020-03-12T02:18:34Z")

</div>

Sorry Larry I fixed it. The surge protector is on the right hand side of the one pic. I had to redo the other pic stupid phone

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 12, 2020, 2:20am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/4 "2020-03-12T02:20:13Z")

</div>

> [@dvandermeulen](#):
>
> Sorry Larry I fixed it. The surge protector is on the right hand side of the one pic. I had to redo the other pic stupid phone.

It is still not made for that type of termination. It is not listed for that, It is wrong.

---

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [March 12, 2020, 2:22am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/5 "2020-03-12T02:22:02Z")

</div>

Ok thanks Larry . Wasn’t sure how these things worked. I have plenty of other stuff I’m calling out in this panel also. Thanks for the help

---

<div class="post-metadata">

**Author:** ![jfudge](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfudge/32/414352_2.png) [@jfudge](https://forum.nachi.org/u/jfudge)\
**Post date:** [March 12, 2020, 2:23am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/6 "2020-03-12T02:23:01Z")

</div>

Panel is contaminated as well.

---

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [March 12, 2020, 2:23am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/7 "2020-03-12T02:23:58Z")

</div>

Hey junior thanks. Yep I’m calling out overspray paint, double tapped neutrals a broken neutral (not in this pic) and missing bushings

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 12, 2020, 2:29am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/8 "2020-03-12T02:29:52Z")

</div>

> [@dvandermeulen](#):
>
> a broken neutral

A broken neutral can be very dangerous. Make sure that is reported well.

---

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [March 12, 2020, 2:34am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/9 "2020-03-12T02:34:07Z")

</div>

Yep, absolutely. Already in

 ![20200311_180848](https://global.discourse-cdn.com/internachi/original/3X/b/4/b4cdbe059ebb4e4fc67b191ede2539455e9425f5.jpeg)

---

<div class="post-metadata">

**Author:** ![jmilby](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jmilby/32/57038_2.png) [@jmilby](https://forum.nachi.org/u/jmilby)\
**Post date:** [March 12, 2020, 6:47am UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/10 "2020-03-12T06:47:07Z")

</div>

If the neutral were broken the circuit would not work. I suspect the neutral was cut off from an abandoned circuit.

---

<div class="post-metadata">

**Author:** ![dvandermeulen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvandermeulen/32/205956_2.png) [@dvandermeulen](https://forum.nachi.org/u/dvandermeulen)\
**Post date:** [March 12, 2020, 12:11pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/11 "2020-03-12T12:11:23Z")

</div>

You might be right but there were multiple switches in the kitchen that didnt work. Not sure if it was related but I’m listing it as broken. Let an electrician sort through the mess

---

<div class="post-metadata">

**Author:** ![jfudge](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfudge/32/414352_2.png) [@jfudge](https://forum.nachi.org/u/jfudge)\
**Post date:** [March 12, 2020, 12:16pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/12 "2020-03-12T12:16:55Z")

</div>

Enough issues for sure. Any contaminated components will need replacement, etc…

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [March 12, 2020, 12:45pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/13 "2020-03-12T12:45:57Z")

</div>

> [@jmilby](#):
>
> If the neutral were broken the circuit would not work. I suspect the neutral was cut off from an abandoned circuit

That’s what I was thinking, as well, Jim, but got on to something in my PM and forgot to mention it. 😄

---

<div class="post-metadata">

**Author:** ![mgoldenberg](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgoldenberg/32/89265_2.png) [@mgoldenberg](https://forum.nachi.org/u/mgoldenberg)\
**Post date:** [March 12, 2020, 1:01pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/14 "2020-03-12T13:01:14Z")

</div>

> [@jfudge](#):
>
> Any contaminated components will need replacement

Bye bye!

> Paint contamination observed in interior of electric panel. Safety hazard, fire  
> hazard, and maintenance concern.  
> Paint can interfere with proper connections between electric components or proper  
> operation of circuit breakers, creating conditions where proper grounding and  
> electrical connections are not present, possibly causing brown-outs, arcing, and fires.  
> Paint can also cause the wire insulation to deteriorate.  
> No approved method exists for cleaning contaminants from panel interiors or  
> components such as bus or terminal bars, circuit breakers or fuses.  
> The panel and/or components inside may need replacing.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [March 12, 2020, 2:03pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/15 "2020-03-12T14:03:50Z")

</div>

Yes there is some slight paint over spray but IMO nothing in those photo’s would indicate that it’s a safety issue.

---

<div class="post-metadata">

**Author:** ![jfudge](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfudge/32/414352_2.png) [@jfudge](https://forum.nachi.org/u/jfudge)\
**Post date:** [March 12, 2020, 2:56pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/16 "2020-03-12T14:56:15Z")

</div>

So this wouldn’t be considered contamination, as to what the code states? Are you saying he shouldn’t call it out?

Internal components of electrical equipment “shall not be damaged or contaminated by foreign materials such as paint, plaster, cleaners, abrasives or corrosive residues.

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [March 12, 2020, 2:57pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/17 "2020-03-12T14:57:24Z")

</div>

You are like a younger Roy.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [March 12, 2020, 2:58pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/18 "2020-03-12T14:58:04Z")

</div>

Who are you referring to?

---

<div class="post-metadata">

**Author:** ![jfudge](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfudge/32/414352_2.png) [@jfudge](https://forum.nachi.org/u/jfudge)\
**Post date:** [March 12, 2020, 2:59pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/19 "2020-03-12T14:59:42Z")

</div>

Haha! I’m curious as to what Robert is saying. Seems to me it would be considered contamination. I would call it out.

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [March 12, 2020, 3:01pm UTC](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597/20 "2020-03-12T15:01:01Z")

</div>

You are the one😁

[Next page](https://forum.nachi.org/t/squared-d-secondary-surge-protector-tapped-into-main/162597.md?page=2)