What should I do when an electrician tells me everything is fine and that the two extra wires connected to the main lugs are safe?
Who is asking you to do anything? You gave your opinion that it’s wrong and to have an electrician look at it. You’re done.
An electrician came and did the work, and he told me those wires are fine and don’t need to be removed because they have wire nuts.
As much as we sometimes would like to "have it done our way”, we can’t force anyone to do anything.
What exactly did your report recommend?
You made your recommendations and the electrician disagreed with you. The person you did the inspection for chose the electrician. You did your job, move on.
Is this your house or one you inspected?
Right, buy WHY is it your problem??? You made your recommendation. You are done. Why do you give two shits what the specialist you advised had to say?? There’s nothing to gain trying to be superman and cramming your opinion down everyone’s throat. You did your job… again, you’re done. Move on.
Dear Emmanuel,
I conducted a re-inspection of the property today. Although the electrician stated that the work was completed, the two wires connected to the main lugs have not been removed. The electrician maintains that the current configuration is safe.
Best regards,
Jesus E Diaz
Like inspectors there are good electricians and bad electricians. I’ll call the one you’re dealing with a bad electrician if he sees nothing wrong with the panel in your photo. Even though you’re not a code inspector the two wires shoved under the terminals is a violation. Once those terminals have been loosen and re-tightened with the additional conductor there is no way of know if the connection is good because it has not been tested with two conductors. Along with that you have two dissimilar metals (copper and aluminum) in contact with each other in a terminal designed for only one conductor. The panel has several other problems as well.
110.14(A) Terminals.
Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solderlugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors. Terminals for more than one conductor and terminals used to connect aluminum shall be so identified
110.14 Electrical Connections.
Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.
When a client complains (about an unnecessary electrician visit) just tell them to have the electrician put it in writing just like you did.
Thank you Sir for your Help and opinion
I, as an inspector, should leave the report still as a double tap in my 4Point report, or should I put all the responsibility on the electrician who is saying that everything is fine, or should he go and remove those wires? I understand that I am not a code inspector, but if something happens on that property, I was the inspector and everything legal is going to come over me.
I answer your question in the other (duplicate) post.
IMO you should just report what you see. You’ve said that upon reinspection the electrician failed to make the corrections. As an electrician and code inspector my opinion may differ from the opinion of a HI. I would follow what the seasoned home inspectors say.
These things come up. The “monkey” is now on the electrician’s back. If asked, I simply say, “The electrician and I disagree, but he is the expert. I as the home inspector, recognize something that looks like a defect and recommend further evaluation by the appropriate expert, which I did. If you still have concerns, get a third opinion.”
You reported on it, recommend a licensed professional further review, you’ve done your job, move on. Some but, not all Electricians are notorious for this crap of talking down to Home Inspectors. If you’re asked to sign off on it for Insurance, tell them no, the electrician can sign off… see how fast he/she fixes it…
We are not the inspection police. You did your job. You found a defect, reported it and recommended action. If no one acts on your report and recommendation, that ain’t your fault or job to try to make them act. Many years ago, I was not included in a lawsuit because I had observed flat to inadequate drainage around a house and recommended improving it. When water flooded the basement, all I ever heard about it was from the plaintiff’s attorney who called to confirm with me what I had reported.
I understand that I did my job, but my client needs the 4 points for his insurance and the electrician is saying that’s fine.
- You called out a defect.
- Another professional disagrees with you.
- You know you are right but you are afraid of the consequences.
What do you want from us?
I agree with the consensus here. You have done your job (and done it correctly)!
It is now time for your client to hash it out with his electrical contractor.