This is a sub-panel for a heat pump package unit; there are two hots and a ground coming in from the top from the main panel; the grounds are on a floating neutral bus with no bonding to box. Shouldn’t there be a neutral from the main and a bonding strap. Thanks

120921 9059 Nighthawk FC - Full, 4 pt 117.jpg

120921 9059 Nighthawk FC - Full, 4 pt 115.jpg

120921 9059 Nighthawk FC - Full, 4 pt 114.jpg

120921 9059 Nighthawk FC - Full, 4 pt 116.jpg

120921 9059 Nighthawk FC - Full, 4 pt 113.jpg

No neutral required for only 240 volt loads but you’re correct the EGC bus should be bonded to the enclosure. Depending on a few things you may have a derating issue with the 4 CCC’s in the FNMC.

Robert thanks for the quick reply; I would’t think the derating will be an issue as the conduit is only about a foot in length.

24" or less and you’re correct no derating required.