I saw this today on a home built in 2022. I light and fan switch was installed inside shower (never seen on a new build) Shower fan and light were not on a GFCI breaker. What do you say. Thanks
Looks fine to me….![]()
Light switches were installed in the shower stall and were not GFCI protected. Recommend corrections be made by a qualified Sparky.
Can’t tell from those pictures where the shower head is in relation to the switches. My WAG is it’s OK cause someone signed off on it. You can put it in the report but don’t expect it to get changed.
did You try sitting on the bench and licking one of the switches to see if You got a little tingle ???
Your mind is in the right place. Call it out.
We all know that it will not be moved, but that doesn’t mean to leave without mentioning.
NEC 404.4(C): Switches in Shower and Tub Spaces
Code Requirement: “Switches shall not be installed within tub or shower spaces unless installed as part of a listed tub or shower assembly.”
Applies to: All switches, including those for lighting, fans, or other electrical devices.
Purpose: To reduce the risk of electrical shock in wet environments where users may be barefoot or wet-skinned, increasing vulnerability.
What Counts as a “Shower Space”?
Even if the shower head isn’t visible in your image, the presence of:
-
A tiled shower bench,
-
Mosaic tile flooring typical of wet zones,
-
And the enclosed layout
…strongly suggests this is a designated shower area. That means any switches mounted on the wall inside this space would violate NEC 404.4(C) unless they are part of a UL-listed shower assembly.
That is a claustrophobic shower. Many years ago, I had a shower like that. I’m not a big guy, and I could lean an inch and be against a wall. I hated that shower.
One might argue that placement of a shower curtain could put the switches outside of the shower. Also, can the switches get wet? It certainly looks questionable, but being recently approved by your AHJ, I would scrutinize it for what the actual risk is. Sometimes, the AHJ gets it wrong which can make for some extra time and effort on our part…welcome to our job.
Gang switch enclosure, contatings 3 separate control switches, installed inside the shower stall wet area.
Recommend a licensed electrical contractor further evaluate the Gang switch enclosure and switches for safe relocation.
Looks like the switches are adjacent to an entry door. Would have to put it in the next room I guess.
There is a distance from the shower (different codes). The tiles on the wall look like 1.5 Tiles, plus the door opening. Basically, can’t operate both at the same time, possibly?
Someone let it slide, or got missed ![]()