Student inquiry regarding Fireplace and chimney course

Can someone explain the following statement from the “How to Inspect Fireplace, Stove and Chimney” course:

The inspector should inspect for connectors from solid fuel-burning appliances that have a rise to the chimney of less than 1/4-inch per foot.

Thanks,

Mikah Simmons

Contact the Education Department directly…

(Scroll down for more…)

2 Likes

Nooo can’t be, that’s building codes and we’re not code Inspectors!

:wink: :wink:

1 Like

Mikah, hope to find you well.

Is that an multiple choice question?
I feel it should read: The inspector should inspect for connectors from solid fuel-burning appliances that have a rise to the chimney for less than 1/4-inch per foot and proper support.

A rise of less than 1/4"-inch per foot is a disallowed slope for a vent connector on solid fuel-burning appliances.

Solid fuels: Wood, Coal, or Pellets.
Solid fuel appliances: Wood stoves. Fireplaces. Specialized boilers and furnaces.

The standard installation requires a minimum slope of 1/4"-inch of rise for every foot or 12"-inches of horizontal run, is to ensure proper upward/upstream flow of combustion flue gases and to prevent dips or sags in the connector pipe.

1 Like

It’s on page 23 of this course accompaniment study guide…

study guide Student-Course-Material.pdf (1.1 MB)

2 Likes

Thanks, Richard.

Picture the horizontal run of stove pipe from an airtight wood stove or pellet stove (coal stove) to the chimney. That is what they are referring to, just eyeball it, does it have a little slope? your good.

2 Likes

In my opinion, it is worded poorly. A better way to state it would be…

“The inspector should inspect connectors from solid fuel-burning appliances to ensure they have a rise to the chimney of at least 1/4-inch per foot.”

2 Likes