# Tankless water heater and pressure relief valve

**URL:** <https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508>\
**Category:** Plumbing Inspections\
**Created:** [June 24, 2008, 4:54pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508 "2008-06-24T16:54:00Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![Chris\_Tan](https://avatars.discourse-cdn.com/v4/letter/c/22d042/32.png) [@Chris\_Tan](https://forum.nachi.org/u/Chris_Tan)\
**Post date:** [June 24, 2008, 4:54pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/1 "2008-06-24T16:54:00Z")

</div>

The home I’m purchasing has a Takagi tankless water heater but does not have a temperature/pressure relief valve or a discharge line. We asked for this to be added and the sellers told us that per the codes for tank-less hot water heaters (California) a pressure relief valve nor a discharge line are needed. Is this true? If so, is it still a good idea to have one installed or does that fact that the heater is tankless make these items not necessary?

Thanks for everyone’s input.

Chris

---

<div class="post-metadata">

**Author:** ![mboyett](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mboyett/32/59512_2.png) [@mboyett](https://forum.nachi.org/u/mboyett)\
**Post date:** [June 24, 2008, 5:24pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/2 "2008-06-24T17:24:48Z")

</div>

Chris,

1. The tankless water heater should have been installed only by a qualified, Tagaki approved installer so it should be proper.
2. Tagaki and others, i.e. Bosch, Noritz, etc require a pressure only relief valve on the hot water output. Pressure only valves such as Cash Acme FWL-2, Zurn P3000BR, or Watts 174A would be required. Temperature sensing is done internally via an integral hi-limit switch.
3. Manufacturer’s requirements supersede all others…it seems you do need a Pressure Relief Valve but it may depend upon your particular model. Contact your local Tagaki authorized installer for more information.

Here is an excerpt from a Tagaki installation manual:  
 ![Capture.JPG](https://global.discourse-cdn.com/internachi/original/2X/5/517b649dfd334950cd03087305327fb9e8b2c582.jpeg)

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [June 24, 2008, 6:34pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/3 "2008-06-24T18:34:11Z")

</div>

Interesting since the regular tank models have expansion tanks on the cold side.

Gotta think about that one.

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [June 24, 2008, 6:36pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/4 "2008-06-24T18:36:34Z")

</div>

Expansion tanks and pressure relief valves serve two different purposes.

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [June 24, 2008, 6:43pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/5 "2008-06-24T18:43:47Z")

</div>

Yes and no  
They both deal with the problem of water expansion.  
Though I understand what you mean.(just had to get off post.)

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [June 24, 2008, 6:46pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/6 "2008-06-24T18:46:27Z")

</div>

I meant to state TPR and expansion tank.

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [June 24, 2008, 6:52pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/7 "2008-06-24T18:52:41Z")

</div>

close enough

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [June 24, 2008, 8:59pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/8 "2008-06-24T20:59:35Z")

</div>

> [@Chris Tan](#):
>
> The home I’m purchasing has a Takagi tankless water heater but does not have a temperature/pressure relief valve or a discharge line. We asked for this to be added and the sellers told us that per the codes for tank-less hot water heaters (California) a pressure relief valve nor a discharge line are needed. Is this true? If so, is it still a good idea to have one installed or does that fact that the heater is tankless make these items not necessary?
> 
> Thanks for everyone’s input.
> 
> Chris

A relief valve is absolutely necessary with any type of water heating device. A combination temperature/pressure relief valve is only required with storage-tank type heaters.

The relief valve doesn’t necessarily need to be near the heater, although most competent installers will generally place it relatively close to the heater.

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [June 24, 2008, 10:38pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/9 "2008-06-24T22:38:22Z")

</div>

Makes sense

---

<div class="post-metadata">

**Author:** ![jgilleland](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgilleland/32/1326_2.png) [@jgilleland](https://forum.nachi.org/u/jgilleland)\
**Post date:** [June 25, 2008, 7:03pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/10 "2008-06-25T19:03:40Z")

</div>

Good post Jeff. Tankless water heaters are subject to the same type of failures that tank type water heaters occasionally suffer from.

 ![tagaki install.jpg](https://global.discourse-cdn.com/internachi/original/2X/3/37ab8c5f8ed3b1e81b2a9a060bbe044f37b49a6e.jpeg)

---

<div class="post-metadata">

**Author:** ![jallingham](https://avatars.discourse-cdn.com/v4/letter/j/53a042/32.png) [@jallingham](https://forum.nachi.org/u/jallingham)\
**Post date:** [June 25, 2008, 10:19pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/11 "2008-06-25T22:19:45Z")

</div>

> [@Chris Tan](#):
>
> The home I’m purchasing has a Takagi tankless water heater but does not have a temperature/pressure relief valve or a discharge line. We asked for this to be added and the sellers told us that per the codes for tank-less hot water heaters (California) a pressure relief valve nor a discharge line are needed. Is this true? If so, is it still a good idea to have one installed or does that fact that the heater is tankless make these items not necessary?
> 
> Thanks for everyone’s input.
> 
> Chris

I’m starting to see these more frequently, usually coupled up with a holding tank and a high velocity heating system. They always have relief valves.

---

<div class="post-metadata">

**Author:** ![jgilleland](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgilleland/32/1326_2.png) [@jgilleland](https://forum.nachi.org/u/jgilleland)\
**Post date:** [June 26, 2008, 4:11am UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/12 "2008-06-26T04:11:45Z")

</div>

John, What is a High Velocity Heating System?  
Is that another name for Instant Heater.  
Thanks.

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [June 26, 2008, 4:18am UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/13 "2008-06-26T04:18:56Z")

</div>

Jack did you make that diagram.?

---

<div class="post-metadata">

**Author:** ![jgilleland](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jgilleland/32/1326_2.png) [@jgilleland](https://forum.nachi.org/u/jgilleland)\
**Post date:** [June 27, 2008, 5:13am UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/14 "2008-06-27T05:13:44Z")

</div>

No it came from one of takagi installation manuals.

---

<div class="post-metadata">

**Author:** ![thenderson2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/thenderson2/32/56880_2.png) [@thenderson2](https://forum.nachi.org/u/thenderson2)\
**Post date:** [September 19, 2014, 5:09pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/15 "2014-09-19T17:09:34Z")

</div>

[http://www.homedepot.com/p/Rheem-EcoSense-4-0-GPM-Max-Flow-Rate-240-Volt-13kw-Electric-Tankless-Water-Heater-RETE-13/202514583#specifications](http://www.homedepot.com/p/Rheem-EcoSense-4-0-GPM-Max-Flow-Rate-240-Volt-13kw-Electric-Tankless-Water-Heater-RETE-13/202514583#specifications)

This does not need a TPR valve right? or do all tankless need them…?

---

<div class="post-metadata">

**Author:** ![eschmidt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/eschmidt/32/89375_2.png) [@eschmidt](https://forum.nachi.org/u/eschmidt)\
**Post date:** [September 19, 2014, 6:35pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/16 "2014-09-19T18:35:23Z")

</div>

> [@jgilleland](#):
>
> John, What is a High Velocity Heating System?  
> Is that another name for Instant Heater.  
> Thanks.

Up here a high velocity heating system is forced air and heat exchangers, smaller ducts carry the same amount of air at higher pressure. They are making a come back, they were popular in commercial high rises once upon a time, but dropped because they were less efficient and more troublesome. Not sure why they are coming back now, except maybe everyone forgot?

> **[Energy Saving Products LTD.](https://www.hi-velocity.com/)**
>
> Hi-Velocity Mini duct heating and air conditioning indoor air quality systems.

> **[Seeking answers for home heating woes](https://www.ctvnews.ca/seeking-answers-for-home-heating-woes-1.776550)**
>
> W5 investigates cases where brand-new HVAC systems aren't working properly, with some homeowners finding that their homes are freezing on one floor and feeling tropical on another.

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [September 20, 2014, 4:09pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/17 "2014-09-20T16:09:26Z")

</div>

Agreed and even Mike Holmes knows that, as they did one show on this superb High Velocity System. Worth watching for sure.

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [September 20, 2014, 11:01pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/18 "2014-09-20T23:01:21Z")

</div>

> [@thenderson2](#):
>
> [http://www.homedepot.com/p/Rheem-EcoSense-4-0-GPM-Max-Flow-Rate-240-Volt-13kw-Electric-Tankless-Water-Heater-RETE-13/202514583#specifications](http://www.homedepot.com/p/Rheem-EcoSense-4-0-GPM-Max-Flow-Rate-240-Volt-13kw-Electric-Tankless-Water-Heater-RETE-13/202514583#specifications)
> 
> This does not need a TPR valve right? or do all tankless need them…?

Well I installed quite a few 100% Electric Tankless Water Heaters and never once put one on it. All were inspected and installed in accordance with the manufacturers instructions. The electric models move water based on turning on the faucet, the elements heat the water as they pass thought the chambers and no pressure was every in the unit…nothing to relieve so to speak.

So I would say not ALL need such a value…but I can only speak for the models (SETS) units.

---

<div class="post-metadata">

**Author:** ![kwood](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kwood/32/473_2.png) [@kwood](https://forum.nachi.org/u/kwood)\
**Post date:** [September 21, 2014, 9:18pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/19 "2014-09-21T21:18:08Z")

</div>

They only relieve pressure when they take a leak. Right Paul. LOL

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [September 22, 2014, 1:07pm UTC](https://forum.nachi.org/t/tankless-water-heater-and-pressure-relief-valve/29508/20 "2014-09-22T13:07:31Z")

</div>

> [@kwood](#):
>
> They only relieve pressure when they take a leak. Right Paul. LOL

Indeed!