Generally it should be installed so that the neutral conductor is short as possible but other than that do you see any issues? Is this a sub-panel?
It’s not a sub-panel, I just want to know if it’s right, that it’s at the top and not at the top of the main.
I spoke with a tech from SquareD(?) he said the location on the bus bar does not matter.
There is no code requirement for it to go next to the main unless it is specifically required by the installation instructions that are part of the listing of the SPD. For most it doesn’t matter where it’s installed. Simplest way to know is to look up the model number and find the installation instructions.
Not required to be directly adjacent to the main. The priority is using the shortest practical leads.
I thought that too until I enlarged the second photo. In the second photo it does appear to be on both busbars. Maybe Jesus can confirm.
I thought that also at first, but decided that no reputable company like Siemens would offset the unit to overhang half-off and out of alignment. I was hoping to find a diagram/graphic on their website, but didn’t see one. I decided to post the info I had, and the OP could make his own decision as to how he wanted to proceed with his write-up (or not).
It is just fine!
GQQD catch.
I think it’s an optical illusion and it is installed on both busbars. Would one of the indicators be red if not Robert? Or, not necessarily?
You sure do catch some detailed information when people send in pictures. You and others have excellent eyes for this and great help to me, every time I read through these posts I learn how to look deeper into things.
Yes it’s on both busbars. Count the slots on each side of the panel from the bottom up. There are 15 slots on the left and 15 slots on the right. 30 slots would be a standard number for this style of panel.
Good question. Those indicators are not LED’s so right out of the box they will still be both green. It’s a mechanical indicator that changes when the SPD fails.
This reminds me of why I decided to finish reports on-site when I struck out on my own. I ran into the optical illusion factor too often when I worked with my dad and his digital camera ![]()
I already put it in the report, it’s covering the protective surge.
So what wording ended up going in the report? The cover not being properly installed?