TPR and flush valve on T

Actualy I was thinking galv to copper .

…if so needs the dielectric connector to prevent electrolysis corrosion.

Agreed. . .

I wouldn’t be concerned about that with this type of application. . .

True …as it is more of a concern on a water supply pipe,which is why I thought nothing of it when looking.

Here is a brightened picture of the other setup.

One purpose for the air gap is to keep the end open where it can be noticed if the TPRV opens, to make the HO aware of a possible safety issue that needs to be looked at. BTW the IPC code allows the drain to end at the WH drain pan. MY Code Check book is out in the truck, else I would provide you with some numbers. If you don’t have them by tommorrow, I will send them to you. Also, if the WH is below grade, they need to install a Watts 210, because the pipe is not allowed to run uphill. You may want to inform them that a WH can build up pressure equal to 200 sticks of Dynamite and can obliterate a house and it’s contents, not to mention the occupants. I do not test the TPRV, but if you do, be aware that it sometimes will take up to 15 minutes to reseal properly.

How about to the AC condensate line?

post 9 item 4 has the answer

Mark…read post #3, especially the bold words. That is straight out of the IRC. So, no not even the a/c condensate can share the TPRV drain piping.

No. Needs to be on its own, to see if it’s discharging.

Bob,

See http://www.ilga.gov/commission/jcar/admincode/077/077008900I12300R.html

and

http://www.ilga.gov/commission/jcar/admincode/077/07700890ZZ9996hfR.html

The first link says 6" though that can be interpreted to minimum.
The graphic shows 4"
Also Chicago can be different, but I think it is safe to say we were right about needing a gap.

The first was directly related to TPRV, second for air gaps for cross connections.

Either way, Chicago is not necessarily Illinois. :shock::wink:

Suprised the mayor hasn’t hit y’all up for a city fee for inspections. :twisted:

-X Sheeeeeesh…He might hear you.

That just about says it all in one neat tidy package.
T.Neyedli
www.alphahomeinspections.ca