What is the correct terminology to describe double tap shown below? Subfeed lug double tap??

I would say, “Double-tapped lug in the subpanel.”
“Double-Lugged”… but is the least of your worries in that panel.
Lot’s of repairs/corrections needed in there.
Refer to a qualified, licensed Electrician for full evaluation and all necessary repairs, up to and including panel and conductor replacement as needed!!
Those wires do not have an overcurrent protection device.
How do you know that?
Looks to me to be a whole house Surge Protector.
Am sorta surprised it’s actually mounted correctly to the panel… regardless of how it’s wired.
More than one conductor terminated in a terminal listed for use with only one conductor.
The red wires and the black wires are on the same circuit. They both do not have the same capacity. If there is an OCPD, it is going to be rated for the black conductors. So the red conductors are not protected. If they are, then the breaker will trip from the panel load.
You’re right, I don’t know.
All we know is what is in the picture.
Those are not sub-feed lugs. They are main lugs. Sub-feed lugs are usually at the bottom.
How do you know that the red conductors are not protected? There’s nothing in the photos or the original post that reveals their purpose or that would necessarily lead to the conclusion that they are not protected.
The OP referred to the lugs as sub-feed lugs, which they are not. However, the red conductors are most likely being used as feeders.
There’s no reason to believe that the red conductors are anything other than feeders. Aside from the improper termination, the feed is no different from what it would be if, in fact, there were subfeed lugs and the red conductors connected to them.
There’s nothing in the OP that suggests that the red conductors are protected by the same OCPD as the black conductors.
I think JJ nailed it. It looks like the wiring for a SPD but who knows based on the photos shown. Since there are only three conductors feeding this panel one could reasonably assume that this is the service so the red conductors are connected on the line side of the panel bus meaning that they are not feeders but service conductors. More information and better photos would help.
Residential applications rarely meet the requirements for tap conductors and those reds to not look to be large enough to be taps either.
Where is the main disconnect?