Typical Sagging Support Beam Repair Plan
Attached is a PDF drawing for reference is a typical repair plan for a crawlspace beam where the seven interior piers have settled over the past 20 years. The beam and I-joists were in good condition but needed to be jacked up, with non-compressible shims inserted above the 6x6 support posts. The house has several drywall cracks, including some of the typical diagonal drywall cracks at interior doors.
The method used to determine the existing sag involved setting my Hilti laser level a few inches below the beam and assigning an elevation of 100 feet to the laser line. I noted the length and width of the rectangular foundation and observed that the beam was placed in the center. I measured the distance between the laser line and the bottom of the beam at each pier, at the center of each span, and at the beam pockets at each end of the beam. Using an Excel spreadsheet, I plotted the distance and elevation of each measurement. It’s not uncommon for each end of the beam to have a different elevation due to construction errors or uneven foundation settlement. In this case, the west end of the beam was 1/4" lower. This is important because if you jack the beam to be perfectly level, the beam at the west end would be 1/4" too high. The solution is to leave the beam ends where they are, as long as the beam is not damaged. To compensate for the west end being 1/4" lower, I plotted a straight line from both beam pockets and raised the beam to meet this red dashed line.
I also added general notes for the contractor, showing the amount of adjustment needed at each pier. I informed them, especially if they have never jacked up a beam before, that new drywall cracks will likely occur and to include repairing them in their bid.
PLAN SHEET.pdf (387.0 KB)
Thank you for the explanation and pdf.