Originally Posted By: mpettitt This post was automatically imported from our archived forum.
Heat pump split system, air handler in garage. A supply vent was installed in the plenum to cool or heat garage. Is this okay, seems I’ve read somewhere that it is wrong, but don’t remember why.
system
(system)
May 28, 2005, 12:00am
2
Originally Posted By: Lee Hammerstein This post was automatically imported from our archived forum.
It is wrong to have a supply or return register in the garage. It opens a path for the fumes from the garage to enter the living area.
system
(system)
May 28, 2005, 12:00am
3
Originally Posted By: mboyett This post was automatically imported from our archived forum.
– Mike Boyett
Capital City Inspections
Austin, Tx
www.capcityinspections.com
system
(system)
May 28, 2005, 12:00am
4
Originally Posted By: hgordon This post was automatically imported from our archived forum.
CAUTION - Carbon Monoxide Poisoning of occupants possible. Have the supply in the garage removed.
– Harvey Gordon
SE Florida NACHI Chapter - President
hgordon@fl.nachi.org
system
(system)
May 29, 2005, 12:00am
5
Originally Posted By: mpettitt This post was automatically imported from our archived forum.
Thanks everyone, got it.