# Un-grounded wiring with three prong outlets

**URL:** <https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395>\
**Category:** Electrical Inspections\
**Created:** [January 26, 2016, 8:32pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395 "2016-01-26T20:32:17Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![cfullmer](https://avatars.discourse-cdn.com/v4/letter/c/9de053/32.png) [@cfullmer](https://forum.nachi.org/u/cfullmer)\
**Post date:** [January 26, 2016, 8:32pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/1 "2016-01-26T20:32:17Z")

</div>

Hello all.  
I’m an inspector in Utah and my boss and I have a question about un-grounded wire with three prong outlets. I am aware that according to code you can not put them on un-grounded wire. But we all know that happens anyway. We had a client today say that the inspector that inspected the home that they are selling either wants them to re-wire the house or to put in two prong outlets.

Is it really that much of a difference when it comes to the shock hazard to have two prong instead of three? Because of the lack of grounding wire it’s still going to shock the same correct? I can see how people assume it has a grounding wire when they see the three prong outlet and that’s why it’s against code.

I guess I’m just looking for other opinions. Usually the way we handle it is inform the client that it is un-grounded so that they are aware of the safety risk that it has. And not really make a big deal about changing the outlet back to two prong. What is your opinion and how do you handle this when you see it?

Looking forward to your responses an thank you in advance.

Cameron Fullmer, Alliance Inspection Services.

---

<div class="post-metadata">

**Author:** ![jolson8](https://avatars.discourse-cdn.com/v4/letter/j/a88e57/32.png) [@jolson8](https://forum.nachi.org/u/jolson8)\
**Post date:** [January 26, 2016, 8:51pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/2 "2016-01-26T20:51:22Z")

</div>

[FONT=Times New Roman][size=2]There are three ways to repair an ungrounded 3-slot receptacle, listed below from most-expensive to least-expensive: 1) Install a ground connection to the receptacle, typically done by running a ground wire to the receptacle, which can be difficult to accomplish. 2) Change out the receptacle for a GFCI-receptacle. GFCI stands for Ground Fault Circuit Interrupter. Essentially, if there is a ground fault (you are being shocked), the circuit is interrupted (shut off to prevent your death). The receptacle should be marked with a sticker, which comes in the box with the receptacle, stating “NO GROUND CONNECTION.” The reason is that some appliances, such as televisions and computers, require a ground connection to work properly and should not be connected to an ungrounded GFCI-receptacle. Also, surge protection devices do not function properly without a ground connection. 3)And last, the cheapest remedy is to change the offending receptacles back to 2-slot, which are still available at most hardware stores.  
[/size][/FONT]

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [January 26, 2016, 9:05pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/3 "2016-01-26T21:05:55Z")

</div>

> [@jolson8](#):
>
> [FONT=Times New Roman][size=2]There are three ways to repair an ungrounded 3-slot receptacle, listed below from most-expensive to least-expensive: 1) Install a ground connection to the receptacle, typically done by running a ground wire to the receptacle, which can be difficult to accomplish. 2) Change out the receptacle for a GFCI-receptacle. GFCI stands for Ground Fault Circuit Interrupter. Essentially, if there is a ground fault (you are being shocked), the circuit is interrupted (shut off to prevent your death). The receptacle should be marked with a sticker, which comes in the box with the receptacle, stating “NO GROUND CONNECTION.” The reason is that some appliances, such as televisions and computers, require a ground connection to work properly and should not be connected to an ungrounded GFCI-receptacle. Also, surge protection devices do not function properly without a ground connection. 3)And last, the cheapest remedy is to change the offending receptacles back to 2-slot, which are still available at most hardware stores. [/size][/FONT]

You forgot the "Harry Homeowner method…

 ![](https://global.discourse-cdn.com/internachi/original/3X/7/b/7bd3caaab8a07a8234d0f800fe64a53ae6c6c620.jpeg)

---

<div class="post-metadata">

**Author:** ![bgrant](https://avatars.discourse-cdn.com/v4/letter/b/49beb7/32.png) [@bgrant](https://forum.nachi.org/u/bgrant)\
**Post date:** [January 27, 2016, 1:06am UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/4 "2016-01-27T01:06:53Z")

</div>

Send this with report.

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [January 27, 2016, 1:52am UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/5 "2016-01-27T01:52:37Z")

</div>

The NEC allows 3 prong receptacles on ungrounded wiring if they are gfi protected.

---

<div class="post-metadata">

**Author:** ![mbitterman](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mbitterman/32/58274_2.png) [@mbitterman](https://forum.nachi.org/u/mbitterman)\
**Post date:** [January 28, 2016, 3:40am UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/6 "2016-01-28T03:40:24Z")

</div>

> [@jjonas](#):
>
> You forgot the "Harry Homeowner method…
> 
> [http://g02.s.alicdn.com/kf/HTB14dW6KpXXXXclXFXXq6xXFXXX7/5-minutes-20ml-transparent-clear-epoxy-glue.jpg](http://g02.s.alicdn.com/kf/HTB14dW6KpXXXXclXFXXq6xXFXXX7/5-minutes-20ml-transparent-clear-epoxy-glue.jpg)

Do not forget the shipping!

---

<div class="post-metadata">

**Author:** ![imayer](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/imayer/32/197054_2.png) [@imayer](https://forum.nachi.org/u/imayer)\
**Post date:** [January 28, 2016, 4:32am UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/7 "2016-01-28T04:32:57Z")

</div>

Why would anyone _want_ two prong outlets?

I was going to ask if you can even buy two prong outlets, but I just googled it, and apparently, yes, you can. :shock:

---

<div class="post-metadata">

**Author:** ![rrosinski](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rrosinski/32/179033_2.png) [@rrosinski](https://forum.nachi.org/u/rrosinski)\
**Post date:** [January 28, 2016, 8:42pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/8 "2016-01-28T20:42:06Z")

</div>

If you leave the three prong outlets in place, they have to have a plug in the ground slot, so as not to imply they are grounded. To people that don’t know better. Someone may come over with a PC and think that their equipment grounded, but is not. The GFI fix, is a Hokey way of fooling people. But acceptable.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [January 28, 2016, 8:56pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/9 "2016-01-28T20:56:10Z")

</div>

install GFCI breakers it is so much easier that way.

---

<div class="post-metadata">

**Author:** ![creynolds1](https://avatars.discourse-cdn.com/v4/letter/c/db5fbb/32.png) [@creynolds1](https://forum.nachi.org/u/creynolds1)\
**Post date:** [January 28, 2016, 9:10pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/10 "2016-01-28T21:10:19Z")

</div>

Would putting gfi breakers in the panel on all circuits that had 2 prong outlets changed to 3 prong work instead of replacing all the outlets with gfi outlets. I am not sure that switching back to a two prong would be a good solution either since the homeowner is probably going to have adaptors in every outlet which make poor connections and pose a fire hazard.

---

<div class="post-metadata">

**Author:** ![rcooke](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rcooke/32/57038_2.png) [@rcooke](https://forum.nachi.org/u/rcooke)\
**Post date:** [January 28, 2016, 10:15pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/11 "2016-01-28T22:15:51Z")

</div>

You do not have to replace all out lets Just the first Receptacle in each string .  
Receptacles I think are much cheaper then breakers .  
You also need to put labels on each plug .

---

<div class="post-metadata">

**Author:** ![mgratton](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mgratton/32/58251_2.png) [@mgratton](https://forum.nachi.org/u/mgratton)\
**Post date:** [January 28, 2016, 10:34pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/12 "2016-01-28T22:34:25Z")

</div>

> [@rcooke](#):
>
> You do not have to replace all out lets Just the first Receptacle in each string .  
> Receptacles I think are much cheaper then breakers .  
> You also need to put labels on each plug .

You mean like this. It is acceptable but the equipment is not protected…

 ![Picture 052 (2015_01_06 20_59_18 UTC).jpg](https://global.discourse-cdn.com/internachi/original/3X/6/9/6928b568d19ae4519e6115944542a1d35c5b64a5.jpeg)

---

<div class="post-metadata">

**Author:** ![rcooke](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rcooke/32/57038_2.png) [@rcooke](https://forum.nachi.org/u/rcooke)\
**Post date:** [January 28, 2016, 10:45pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/13 "2016-01-28T22:45:34Z")

</div>

> [@mgratton](#):
>
> You mean like this. It is acceptable but the equipment is not protected…

If the down stream Plugs are fed from the GFCI outlet then they are protected .

They of course will still not have a ground

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [January 28, 2016, 11:01pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/14 "2016-01-28T23:01:46Z")

</div>

> [@mgratton](#):
>
> You mean like this. It is acceptable but the equipment is not protected…

That is a total abortion.

---

<div class="post-metadata">

**Author:** ![rcooke](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rcooke/32/57038_2.png) [@rcooke](https://forum.nachi.org/u/rcooke)\
**Post date:** [January 28, 2016, 11:09pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/15 "2016-01-28T23:09:12Z")

</div>

> [@rlewis5](#):
>
> That is a total abortion.

Why do you say that .  
What would you do ?.  
I see nothing wrong with this method .  
You at least are sure you got the first plug in the system to protect the rest in each string

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [January 28, 2016, 11:10pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/16 "2016-01-28T23:10:23Z")

</div>

> [@rlewis5](#):
>
> That is a total abortion.

While there are some issues like the unsecured cables, the gfi protection can be provided by gfi receptacles at a much lower cost than breakers.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [January 28, 2016, 11:12pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/17 "2016-01-28T23:12:54Z")

</div>

It is just plane goofy and very unprofessional.  
To have a sparky add all those GFCI outlet would most likely cost more than adding appropriate GFCI breakers.  
I would never add all those GFCI outlet over the panel.

---

<div class="post-metadata">

**Author:** ![rcooke](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rcooke/32/57038_2.png) [@rcooke](https://forum.nachi.org/u/rcooke)\
**Post date:** [January 28, 2016, 11:21pm UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/18 "2016-01-28T23:21:37Z")

</div>

Canadian Prices are at Lowes  
GFCI |breaker $109.00  
GFCI plug $14.89

**Schneider Electric - Homeline**  
**Homeline CHOM GFI 15-Amp Single Pole Ground Fault Plug-On Circuit Breaker** ]([https://www.lowes.ca/breakers/homeline-chom-gfi-15-amp-single-pole-ground-fault-plug-on-circuit-breaker\_g1447382.html?searchTerm=GFCI-Breaker](https://www.lowes.ca/breakers/homeline-chom-gfi-15-amp-single-pole-ground-fault-plug-on-circuit-breaker_g1447382.html?searchTerm=GFCI-Breaker))

Lowe’s Item #: 48969  
Model: CHOM115GFI

[FONT=Calibri] ]([https://www.lowes.ca/products/review.aspx?family=1447382](https://www.lowes.ca/products/review.aspx?family=1447382))[/FONT]

$109.00

**Pass & Seymour/Legrand**  
**Pass & Seymour/Legrand 15-Amp Decorator GFCI Electrical Outlet** ]([https://www.lowes.ca/electrical-outlets/pass-amp-seymourlegrand-15-amp-decorator-gfci-electrical-outlet\_g1201480.html?searchTerm=GFCI-receptical](https://www.lowes.ca/electrical-outlets/pass-amp-seymourlegrand-15-amp-decorator-gfci-electrical-outlet_g1201480.html?searchTerm=GFCI-receptical))  
Lowe’s Item #: 158890  
Model: 1595-WCC10  
$14.89

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [January 29, 2016, 1:58am UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/19 "2016-01-29T01:58:27Z")

</div>

> [@rlewis5](#):
>
> It is just plane goofy and very unprofessional.  
> To have a sparky add all those GFCI outlet would most likely cost more than adding appropriate GFCI breakers.  
> I would never add all those GFCI outlet over the panel.

I guess we will differ. The receptacle is about 1/3 the price of a breaker. The breaker may not be available to fit the panel. It is also easier to add the receptacle in the larger box and it saves time by not needing to find the first receptacle in the string which makes it even more cost effective. It also avoids any further need to disrupt the old insulation in the device boxes.

---

<div class="post-metadata">

**Author:** ![sphillips1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sphillips1/32/181769_2.png) [@sphillips1](https://forum.nachi.org/u/sphillips1)\
**Post date:** [January 29, 2016, 3:06am UTC](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395/20 "2016-01-29T03:06:57Z")

</div>

I found this comment on a forum a few years back during electrical school. This is how I explain to the buyer that installing GFCI’s or GFCI CB’s is a good idea even if the outlets don’t actually have an EGC. Most people don’t want to change back to 2-prong, and most don’t want to run a ground to each receptacle.

"Let’s look at a scenario… You replace a 2 prong outlet with a standard 3 prong. No equipment ground is present. Now I plug a 3 prong vacuum into the outlet and the motor shorts to the metal parts of the vac. The handle of the equipment is energized and now if you touch a grounded object it can cause serious injury.

Now same scenario with a GFCI. When you touch the grounded object the GFCI senses the current is not the same coming in as it is going out and trips."

[Next page](https://forum.nachi.org/t/un-grounded-wiring-with-three-prong-outlets/103395.md?page=2)