# TV for the Bath Tub?

**URL:** <https://forum.nachi.org/t/tv-for-the-bath-tub/56083>\
**Category:** Electrical Inspections\
**Created:** [January 27, 2011, 3:15am UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083 "2011-01-27T03:15:15Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![wcole](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcole/32/59521_2.png) [@wcole](https://forum.nachi.org/u/wcole)\
**Post date:** [January 27, 2011, 3:15am UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/1 "2011-01-27T03:15:15Z")

</div>

I ran across this today and would like to get some feedback. First picture is the outlet and the second is a whirlpool tub below the outlet/shelf. I am thinking about writing it up as being unsafe and advising my client to have it removed. It is a GFCI outlet. Thoughts???

 ![DSCI0100.jpg](https://global.discourse-cdn.com/internachi/original/3X/b/9/b9a5da78d743bd62d8f7a6eeef7f2b324bf3780d.jpeg)

 ![DSCI0099.jpg](https://global.discourse-cdn.com/internachi/original/3X/1/d/1dbf23383bcf837f6e6b59c06ad989ac939aa03b.jpeg)

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [January 27, 2011, 3:22am UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/2 "2011-01-27T03:22:12Z")

</div>

It is outside the tub line ?

No shower,do you have more of a broad shot to get a sense of perspective as the tub looks so small in that shot.

---

<div class="post-metadata">

**Author:** ![wcole](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcole/32/59521_2.png) [@wcole](https://forum.nachi.org/u/wcole)\
**Post date:** [January 27, 2011, 3:28am UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/3 "2011-01-27T03:28:31Z")

</div>

I do not have another shot but you are right. It is a small tub for the area. I might want to just advise my client to watch what he puts on the shelf and make sure it is secured.

---

<div class="post-metadata">

**Author:** ![jbuckley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jbuckley/32/172460_2.png) [@jbuckley](https://forum.nachi.org/u/jbuckley)\
**Post date:** [January 27, 2011, 3:34am UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/4 "2011-01-27T03:34:26Z")

</div>

I would advise on the potential hazard, especially if or when the GFCI fails to work. Let them know it may also fail the CO inspection and need to be removed.

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [January 27, 2011, 4:32am UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/5 "2011-01-27T04:32:28Z")

</div>

Looking at it again it is within what would be considered the tub space.  
I would call it out even if it is cool.No TV wall mount even means sitting it on the wet pedestal .

---

<div class="post-metadata">

**Author:** ![rstrand](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rstrand/32/235_2.png) [@rstrand](https://forum.nachi.org/u/rstrand)\
**Post date:** [January 27, 2011, 5:54am UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/6 "2011-01-27T05:54:59Z")

</div>

You can stand in a tub full of water and are able to touch the receptacle???

Hmmmm…

---

<div class="post-metadata">

**Author:** ![wcole](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcole/32/59521_2.png) [@wcole](https://forum.nachi.org/u/wcole)\
**Post date:** [January 27, 2011, 12:56pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/7 "2011-01-27T12:56:32Z")

</div>

I am going to call it out as being unsafe to cover my butt and not “fry” his. Thanks for the responses!

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [January 27, 2011, 12:57pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/8 "2011-01-27T12:57:26Z")

</div>

There are 12v TV available for this application powered from a wall pack.

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [January 27, 2011, 2:29pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/9 "2011-01-27T14:29:47Z")

</div>

> [@rstrand](#):
>
> You can stand in a tub full of water and are able to touch the receptacle???
> 
> Hmmmm…

Can you run your hand under a sink faucet and touch a counter-top receptacle?

Can you stand on a wet patio floor and touch a receptacle?

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [January 27, 2011, 2:32pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/10 "2011-01-27T14:32:14Z")

</div>

As there is no shower present, I don’t see any particular hazard present if the outlet is GFCI protected. There is no code that prohibits that particular use.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [January 27, 2011, 7:38pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/11 "2011-01-27T19:38:23Z")

</div>

> [@jfunderburk](#):
>
> As there is no shower present, I don’t see any particular hazard present if the outlet is GFCI protected. There is no code that prohibits that particular use.

What about this:

> [@](#):
>
> 406.8 Receptacles in Damp or Wet Locations.  
> (B) Wet Locations.  
> (1) 15- and 20-Ampere Receptacles in a Wet Location. 15- and 20-ampere, 125- and 250-volt receptacles installed in a wet location shall have an enclosure that is weatherproof whether or not the attachment plug cap is inserted. All 15- and 20-ampere, 125- and 250-volt nonlocking receptacles shall be listed weather-resistant type.  
> FPN: The types of receptacles covered by this requirement are identified as 5-15, 5-20, 6-15, and 6-20 in ANSI/NEMA WD 6-2002, National Electrical Manufacturers Association Standard for Dimensions of Attachment Plugs and Receptacles.]  
> Exception: 15- and 20-ampere, 125- through 250-volt receptacles installed in a wet location and subject to routine high-pressure spray washing shall be permitted to have an enclosure that is weatherproof when the attachment plug is removed.  
> (2) Other Receptacles. All other receptacles installed in a wet location shall comply with (B)(2)(a) or (B)(2)(b).  
> (a) A receptacle installed in a wet location, where the product intended to be plugged into it is not attended while in use, shall have an enclosure that is weatherproof with the attachment plug cap inserted or removed.  
> (b) A receptacle installed in a wet location where the product intended to be plugged into it will be attended while in use (e.g., portable tools) shall have an enclosure that is weatherproof when the attachment plug is removed.\*\*  
> (C) Bathtub and Shower Space. Receptacles shall not be installed within or directly over a bathtub or shower stall.\*\*

---

<div class="post-metadata">

**Author:** ![jfunderburk](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jfunderburk/32/187920_2.png) [@jfunderburk](https://forum.nachi.org/u/jfunderburk)\
**Post date:** [January 27, 2011, 7:50pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/12 "2011-01-27T19:50:49Z")

</div>

> [@Robert\_Meier](#):
>
> What about this:**(C) Bathtub and Shower Space. Receptacles shall not be installed within or directly over a bathtub or shower stall.**

I searched the IRC (it’s not there) and neglected the NEC. Thanks for the correction.

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [January 27, 2011, 8:07pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/13 "2011-01-27T20:07:25Z")

</div>

Grey area as the receptacle is not installed directly over the tub.

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [January 27, 2011, 8:11pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/14 "2011-01-27T20:11:07Z")

</div>

> [@mlarson](#):
>
> Grey area as the receptacle is not installed directly over the tub.

No ,but it is in the tub zone.

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [January 27, 2011, 8:12pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/15 "2011-01-27T20:12:19Z")

</div>

> [@belliott](#):
>
> No ,but it is in the tub zone.

Are you sure?

It is not in the tub footprint.

---

<div class="post-metadata">

**Author:** ![belliott](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/belliott/32/57038_2.png) [@belliott](https://forum.nachi.org/u/belliott)\
**Post date:** [January 27, 2011, 9:37pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/16 "2011-01-27T21:37:45Z")

</div>

> [@mlarson](#):
>
> Are you sure?
> 
> It is not in the tub footprint.

By tub zone I am referring to an area dedicated to the tub.  
A bigger picture would have provided proper perspective.

---

<div class="post-metadata">

**Author:** ![rstrand](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rstrand/32/235_2.png) [@rstrand](https://forum.nachi.org/u/rstrand)\
**Post date:** [January 27, 2011, 9:52pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/17 "2011-01-27T21:52:34Z")

</div>

My criteria is this;

Is it safe enough for my own family? Would I leave my child in this tub while I went to grab a clean towel? I really could care less what any code reference says, I would advise my client of the potential danger and recommend removal.

Just my opinion.

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [January 27, 2011, 10:50pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/18 "2011-01-27T22:50:50Z")

</div>

It is no different than having a receptacle over a sink counter next to the tub IMHO.

Since this is not a shower and the area is not subject to spray, I fail to see a safety real hazard.

IMHO of course.

It would be stupid to put any line powered device on that shelf as it is an accident waiting to happen even though the GFCI would prevent serious injury.

---

<div class="post-metadata">

**Author:** ![wcole](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/wcole/32/59521_2.png) [@wcole](https://forum.nachi.org/u/wcole)\
**Post date:** [January 27, 2011, 10:58pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/19 "2011-01-27T22:58:46Z")

</div>

My statement:  
In my opinion the outlet should be removed as a safety precaution. The close proximity to the tub could lead to a possible electrocution.

---

<div class="post-metadata">

**Author:** ![mlarson](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mlarson/32/89225_2.png) [@mlarson](https://forum.nachi.org/u/mlarson)\
**Post date:** [January 27, 2011, 11:20pm UTC](https://forum.nachi.org/t/tv-for-the-bath-tub/56083/20 "2011-01-27T23:20:42Z")

</div>

> [@wcole](#):
>
> My statement:  
> In my opinion the outlet should be removed as a safety precaution. The close proximity to the tub could lead to a possible electrocution.

And if your client asks you:

Isn’t that what the GFCI is for?

The fact of the matter is that there are differences of opinion on this very issue an AHJs will not all agree.

It is fine to offer your opinion or mine but it is also important to understand that neither is not definitive.

Good luck.