Looking for some feedback. I did an inspection in Dunedin, FL in Pinellas County.

It worked like a champion and was 8 years old. No permitting data available. In my inspection report I am including this was heater as a defect as a poor install method.

The following deficiencies were observed:

  • Despite a small top cover, the unit remains exposed to the elements, which can lead to accelerated wear, corrosion, and safety issues.
  • The thermal expansion tank is unsupported, placing strain on plumbing fittings.
  • Corrosion is visible on the water supply connections, possibly from exposure.
  • The unit was resting on round masonry paver(s).

Here is my main question. Would you all, or would all NOT include this in a 4-Point indicating that the water heater is unsatisfactory?

I THANK YOU ALL FOR A RAPID RESPONSE!!!

1 Like

I write up all water heaters installed outside that aren’t in an enclosure (such as a dedicated WH enclosure) for a 4pt.

Every Rheem install guide I’ve read states:
“Do not install the water heater in outdoor, unprotected areas”

Corroded fittings are a write up also. I let the underwriter decide how much corrosion they’ll accept.

Expansion tank issues depend on specifics for the 4pt.

The pavers in this case are tied to the improper exterior installation method.

2 Likes

Thanks Dom

The four point already asks for the location of the water heater, so you do not need to write it up as a deficiency. They can decide for themselves. I would imagine that the insurance company would prefer the unit being outside as there is no longer a risk of damage to the interior. If the homeowner is ok with it, I would let it go. If it was a new purchase, I would note that the location isnt ideal.

Every WH expansion tank i see is supported solely by the fitting. Doesn’t seem to be a problem. i wouldn’t call that out.

I call every expansion tank out that’s not properly supported in the event that the bladder fails and fills the tank with water. I’ve seen them bend copper pipes and even have seen the tank itself get damaged.

I rarely find one anymore that’s not properly supported.

I recently called this one out for lacking proper support.

do water heater expansion tanks need to be properly supported? - Google Search

Yes, water heater expansion tanks must be properly supported, and not solely by the connecting piping. Manufacturers typically specify this in their installation instructions. The primary reason for this is to prevent stress on the plumbing connections, which can lead to leaks or failure, especially when the tank is full of water.

Here’s why and how they should be supported:

  • Not by piping alone:

The International Plumbing Code (IPC) (308.10) and manufacturers’ instructions explicitly state that expansion tanks should not be supported by the pipes connected to them.

  • Vertical vs. Horizontal:

Tanks installed vertically (above or below the piping) may be supported by the piping if the manufacturer allows it, but horizontal installations always require additional support.

  • Manufacturer Instructions:

Always consult the specific tank’s installation instructions for the proper support method.

3 Likes

You need more than that.
Like the wiring conduit.
Clearance from the HVAC.
Anything else we can’t see.

Are you predicting the future of this appliance?

How can it be on the ground if it’s on pavers?

Consider where hot water heaters are installed. Many are worse than this. This is Florida right?

Anyway, you need to work on more than “This is not what i normally see”…
Find something in your state SOP that fits.

1 Like

Before we move onto 4-point. I think your concerns may be valid, but you would need a little more and a little less than what you stated.

This is a Rheem installation manual excerpt. I would recommend always starting here for further insight when something is unconventional. Often you can say more with less because you are stating facts.

There is an installation checklist, here is just a snippet.

The water heater was installed at the rear exterior. According to the manufacturer this unit is for indoor use only. Additional concerns observed such as corrosion at pipe unions, insufficient support for the expansion tank, and the tank was placed on pavers subject to settlement.

1 Like

Looks like 95% of the water heaters I see here in Hawaii… but that one actually has a nice cover :slight_smile: :slight_smile:

1 Like

Morning, Donald. Hope to find you well and in good spirits today.

To properly install a Rheem Classic Series outdoor water heater, you’ll need to consult the specific installation manual for your model. Is that SoP?

Certain brands/makes/types of water heaters, particularly on-demand water heaters, can be installed outdoors. I have no bones with that.

In most cases, based on the quality of, and manufacturer’s suggested service life, guarantees, and installation locations & methods of course, the average life expectancy of a water heater is about 8 to 12 years, and varies with the location and design of the unit, quality of installation, maintenance schedule and water quality as explained above, hopefully…Lol.

Write up obvious visual clearance and physical deficiencies and safety defects.
Note manifesting and serial numbers.

Move on.

That’s my wag.

Every WH here gets inspected by the local plumbing AHJ. None have additional expansion tank support. Hard sell as a defect when thw AHJ approves it.


http://media.wattswater.com/2915054.pdf

2 Likes

If the water piping has adequate support near the tank, and the tank is in a vertical position, then extra support may not be required, in my opinion. However, any horizontal installation should obviously have additional support added.

So, the question is, what is adequate support for the piping on a vertical tank? Well, you just have to use your own judgement. Figure 20-30 lbs of weight for a typical tank full of water.

1 Like

They are never full of water unless the bladder ruptures.

Yep, so that is the max weight we need to support.

1 Like

Even if the bladder ruptures, it isn’t full of water unless the shrader valve fails as well.

That’s probably true. Either way, plan for worst case, which is a tank full of water.

I like when I find them just piped on top of the cpvc. If I touch and they wobble, it’s full and a call out.

2 Likes