THE RIGGED RECEPTACLE

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



THE RIGGED RECEPTACLE


![](upload://5jQ22GNiocc5k0A9go8tPDV6vcz.jpeg)

Quote:
Randy Barnett, senior instructor, American Trainco, Englewood, Colo., sent me this photo of what was left of a receptacle that was installed in a large Midwest hospital.

The maintenance technician, who brought the receptacle to one of Barnett's training classes, said after he plugged in his vacuum cleaner and turned it on, the receptacle immediately exploded!

Investigation by the hospital's electric shop revealed that the receptacle had been improperly connected to a 480V circuit.

Luckily for him the vacuum wasn't on when he plugged into the receptacle.

You might ask yourself, How could a 120V receptacle be wired into a 480V system?

During a recent remodeling project at the hospital, a contract electrician needed some temporary 480V power, so he rigged a 120V receptacle to get the job done.

One can only wonder how he modified the plug he was using at the time. When asked about the situation, he said he simply forgot to disconnect it after he was done with his project.

Aside from the fact that the installation violates the Code's requirements that prohibit the use of equipment for a purpose for which it's neither suitable nor listed (110.3), the issue raises questions about whether any such electrician could be considered qualified.


Food for thought, watch out for mixed and crossed voltages that could result in a similar hazard.


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



We had a similar situation when I was with IBM. Someone had wired a 5-15 to 277v.


The guy who plugged in the keypunch did have it on and it neatly melted the prongs off flush to the face of the plug.


I didn’t see the receptacle but I did see the wall afterward. There was a burn ring about a foot in diameter in the drywall. The guy had flash burns on his hand and skidmarks in his shorts.


Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



Thanks Greg, can we find a picture or sketch of the NEMA 5-15 configuration?


![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: phinsperger
This post was automatically imported from our archived forum.



While on the subject of outlets in hospitals, I have noticed that in different hospitals the outlets were all upside down (with the ground at the top). This went both for regular outlets as well as isolated ground outlets. Anybody know why?



.



Paul Hinsperger
Hinsperger Inspection Services
Chairman - NACHI Awards Committee
Place your Award Nominations
here !

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



Paul"


I believe that most Hospitals follow a recommendation found in their hospital standards, and that suggestion is UP for the ground pin, and in many cases for a good reasons when metal plates are used.

This subject has led to tears where grown men and women have wept trying to come up with a reasonable answer ... I will have some pictures and surprises during the Convention seminar I am scheduled to teach.

Search here for that information:

http://www.jcaho.org/


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Joe’s description of the battles over grounds up or down is very accurate. icon_lol.gif


All I will say is at present it is not covered directly in the NEC.

The company I work for has a policy of grounds up or neutrals up if the receptacle is horizontal.

We apply this in all new buildings, on remodels we follow what is already installed.


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: lfranklin
This post was automatically imported from our archived forum.



Well the rumors around here is that an industrial electrician will put the


ground pin up. While a residential electrician will put the ground pin down.


So I guess it depends on where their early training was.

Up or down I have no ideal


Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



I found a link that shows different configurations here including the NEMA 5-15


http://frentzandsons.com/Hardware%20References/plugandreceptacleconfiguratio.htm


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



This is another one


http://www.quail.com/nema.cfm


When they tracked down the problem with the outlet we had it turned out a "building electrician" (read:"janitor with a screwdriver") had tapped off the flourecent in the room for the new receptacle. I guess the grey/violet colors didn't spur any curiosity about what was going on the box. An 026 keypunch used a ferro-resonant power supply that tried to make that 277 be 120v and it looked like a bolted short.
The strange thing was it didn't hurt the keypunch. There was a blown fuse but that was the only problem ... beside the smoked plug cap.


Originally Posted By: phinsperger
This post was automatically imported from our archived forum.



My understanding is the main focus of the arugments around receptical orientan is that if the plug is half falling out and most commonly on a downward angle;


1) Ground up helps to protect objects (including fingers) from touching the hot. (in a sideways install put the neutral up)

vs.

2) Ground down so you don't loose ground protection with hot still energized. (in a sideways install put the neutal down)

My question is has there ever actually been a study to determine which is more likely to prevent injury?


--
.


Paul Hinsperger
Hinsperger Inspection Services
Chairman - NACHI Awards Committee
Place your Award Nominations
here !