# Sub panel improper wiring

**URL:** <https://forum.nachi.org/t/sub-panel-improper-wiring/225101>\
**Category:** Electrical Inspections\
**Created:** [February 1, 2023, 12:28am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101 "2023-02-01T00:28:50Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![aponder](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/aponder/32/60168_2.png) [@aponder](https://forum.nachi.org/u/aponder)\
**Post date:** [February 1, 2023, 12:28am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/1 "2023-02-01T00:28:50Z")

</div>

I inspected a sub panel that had your standard romex coming into the panel. It looked like a rush job and whoever did it couldn’t get to the ground bus. So, they attached the wire to a screw inside the panel. Part of me thinks; “ok, so the screw is attached to the panel just like the ground bus is attached to the panel so it’s conceivable it’s ok.” but the OC part of me says, “no, the wire belongs on the bus like everyone else”. What are your thoughts? Thanks in advance.

 ![IMG_3505](https://global.discourse-cdn.com/internachi/original/4X/1/2/a/12a7b65c2a87e6933c875bee88e3b7db5db18973.png)

 ![IMG_3506](https://global.discourse-cdn.com/internachi/original/4X/f/d/9/fd9595376443a38d350bd67aa38d1ddd9eaf5243.png)

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [February 1, 2023, 12:33am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/2 "2023-02-01T00:33:04Z")

</div>

> [@aponder](#):
>
> What are your thoughts?

I don’t believe that screw is listed and labeled for that purpose…

---

<div class="post-metadata">

**Author:** ![aponder](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/aponder/32/60168_2.png) [@aponder](https://forum.nachi.org/u/aponder)\
**Post date:** [February 1, 2023, 12:46am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/3 "2023-02-01T00:46:15Z")

</div>

Dang Larry, you just trumped both sides of my brain and went for the obvious. Thanks for the insight man. I appreciate you!

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [February 1, 2023, 4:33am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/4 "2023-02-01T04:33:22Z")

</div>

What Larry said…improper termination.

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [February 1, 2023, 2:15pm UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/5 "2023-02-01T14:15:13Z")

</div>

> [@aponder](#):
>
> Part of me thinks; “ok, so the screw is attached to the panel just like the ground bus is attached to the panel so it’s conceivable it’s ok.” but the OC part of me says, “no, the wire belongs on the bus like everyone else”. What are your thoughts? Thanks in advance.

You do not ground sub/remote panels.  
The single neutral terminating on the netral buss should suffice if the system was correctly wired.  
A sub/remote panel ground terminal, not a buss, should be bonded to the enclosure.

I have no idea why someone terminated what looks like a ground conductor on the screw for plastic retention channel separating the neutral busses from the metal enclosure.

---

<div class="post-metadata">

**Author:** ![jmilby](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jmilby/32/57038_2.png) [@jmilby](https://forum.nachi.org/u/jmilby)\
**Post date:** [February 1, 2023, 10:05pm UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/6 "2023-02-01T22:05:15Z")

</div>

Subpanels need to be grounded. A single neutral is not enough. If the panel is properly wired post 2008 NEC in a detached structure or anytime in an attached structure it should be feed with a 4 wire feed with a dedicated grounding conductor as well as the neutral. Pre 2008 panels in detached structures were allowed with a 3 wire feed as long as no metallic paths existed between buildings. In those panels the ground was bonded to neutral like a service.

---

<div class="post-metadata">

**Author:** ![mparks3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks3/32/277434_2.png) [@mparks3](https://forum.nachi.org/u/mparks3)\
**Post date:** [February 2, 2023, 1:26am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/7 "2023-02-02T01:26:52Z")

</div>

> [@ryoung7](#):
>
> You do not ground sub/remote panels.

Yes you do.

> [@ryoung7](#):
>
> The single neutral terminating on the netral buss should suffice if the system was correctly wired.

Correct.

> [@jmilby](#):
>
> If the panel is properly wired post 2008 NEC in a detached structure or anytime in an attached structure it should be feed with a 4 wire feed with a dedicated grounding conductor as well as the neutral. Pre 2008 panels in detached structures were allowed with a 3 wire feed as long as no metallic paths existed between buildings. In those panels the ground was bonded to neutral like a service.

That is citing code.

As Robert implied a 4 wire system does not make panels down stream safer. If a qualified individual works on the electrical system no problems. We went to a 4-wire system because unqualified individuals were creating paralleled panels and creating hazards.

If you are in a new build and a sub is ran in 3-wire it is a code violation. Not a safety violation.

The OP is safe just not code compliant. That is what makes electrical inspections tricky.

You dare not say that it is safe and you dare not say that it is not code compliant. I like improper termination

---

<div class="post-metadata">

**Author:** ![jmilby](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jmilby/32/57038_2.png) [@jmilby](https://forum.nachi.org/u/jmilby)\
**Post date:** [February 2, 2023, 1:38am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/8 "2023-02-02T01:38:58Z")

</div>

The 4 wire feed does make the installation safer as it provides a dedicated ground path without depending on the neutral.

---

<div class="post-metadata">

**Author:** ![mparks3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks3/32/277434_2.png) [@mparks3](https://forum.nachi.org/u/mparks3)\
**Post date:** [February 2, 2023, 1:50am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/9 "2023-02-02T01:50:24Z")

</div>

> [@jmilby](#):
>
> The 4 wire feed does make the installation safer as it provides a dedicated ground path without depending on the neutral

How so? Both methods only have 1 path to ground.

---

<div class="post-metadata">

**Author:** ![dhorton2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhorton2/32/178593_2.png) [@dhorton2](https://forum.nachi.org/u/dhorton2)\
**Post date:** [February 2, 2023, 3:17am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/10 "2023-02-02T03:17:31Z")

</div>

> [@mparks3](#):
>
> How so? Both methods only have 1 path to ground.

It prevents stray current from the neutral from traveling on all the grounding conductors.  
You can’t do that unless you have a dedicated EGC

---

<div class="post-metadata">

**Author:** ![srechkin](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/srechkin/32/180448_2.png) [@srechkin](https://forum.nachi.org/u/srechkin)\
**Post date:** [February 2, 2023, 3:20am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/11 "2023-02-02T03:20:43Z")

</div>

Arguing with an electrical inspector in a state where home inspector is “not allowed” to remove the cover to an electrical panel. Good luck!

---

<div class="post-metadata">

**Author:** ![mparks3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks3/32/277434_2.png) [@mparks3](https://forum.nachi.org/u/mparks3)\
**Post date:** [February 2, 2023, 3:26am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/12 "2023-02-02T03:26:12Z")

</div>

> [@dhorton2](#):
>
> It prevents stray current from the neutral from traveling on all the grounding conductors.

Connections prevent that not the # of conductors. You can safely wire sub panels with 3-wire all day long. They just won’t be code compliant.

---

<div class="post-metadata">

**Author:** ![dhorton2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhorton2/32/178593_2.png) [@dhorton2](https://forum.nachi.org/u/dhorton2)\
**Post date:** [February 2, 2023, 4:02am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/13 "2023-02-02T04:02:41Z")

</div>

> [@mparks3](#):
>
> Connections prevent that not the # of conductors. Yo

Really? Then what is the point of removing the bonding screw at the sub panel?  
Wait, I’ll answer for you… it is to prevent current from traveling on the grounding conductors… so how can you do that with 3 wire?  
You know, there’s a reason codes change

---

<div class="post-metadata">

**Author:** ![mparks3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks3/32/277434_2.png) [@mparks3](https://forum.nachi.org/u/mparks3)\
**Post date:** [February 2, 2023, 4:05am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/14 "2023-02-02T04:05:25Z")

</div>

> [@dhorton2](#):
>
> You know, there’s a reason codes change

Yes. And I can teach the code in Ohio. The change was in 2008 NEC. Would you like to learn how?

---

<div class="post-metadata">

**Author:** ![dhorton2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhorton2/32/178593_2.png) [@dhorton2](https://forum.nachi.org/u/dhorton2)\
**Post date:** [February 2, 2023, 4:13am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/15 "2023-02-02T04:13:50Z")

</div>

> [@mparks3](#):
>
> Would you like to learn how?

Yes, since I’ve already asked twice:

> [@dhorton2](#):
>
> it is to prevent current from traveling on the grounding conductors… so how can you do that with 3 wire?

---

<div class="post-metadata">

**Author:** ![mparks3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks3/32/277434_2.png) [@mparks3](https://forum.nachi.org/u/mparks3)\
**Post date:** [February 2, 2023, 4:19am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/16 "2023-02-02T04:19:36Z")

</div>

I just threw this together. Tell me which is safe.

 ![image](https://global.discourse-cdn.com/internachi/original/4X/a/a/d/aad6badfa3d744b89b1d5c9e90d3f85aa0f53ade.png)

---

<div class="post-metadata">

**Author:** ![mparks3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks3/32/277434_2.png) [@mparks3](https://forum.nachi.org/u/mparks3)\
**Post date:** [February 2, 2023, 4:22am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/17 "2023-02-02T04:22:12Z")

</div>

Each is HHN / hot hot neutral / no EGC equipment grounding conductor

---

<div class="post-metadata">

**Author:** ![mparks3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks3/32/277434_2.png) [@mparks3](https://forum.nachi.org/u/mparks3)\
**Post date:** [February 2, 2023, 4:24am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/18 "2023-02-02T04:24:57Z")

</div>

![image](https://global.discourse-cdn.com/internachi/original/4X/3/1/a/31ab134a438323079a225dd89aec86dfacb736f0.png)

---

<div class="post-metadata">

**Author:** ![dhorton2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dhorton2/32/178593_2.png) [@dhorton2](https://forum.nachi.org/u/dhorton2)\
**Post date:** [February 2, 2023, 4:26am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/19 "2023-02-02T04:26:27Z")

</div>

Apparently we arent talking about the same thing. For the first diagram: Missing bonding at the right sub panel results in 2 things.  
1.The enclosure isnt grounded/bonded to the grounding conductors, which can result in the breakers not tripping in the event of ground fault.  
2. It also means the grounds and the neutrals are bonded together at the bus bars. Which, like I said, will result in stray neutral current all throughout the home on the grounding conductors.

---

<div class="post-metadata">

**Author:** ![mparks3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mparks3/32/277434_2.png) [@mparks3](https://forum.nachi.org/u/mparks3)\
**Post date:** [February 2, 2023, 4:28am UTC](https://forum.nachi.org/t/sub-panel-improper-wiring/225101/20 "2023-02-02T04:28:27Z")

</div>