# This has to be wrong, right?

**URL:** <https://forum.nachi.org/t/this-has-to-be-wrong-right/79390>\
**Category:** Electrical Inspections\
**Created:** [July 15, 2013, 12:01am UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390 "2013-07-15T00:01:31Z")\
**Posts on this page:** 16\
**Page:** 1

<div class="post-metadata">

**Author:** ![slagueux](https://avatars.discourse-cdn.com/v4/letter/s/b9bd4f/32.png) [@slagueux](https://forum.nachi.org/u/slagueux)\
**Post date:** [July 15, 2013, 12:01am UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/1 "2013-07-15T00:01:31Z")

</div>

Duplex, one 200 amp service entrance, the other 100 amp.

Both service disconect bonded together. That can’t be right, right?

Oh by the way, yes on the 3rd and 4th pic. those are hanging live wires. I almost craped my pants when I saw that.

 ![IMGP1214.jpg](https://global.discourse-cdn.com/internachi/original/2X/5/51d9fe7c9a465ca6f213c0a09df80d6c2958f5ae.jpeg)

 ![IMGP1213.jpg](https://global.discourse-cdn.com/internachi/original/2X/4/49f55af514d4830b0882c582384159069b7787e0.jpeg)

 ![IMGP1208.jpg](https://global.discourse-cdn.com/internachi/original/2X/9/94f1c8cb83e5d03f135c12ec5559aeb0cfd23335.jpeg)

 ![IMGP1207.jpg](https://global.discourse-cdn.com/internachi/original/2X/c/c998e92a6272abd554ac760c40e4b7802f3ec3d4.jpeg)

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [July 15, 2013, 2:35pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/2 "2013-07-15T14:35:21Z")

</div>

Are the split bolts on the GEC? The pics are too small to see any details.

---

<div class="post-metadata">

**Author:** ![slagueux](https://avatars.discourse-cdn.com/v4/letter/s/b9bd4f/32.png) [@slagueux](https://forum.nachi.org/u/slagueux)\
**Post date:** [July 15, 2013, 2:58pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/3 "2013-07-15T14:58:30Z")

</div>

the splice is actually on the gounding electrode conductor. The electrician bonded the second service disconect to it thinking that would provide correct grounding. What he did is he merged the first 200 amp service to the second 100 amp making this a dangerous situation imo.

If you click on those pics, won’t they open?

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [July 15, 2013, 3:01pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/4 "2013-07-15T15:01:04Z")

</div>

They open for me.

---

<div class="post-metadata">

**Author:** ![kbrittain](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kbrittain/32/59414_2.png) [@kbrittain](https://forum.nachi.org/u/kbrittain)\
**Post date:** [July 15, 2013, 5:14pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/5 "2013-07-15T17:14:11Z")

</div>

The live hanging wires is enough by itself to disclaim the system and refer it to a licensed electrican

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [July 15, 2013, 6:32pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/6 "2013-07-15T18:32:01Z")

</div>

> [@slagueux](#):
>
> the splice is actually on the gounding electrode conductor. The electrician bonded the second service disconect to it thinking that would provide correct grounding. What he did is he merged the first 200 amp service to the second 100 amp making this a dangerous situation?

No it is not dangerous and is required to be bonded to the GEC.

---

<div class="post-metadata">

**Author:** ![slagueux](https://avatars.discourse-cdn.com/v4/letter/s/b9bd4f/32.png) [@slagueux](https://forum.nachi.org/u/slagueux)\
**Post date:** [July 15, 2013, 7:26pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/7 "2013-07-15T19:26:28Z")

</div>

> [@Jim\_Port](#):
>
> No it is not dangerous and is required to be bonded to the GEC.

I understand that equipments need to be bonded.

So in that case, would’nt both service disconect require their own separate GEC?

What if one has to be turned off for electrical work in one of the appartment. Could’nt it still get energized via the second service entrance if there is an over-voltage surge comming from this one, could it?

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [July 15, 2013, 7:55pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/8 "2013-07-15T19:55:44Z")

</div>

Aluminum and copper under same lug is a No. Also lug appears to only be rated for One conductor.  
[http://www.nachi.org/forum/attachments/f19/66862d1373846378t-has-wrong-right-imgp1213.jpg](http://www.nachi.org/forum/attachments/f19/66862d1373846378-has-wrong-right-imgp1213.jpg)

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [July 15, 2013, 8:00pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/9 "2013-07-15T20:00:49Z")

</div>

> [@](#):
>
> Duplex, one 200 amp service entrance, the other 100 amp.

Also, are there two separate meters, two separate sets of service entrance cables feeding individual service disconnects?

---

<div class="post-metadata">

**Author:** ![slagueux](https://avatars.discourse-cdn.com/v4/letter/s/b9bd4f/32.png) [@slagueux](https://forum.nachi.org/u/slagueux)\
**Post date:** [July 15, 2013, 8:08pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/10 "2013-07-15T20:08:18Z")

</div>

> [@ccurrins](#):
>
> Also, are there two separate meters, two separate sets of service entrance cables feeding individual service disconnects?

Yes, 2 meters. 2 distinct service entrances

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [July 15, 2013, 8:42pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/11 "2013-07-15T20:42:43Z")

</div>

How would a ground going to a rod energize a panel?

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [July 15, 2013, 8:43pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/12 "2013-07-15T20:43:58Z")

</div>

> [@ccurrins](#):
>
> Aluminum and copper under same lug is a No. Also lug appears to only be rated for One conductor.  
> [http://www.nachi.org/forum/attachments/f19/66862d1373846378t-has-wrong-right-imgp1213.jpg](http://www.nachi.org/forum/attachments/f19/66862d1373846378-has-wrong-right-imgp1213.jpg)

Are you sure that’s aluminum? Looks like old tinned copper from the insulation.

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [July 15, 2013, 8:44pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/13 "2013-07-15T20:44:23Z")

</div>

> [@ccurrins](#):
>
> Aluminum and copper under same lug is a No. Also lug appears to only be rated for One conductor.  
> [http://www.nachi.org/forum/attachments/f19/66862d1373846378t-has-wrong-right-imgp1213.jpg](http://www.nachi.org/forum/attachments/f19/66862d1373846378-has-wrong-right-imgp1213.jpg)

Those are not lugs. They are split bolts.

You can have one GEC system for two services.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [July 15, 2013, 9:11pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/14 "2013-07-15T21:11:46Z")

</div>

> [@Jim\_Port](#):
>
> Those are not lugs. They are split bolts.
> 
> You can have one GEC system for two services.

I agree and taps to the GEC are not required to be irreversible so split bolts are permitted.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [July 15, 2013, 9:14pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/15 "2013-07-15T21:14:42Z")

</div>

> [@Robert\_Meier](#):
>
> Are you sure that’s aluminum? Looks like old tinned copper from the insulation.

You’re correct it is tinned copper. I didn’t look close enough (blow up picture) first time.

---

<div class="post-metadata">

**Author:** ![slagueux](https://avatars.discourse-cdn.com/v4/letter/s/b9bd4f/32.png) [@slagueux](https://forum.nachi.org/u/slagueux)\
**Post date:** [July 15, 2013, 10:49pm UTC](https://forum.nachi.org/t/this-has-to-be-wrong-right/79390/16 "2013-07-15T22:49:19Z")

</div>

Thanks for all your inputs guys, I’ll go to bed tonight a little _brighter_…