# Tiny service entrance question

**URL:** <https://forum.nachi.org/t/tiny-service-entrance-question/59655>\
**Category:** Electrical Inspections\
**Created:** [May 27, 2011, 2:52pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655 "2011-05-27T14:52:50Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [May 27, 2011, 2:52pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/1 "2011-05-27T14:52:50Z")

</div>

Anyone ever seen anything like this? The neutral at the service mast is spliced to a tiny, solid (perhaps size six or eight) conductor from the utility line. This is the smallest neutral I’ve ever seen. Don’t recall ever seeing a splice like this.

 ![052611 027.jpg](https://global.discourse-cdn.com/internachi/original/2X/d/df96e767a1bf5ad0029a85910016c87c75960f23.jpeg)

---

<div class="post-metadata">

**Author:** ![Brian\_A.MacNeish](https://avatars.discourse-cdn.com/v4/letter/b/90db22/32.png) [@Brian\_A.MacNeish](https://forum.nachi.org/u/Brian_A.MacNeish)\
**Post date:** [May 27, 2011, 3:19pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/2 "2011-05-27T15:19:41Z")

</div>

> [@jfunderburk](#):
>
> Anyone ever seen anything like this? The neutral at the service mast is spliced to a tiny, solid (perhaps size six or eight) conductor from the utility line. This is the smallest neutral I’ve ever seen. Don’t recall ever seeing a splice like this.
> 
> ![052611 027.jpg](https://global.discourse-cdn.com/internachi/original/2X/d/df96e767a1bf5ad0029a85910016c87c75960f23.jpeg)

Canadian:

**Size of neutral conductor**

\*\*(1) \*\*The size of the neutral conductor shall have sufficient ampacity to carry the unbalanced load

\*\*(3) \*\*The size of the service neutral shall not be smaller than the size of a neutral selected in accordance in subrule (1) and shall not be smaller than:  
**(a)** #10 AWG copper or #8 AWG aluminum

---

<div class="post-metadata">

**Author:** ![jbraun](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jbraun/32/536_2.png) [@jbraun](https://forum.nachi.org/u/jbraun)\
**Post date:** [May 27, 2011, 3:27pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/3 "2011-05-27T15:27:33Z")

</div>

A local line worker once told me the current standard is the neutral cannot be no smaller than the power.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [May 27, 2011, 3:53pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/4 "2011-05-27T15:53:42Z")

</div>

Given the fact that it hasn’t burnt up I’m guessing that the size isn’t a problem. Could have been left over from an old 30 amp service that was upgraded at some point.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [May 27, 2011, 4:22pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/5 "2011-05-27T16:22:52Z")

</div>

Just have it evaluated when the lack of a drip loop gets corrected.

---

<div class="post-metadata">

**Author:** ![jpope](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jpope/32/59425_2.png) [@jpope](https://forum.nachi.org/u/jpope)\
**Post date:** [May 27, 2011, 4:44pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/6 "2011-05-27T16:44:31Z")

</div>

Utility companies pretty much get to do what they want, and they get to make the call here. It’s an open-air conductor and probably capable of carrying more load than would ever be necessary.

---

<div class="post-metadata">

**Author:** ![Brian\_A.MacNeish](https://avatars.discourse-cdn.com/v4/letter/b/90db22/32.png) [@Brian\_A.MacNeish](https://forum.nachi.org/u/Brian_A.MacNeish)\
**Post date:** [May 27, 2011, 7:04pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/7 "2011-05-27T19:04:24Z")

</div>

> [@jbraun](#):
>
> A local line worker once told me the current standard is the neutral cannot be no smaller than the power (???).

Please explain what “the power” is?

---

<div class="post-metadata">

**Author:** ![Brian\_A.MacNeish](https://avatars.discourse-cdn.com/v4/letter/b/90db22/32.png) [@Brian\_A.MacNeish](https://forum.nachi.org/u/Brian_A.MacNeish)\
**Post date:** [May 27, 2011, 7:05pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/8 "2011-05-27T19:05:40Z")

</div>

The NEC not have a rule on the neutral conductor size??

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [May 28, 2011, 12:45pm UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/9 "2011-05-28T12:45:06Z")

</div>

> [@Brian\_A.MacNeish](#):
>
> The NEC not have a rule on the neutral conductor size??

There are several. However, the service drop conductors in this photo would not fall under the purview of the NEC.

---

<div class="post-metadata">

**Author:** ![agallatin](https://avatars.discourse-cdn.com/v4/letter/a/91b2a8/32.png) [@agallatin](https://forum.nachi.org/u/agallatin)\
**Post date:** [May 30, 2011, 2:49am UTC](https://forum.nachi.org/t/tiny-service-entrance-question/59655/10 "2011-05-30T02:49:34Z")

</div>

Jeffrey is correct . The electrical companies make their own rules . Here the codes starts after the meter .:D:D:D