I was helping a friend out this evening and saw this as his ceiling joist/ rafter tie assembly.

The rafter is seated on top of the ceiling joist and there is a 2x4 plate running parallel to join them together.

He said it needed to be done this way

 ![image](https://global.discourse-cdn.com/internachi/original/4X/f/e/4/fe41935616de4854d0f2218e8c56ac039c55aad1.jpeg)  
because the insulation needed to go over the top plate and have no compression. Does this make sense?

Has anyone seen something like this and is this a concern? I’m ignorant of the engineering of this and want to help him not have his roof fall down.

Any help or advice is greatly appreciated

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [April 1, 2023, 2:14am UTC](https://forum.nachi.org/t/unusual-rafter-tie/227386/2 "2023-04-01T02:14:27Z")

</div>

Specified by the Truss Engineer.

---

<div class="post-metadata">

**Author:** ![rmayo](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmayo/32/59218_2.png) [@rmayo](https://forum.nachi.org/u/rmayo)\
**Post date:** [April 1, 2023, 1:07pm UTC](https://forum.nachi.org/t/unusual-rafter-tie/227386/3 "2023-04-01T13:07:22Z")

</div>

That’s a stick built roof so the large ceiling rafters indicate a room is planned for that upper space. Placing the rafters on top of the ceiling joists raises the ceiling height may be a reason. Not much to go by based on one picture.

---

<div class="post-metadata">

**Author:** ![msenty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/msenty/32/271584_2.png) [@msenty](https://forum.nachi.org/u/msenty)\
**Post date:** [April 1, 2023, 1:13pm UTC](https://forum.nachi.org/t/unusual-rafter-tie/227386/4 "2023-04-01T13:13:53Z")

</div>

In snow country, I’d be concerned with that configuration. That’s a hand framed rafter system and unconventional connection method between the rafter and the ceiling joist. The 2 x 4 tie between the ceiling joist and rafter appears weak and unable to resist outward thrust from the rafter. Yes, there is a need for a raised heel for insulation, but there is also a need for good structure. Evaluation by an engineer or experienced builder is warranted.

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [April 1, 2023, 1:15pm UTC](https://forum.nachi.org/t/unusual-rafter-tie/227386/5 "2023-04-01T13:15:45Z")

</div>

> [@msenty](#):
>
> Yes, there is a need for a raised heel for insulation, but there is also a need for good structure. Evaluation by an engineer or experienced builder is warranted.

I agree with Mike…

---

<div class="post-metadata">

**Author:** ![bhoefer](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bhoefer/32/408971_2.png) [@bhoefer](https://forum.nachi.org/u/bhoefer)\
**Post date:** [April 1, 2023, 1:50pm UTC](https://forum.nachi.org/t/unusual-rafter-tie/227386/6 "2023-04-01T13:50:14Z")

</div>

Modern trusses use (truss) gang nail plates for good reasons. We are likely talking about the shear strength of 80+ nails with two nail plates (both sides) versus about 10 total on average I see in the picture. I seriously doubt this roof was engineered. So, in a report I would recommend that it be evaluated by qualified professional. It it was a friend, I would tell them to order and install appropriately-sized gang nail plates (both sides, of course), along with appropriately-sized hurricane ties.

 ![raised-heel-truss-engineered-wood-association-main-700x525](https://global.discourse-cdn.com/internachi/original/4X/5/9/3/593c575e35fc0e953dc91149605fcb63d1a21bc6.jpeg)

---

<div class="post-metadata">

**Author:** ![srechkin](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/srechkin/32/180448_2.png) [@srechkin](https://forum.nachi.org/u/srechkin)\
**Post date:** [April 1, 2023, 2:03pm UTC](https://forum.nachi.org/t/unusual-rafter-tie/227386/7 "2023-04-01T14:03:23Z")

</div>

It’s a raised heel. If a ridge beam was installed, no problem. Otherwise, the 2x4 rafter/ceiling joist ties and their nailing schedule need to be approved by AHJ/SE.

---

<div class="post-metadata">

**Author:** ![kleonard](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/kleonard/32/170953_2.png) [@kleonard](https://forum.nachi.org/u/kleonard)\
**Post date:** [April 1, 2023, 5:34pm UTC](https://forum.nachi.org/t/unusual-rafter-tie/227386/8 "2023-04-01T17:34:22Z")

</div>

Do you have any more pictures Matthew?  
@mpowell10

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [April 1, 2023, 9:16pm UTC](https://forum.nachi.org/t/unusual-rafter-tie/227386/9 "2023-04-01T21:16:55Z")

</div>

> [@rmayo](#):
>
> rafters on top of the ceiling joists

I concur…

---

<div class="post-metadata">

**Author:** ![sbridges2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sbridges2/32/213319_2.png) [@sbridges2](https://forum.nachi.org/u/sbridges2)\
**Post date:** [April 1, 2023, 9:43pm UTC](https://forum.nachi.org/t/unusual-rafter-tie/227386/11 "2023-04-01T21:43:09Z")

</div>

![images](https://global.discourse-cdn.com/internachi/original/4X/0/4/8/0482f2589ad8666c8db2e1a9926697909562ad44.jpeg)