Unable to indetify electrical panel

Hey fellow inspectors! I had trouble identifying this electrical panel. Has anyone came across this brand? There were no labels to identify.



Looks like a problematic Zinsco panel.

11 Likes

My guess as well. Zinsco plus about a half dozen other violations equals time for a new panel.

8 Likes

Please enlighten me on other issues.

To begin with…

5 Likes

Yes sir! First thing I noticed when removing dead front cover.

What else did you see??

Honestly, I didn’t see any other issues. Could you help me if there are?

Darius, as HIs, we’re not here to call out all the minor issues we see, but ones that we see and recommend further evaluation by a professional. You’ve have enough info to do that, and my guess is that you did.

Point being, once a major concern is brought to attention for further evaluation, don’t worry about the others…the other party will figure that out.

2 Likes

How about some “clear” photos of both Bus bars?

1 Like

A few wider shots of the panel may provide other details not visible in the photos. You’re close ups are great but a few shots of the entire panel would help.

3 Likes

Is this an aluminum conductor?

And, looks like several mwbc’s without handle ties.

1 Like

I realize we are not code inspectors and can call out whatever we want, but I think I would skip the MWBC handle tie call out in this instance. The panel appears as though it was installed long, long before that was ever required.

2 Likes

I agree, I probably wouldnt mention it if I was recommending a new panel anyways.

I was just answering his request for other ‘defects’ noted :slightly_smiling_face:

2 Likes

It’s a moving target it seems sometimes, lol. Another good example is termination covers, which are now required. I can’t imagine calling that out on all the older panels.

3 Likes

Thanks! All the info I gather from experienced inspectors helps a ton, and I sincerely appreciate all the input you guys offer. I know there’s a lot I still have to learn.

I actually saw that! I wasn’t sure where it lead to. I took this pic of the branch wiring to make sure it wasn’t solid aluminum.

1 Like