Sub Panel Feeder

Seems like people are always thinking outside the box… I’m inclined to think that while being unorthodox, that this feed to the Sub Panel is OK, but thought I would ask for a second opinion.

This image:

The neutrals and EGC’s need to be separate at the subpanel among other violations.

The neutral terminal appears to have a bonding strap attached to it, there are missing knock-outs to name some others.

Nothing about this installation is “proper,” but it will certainly provide power to its intended circuits. . .

Thanks Robert and Jeff, the client’s father is an electrician and also the Fire Marshall, I visited with him and he plans to make the proper corrections.