STAB-LOC service panel

Hi Friends

I am looking for your help on if I should put in my inspection report recommending the replacement of old Stab-Loc service panel due to it known unreliable breakers. It is still functioning but I didn’t test it. Some of the breakers triggered my non-contact voltage probe red light, some didn’t. Should I write it up as “Major defect” or “Information Only”. Either way, I will recommend a licensed electrician.

Thank you

The electrical service Panel was manufactured by the Federal Pacific Electric company and used “Stab-Lok” circuit breakers. There is evidence that both double and single-pole versions of these Stab Lok circuit breakers fail by not tripping when they are supposed to, which in turn often leads to breakers overheating and in some cases, electrical fires. However, in 2011 the Consumer Products Safety Commission (CPSC) closed an investigation into this product because they did not have enough funding to establish that the circuit breakers pose a risk of injury/fire to consumers. Regardless, and due to other evidence of safety issues, it is recommended that a qualified electrician carefully evaluate all Federal Pacific panels and make recommendations. Some insurance companies are not offering property insurance with this manufacturer’s panel installed in single-family homes. I recommend that you check with your insurance provider if they allow this equipment.

Below is a link to a document by the Casualty Underwriters Association of America and their view on aged panels.

https://www.cauinsure.com/Include/Documents/P11%20-%20Aging%20Electrical%20Systems.pdf

8 Likes

Remove “Major” from your HI vocabulary. Its either a defect or not a defect. Sometimes, I use the term “Significant” in lieu of stronger language such as “Major”. Although, I’m curious if I’m falling into the same trap that I’m championing against? I’m monitoring the feedback… :sweat_smile:

7 Likes

Every narrative is a de facto rating. However, lumping defects into predefined categories such as major or minor can be a problem IMO, especially for newer inspectors.

Just as you, I avoid the term major or minor and often use the term ‘significant’ in a narrative if I am writing hard on an issue.

2 Likes

Simply state it is an obsolete panel. That means it is no longer manufactured and parts may not be available for upgrades or repairs.

Then provide a link that supplies all that information about breakers that don’t trip etc. Let them decide.

5 Likes

No, you shouldn’t recommend replacement, in my opinion. But, you should recommend it be fully evaluated by a qualified electrical contractor. If it needs replacement, let the electrician make that call.

3 Likes

I call all FPE panels out as not only a major defect, but also a safety and fire hazard, I also recommend replacement of these, and some other panels due to documented failures and fires.

Fortunately, most Real Estate Agents in the markets I serve are aware of the issues with these panels and recommend that their clients replace them before they put their house on the market.

are federal pacific electric panels a fire hazard - Google Search

AI Overview

Yes, Federal Pacific Electric (FPE) Stab-Lok electrical panels are a known fire hazard

due to their circuit breakers’ tendency to fail to trip during overloads, leading to overheating and potential fires. This failure is attributed to a flaw in the breaker’s internal mechanism and falsified safety testing by FPE. Experts and fire departments recommend replacing these panels with modern, up-to-date circuit breaker panels.

Why they are dangerous:

  • **Breaker Failure:**The primary danger is that the Stab-Lok circuit breakers may not function as designed, failing to trip or cut off power during an electrical overload or short circuit.

  • **Overheating and Fires:**This failure allows electrical wires to become excessively hot, which can then ignite a fire.

  • **Falsified Testing:**The company, Federal Pacific, was found to have falsified safety testing results to make their breakers appear compliant with industry standards.

  • **Stab-Lok Breaker Failure in Testing:**Studies have shown that these breakers can fail to trip under heavy loads nearly 80% of the time.

What to do if you have an FPE panel:

  1. Inspect your panel: Look inside the breaker area for the name “Stab-Lok” to identify if you have an FPE panel.

  2. Contact a licensed electrician: Get an assessment from a qualified electrician to confirm the hazard.

  3. Schedule a replacement: Insist on a complete replacement of the FPE panel with a modern, safe circuit breaker panel.

  4. Inform home inspectors: If you are a new home buyer, ensure your home inspector checks for FPE panels and insist on replacement before purchasing the property.

6 Likes

^^^^ Same here.

2 Likes

This is popular topic. I am in the camp that defects are not equal. Some are major and some are not. Semantics between “major” and “significant”. If you are more comfortable with “significant”, that’s fine. I use “major.” I want my clients to know that FPE panels have well documented problems in addition to the two that I’ve seen that were ready to burn the house down. They have major design defects, even if this one appears to be chugging along today.

If you tell me, that’s a defect, I am going to ask you what that means. How are you going to describe a defect without grading the seriousness.
An FPE panel is a defect. Ok, what do you mean? I just find a defect, and you should do your own research and decide what you want to do? Maybe we’re different around here, but my clients seem to think they are paying me the medium size bucks to tell them if this or that defect is a big deal or not. I expect and demand the same from any contractor I hire.

5 Likes

That’s another word to be very cautious with using in your report(s)!

3 Likes

It is common now. Another canned category. Minor, major, maintenance, and monitor.

I guess the homeowner is now to be the expert, and is to determine when/why action is to be taken.

4 Likes

Yup.
I guess if the Home Inspector isn’t capable enough to make a determination, just pass it off to the homeowner. It’s their money, right?!

4 Likes

Thank you Bert for your feedback, greatly apprecated

2 Likes

Thank you David for your feedback

1 Like

Thank you Kevin for your detailed comments

2 Likes

Thank you Lon for your response

Thank you Brian for your reply

Thanks Jeffrey

Which they will.. I doubt any electrician would say it’s fine, when they can make an easy sale

4 Likes

I always recommend replacement of these panels for a variety of reasons…..

1 Like