I know this receptacles is fine for a kitchen, but not on the exterior. But I had to laugh when I pulled it in my kitchen.
If it is installed in a waterproof box with a wet location cover, is it still in a wet location?
Yes it is still not allowed. Exterior GFCI must be (WR) weather-resistant. And they usually have that mark on them. But do any inspectors actually check that? I know I don’t. I think realtors will think we are nit picking if we reported them.
Here is what the code says
NEC Section 406.8 (often 406.9 in newer editions) dictates that 15 and 20A, 125/250V receptacles in damp or wet locations must be weather-resistant (marked “WR”) and protected by specific covers. Wet locations require a “bubble” cover that stays weatherproof while a plug is in use, while damp locations only require a cover when not in use.
So, why did you laugh? What is funny?
Well because I know that 90% of outdoor GFCI’s are not rated for wet locations. And that a kitchen can be a wet location as well.
The difference between WR GFCI and regular GFCI is the WR have the contacts and mounting straps nickel plated and use stainless steel mounting screws. I believe the plastic may also have some UV protection. I don’t call out out exterior GFCI that are not WR. I will just note that when replacing use WR type. Regardless, I find the most failed GFCI’s of both types, outdoors.
During a flood the whole house can be a wet location. Nothing funny about that. No NEC coverage either.
We are NOT code inspectors. You will not know if the outlet is ‘weatherproof’ or not without disassembly. Since you brought it up, explain the exception.
406.8(B)(1)
All 15- and 20-ampere, 125- and 250-volt nonlocking receptacles
shall be listed weather-resistant type.
- FPN: The types of receptacles covered by this requirement
- are identified as 5-15, 5-20, 6-15, and 6-20 in ANSI/NEMA
- WD 6-2002, National Electrical Manufacturers Association
- Standard for Dimensions of Attachment Plugs and
- Receptacles.]
Exception: 15- and 20-ampere, 125- through 250-volt receptacles
installed in a wet location and subject to routine
high-pressure spray washing shall be permitted to have an
enclosure that is weatherproof when the attachment plug is
removed
Effective Jan. 1, 2011
https://www.ecmag.com/magazine/articles/article-detail/miscellaneous-2008-nec-proposals
I think that the sticker is a good idea. It might keep the sparky from installing this in a wet location and then have to fix the violation after inspection. As noted these receptacles are fine is dwelling kitchens (or bathrooms) which are by NEC definition dry locations.
The homeowner or handyman is still going to buy and install whichever receptacle is cheaper.
They should come with a sticker for the electricians!
That includes installing non-TR receptacles, like the ones in the above post.
That were always a bad idea and no substitute for parental supervision and discipline. I simply can’t imagine how so many people survived before the ‘nanny’ state took over.
It’s another thing that has so far escaped local enforcement. Are other AHJ’s enforcing this?