the 65 degree question

Don’t have any literature but have a head full experience.

The proper term is called (liquid migration) which occurs during the off cycle of the unit. Liquid freon will seek the coldest area of an enclosed system between the furnace A-coil and the outside condensing unit. When outside ambients are below 60 degrees the MFG recommends not to operate these units because the coldest area of the system will be the outside unit and if liquid freon is lying in the compressor you can can damage the valves in the compressor when you start it up.

Freon is simply stated, all about pressure temperature relationship if the home or the area of the furnace A-coil is in a warmer area than the condensing unit the freon will migrate toward the coldest area in a shut down mode. Once the compressor is actually started and operated in a normal mode no damage will occur to the compressore the damage will occur on the initial starting of the unit.

If the outside unit is equipped with a crankcase heater the possibility of liquid migration is almost nil as the heat will drive the liquid freon from the crankcase

If this sounds like Greek I can try another approach.