Hi inspectors. I was thermal imaging my house and found these weird cold spots on the roof. The house has a cathedral style roof. They are evenly spaced and doesn’t look like moisture intrusion. I put my moisture meter and its dry. Some explanation will be appreciated. Thanks
What part of the roof structure do you think you are seeing and should not be there?
Not necessarily structure. I am just curious about these cold spots. Im thinking that they are rafter joints but wouldn’t roof rafters be one piece from ridge to tail?
Curious… what extent of professional training do you have with Thermal AND Building Science?
I dont have any training with thermals yet. Im familiar with basic building science but not an expert. So I figured i should ask people smarter than me.
You are seeing thermal bridging of the framing. My guess is that there is some kind of webbing or connection at the darker anomalies.
How old is the home? If built within the last 40 years, it’s a good likelihood they are TRUSSES and not Rafters… which makes all the difference, thus my question regarding your experience.
Here’s a photo of a (section) of a Vaulted ceiling / Cathedral Roof framing in progress.
Do you see anything that may be causing the ‘low temp differential’ you are observing?
And here’s a link to the video it was taken from. I recommend you watch this and many others to become familiar with what you need to be aware of while inspecting.
Note: On-line Videos are great for general information awareness, but in most cases DO NOT watch them in an attempt to gain specific DETAILS as they often contain more mistakes than you can ‘shake a stick at’!
Makes sense now. It could very well be trusses. House was built in 2002. There must me some sort of webbing at those cold spots. Thanks for the help
Metal gusset plate.
Next question, why do you think they produce a thermal anomaly?
Lower R value then insulation causing cold spots
I use thermal imaging occasionally on inspections, but don’t advertise it, or use it as a be all and end all. I don’t think it requires as much training as some think, but many people, especially inspectors (not usually on here), and many home owners think it’s a magic trick that finds water leaks or sees through walls. It does not, it measures or detects infrared radiation, or heat. That’s it. It’s also easily tricked by reflective materials. Water leaks take time to show up on a thermal imaging cameras, sometimes hours. In cases of water leaks it can find those through water evaporation. If the water is close to the temp on the inside of the home it may not show up at all. I’m over simplifying, but that’s the gist of it. I basically use it as an aid, or a tool to confirm what I’m already seeing or aware of. If that makes sense.
Yep, that sort of explains the thermal bridging. The theory is we have trusses with metal gussets. What about the cold spots at the joints?
Have you been through the training? Say level 1?
It could be related to how the insulation is laid around the truss structure
Yes I have. And I believe it’s helpful. But for home inspections idk. But again much of that is covered in level 1 which now that I’m saying, and in the case of this thread I think it’s necessary. But if you can grasp what a thermal imaging camera does, and its limitations, idk. Clearly a lot of people can’t, in which case I’ll go back on what I said and say that yes, everyone should have training. Maybe I’m overestimating people in thinking that it’s not very complicated.
Do you have the answers to the questions I am asking the OP? I ask this because not understanding the science can lead to misinterpretation. It is not a criticism of anyone.
And I agree, qualitative is far different from quantitative, but even qualitative scans can lead to issues. For example, whipping this thing out on an electrical panel has likely caused more problems than it has ever solved, based on what I see on this MB.
Do yourself a favor and don’t use thermal cameras on inspections until you do get some training. Your insurance provider with thank you for it. . . . .AND . . . . Good answer to JJ’s question. The only way to learn is to ask, right??
First off, that is a ceiling, not a roof. This is one of those occasions where words matter.
Secondly, it has been mentioned by others that these areas are likely where there are truss plates. I agree 100%. The fact that there is a consistent pattern covering the ceiling is the giveaway in this instance.
Typically truss plates don’t wrap around the bottom edge, but in your case they probably do, at least in part. This is why they are so predominantly visible. Since the steel can conduct heat energy better than wood and both the wood truss and steel plates are in direct contact with the drywall, these “cold spots” are what you will see while thermal bridging is taking place when the attic space is cold, the living space is warm, and there is enough temperature differential for the camera to see it. Do this again in the heat of the summer and you just might see warm spots in the same areas.
When you see “cold spots” such as this, don’t immediately think to yourself “I have to throw a moisture meter at those spots”. Just because a thermal camera shows a cold or cool spot, doesn’t mean it is necessarily wet, especially if there is a pattern that repeats across an entire room. Look at what the weather has been doing first. If it hasn’t rained or snowed in let’s say 12 weeks, it’s been warm during the day, cool at night, the relative humidity has been relatively stable, and the entire roof structure has been dry for that 12 weeks, what do you suppose that moisture meter is going to tell you?
The issue is that when there is metal behind or in direct contact with the drywall, moisture meters can get confused and will think the metal is water, giving you false readings. Sometimes you get lucky and the meter will give you at least a close to accurate reading, but more often than not it will be wrong in this situation.
I definitely agree there.
Here’s a Tip to help in this scenario:
When your Moisture Meter reads “No Moisture Present”, but your Thermal indicates a target is present… use a strong magnet or stud finder to detect if metal is present. Remember that Aluminum, Copper, Lead (and some others not likely found in a homes construction) are not magnetic, so this trick should only be used to help eliminate or enforce the information gleaned with your other observations.
That being said, you are (typically) not being hired or paid to diagnose any issue, only to discover and report what you do observe!