Subpanel disconnect & 6 movement rule
I have a subpanel in a condo unit that is protected by a breaker upstream on the feed to the subpanel. There is no main disconnect on the subpanel, and there are 12 circuit breakers in the subpanel. I understand there is no need for a main breaker in the subpanel because of the breaker upstream.
I do not understand if or how the “6 movement” rule applies here. Does this rule mean I now have to see a main disconnect in this subpanel? Initial research is not providing me with an answer.
This building was built in 1982. Four wire feed.
I think it depends on the location of the panel feeding the sub panel. In a single family dwelling, as long as the main panel is in the same ‘structure’ no main is required on the sub. I am not sure what the regulation is for condo’s.
Maybe you can decipher this, I cannot :wink:
https://www.eaton.com/content/dam/eaton/products/low-voltage-power-distribution-controls-systems/switchboards/wp014008en.pdf
My understanding is the six hand movements is a substitute for a main so I’d think of them the same. Are sub panels required to have mains? Generally, no, so it sounds like your situation is setup okay. I tread pretty lightly on these things that have been in place for years and are functioning as intended. The risk of being wrong and pissing everyone off is high and there is really not much reward for being “right”. You have lots of good defense if anyone ever tried to come after you for not bringing it up.
It would be rare to find a main breaker on the panel in the condo unit. Not needed and extra cost.
Disconnect located at the meter, in the same building, serves as the disconnect means for the unit. No disconnect needed inside of the unit (though it is nice).
It doesn’t.
What do you not understand?
The document I provided does not seem to directly apply to the OP’s question but had some related disconnect information. My comment was more tongue and cheek because these technical bulletins often raise as many questions as it answers.
It doesn’t because the six movement rule applies to service disconnects. The single CB upstream of this panel is the service disconnect so there is no limit as to the number of circuit breakers that can be in that panel other than what is part of the panel’s listing.