The following is specific to Florida, although the FBC is pretty much a direct copy of the IRC. Truth be known, the FBC is actually falling behind the IRC but that’s another topic for another time.
The issue we have here is not reading the entire code when it comes to T & P line piping, I have had this discussion with many code officials and inspectors and most get it wrong. The FBC has always stated that in cases where there is conflict within a code, that the most stringent shall apply. In the case of T & P line piping, you have to understand that the code states the manufacturer’s specifications shall take precedence unless the code is more restrictive, in which case the code would take precedence. Watts is one of the more common T & P manufacturer’s I run into, I have contacted them to inquire about there recommendations for the piping and they stated either “polypropylene or copper” was what they approved. I believe that’s what their lines are made of, the side mount line is poly and the topside mount line is brass.
That being said, the code reference goes like this(using residential):
***2010 Florida Building Code, Residential 102.1 General.
**Where there is a conflict between a general requirement and a specific requirement, the specific requirement shall be applicable. Where, in any specific case, different sections of this code specify different materials, methods of construction or other requirements, the most restrictive shall govern. *
*2010 Florida Building Code, Residential M2005.1 General.
Water heaters shall be installed in accordance with the manufacturer’s installation instructions and the requirements of this code. Water heaters installed in an attic shall conform to the requirements of Section M1305.1.3. Gas-fired water heaters shall conform to the requirements in Chapter 24. Domestic electric water heaters shall conform to UL 174 or UL 1453. Commercial electric water heaters shall conform to UL 1453. Oiled-fired water heaters shall conform to UL 732. *
*P2803.5 Combination *pressure-/temperature-relief valves. **
Combination pressure-/temperature-relief valves shall comply with all the requirements for separate pressure- and temperature-relief valves.
*P2803.6.1 ****Requirements for discharge pipe. **
The discharge piping serving a pressure-relief valve, temperature relief valve or combination valve shall: *
13. Be constructed of those materials listed in Section P2904.5 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.
The manufacturer installation instructions are in clear conflict with the code as most require the piping to meet 250 degrees without distortion. Also, the code is in conflict with itself over what is required. ASME A112.4.1 is not a schedule of approved piping, but a schedule of temperature pressure type ratings for specific piping. ASME A112.4.1 being the more stringent application, the piping must meet the requirements of the manufacturer specifications both of the vale and water heater. In which case the line must be metallic and capable of handling temperatures at 250 degrees.