# Water heater shut off valve required?

**URL:** <https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469>\
**Category:** Plumbing Inspections\
**Created:** [November 10, 2020, 5:06pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469 "2020-11-10T17:06:32Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![pmccoy3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pmccoy3/32/57038_2.png) [@pmccoy3](https://forum.nachi.org/u/pmccoy3)\
**Post date:** [November 10, 2020, 5:06pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/1 "2020-11-10T17:06:32Z")

</div>

I inspected a 2006 model manufactured home that does not have a cold water shut off valve at the water heater. However, there is one approximately 7 feet from the water heater located on the wall that’s labeled “main shut off”.

What’s your thoughts on this and should I recommend one to be installed at the tank itself?

Thanks!

---

<div class="post-metadata">

**Author:** ![slord](https://avatars.discourse-cdn.com/v4/letter/s/f19dbf/32.png) [@slord](https://forum.nachi.org/u/slord)\
**Post date:** [November 10, 2020, 5:26pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/2 "2020-11-10T17:26:05Z")

</div>

Does the main shut off turn off all the water? Or just the tank

---

<div class="post-metadata">

**Author:** ![slord](https://avatars.discourse-cdn.com/v4/letter/s/f19dbf/32.png) [@slord](https://forum.nachi.org/u/slord)\
**Post date:** [November 10, 2020, 5:34pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/3 "2020-11-10T17:34:42Z")

</div>

There should be a dedicated shutoff at the tank. I would recommend one.  
It makes it easier to replace without losing water to the whole house and if it needs to be shutoff and the main will not work due to failure it is effort well spent.  
Unless they are going to be exercising the main shutoff Noone knows if it actually works or not.

---

<div class="post-metadata">

**Author:** ![pmccoy3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pmccoy3/32/57038_2.png) [@pmccoy3](https://forum.nachi.org/u/pmccoy3)\
**Post date:** [November 10, 2020, 5:41pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/4 "2020-11-10T17:41:48Z")

</div>

The main water to the home.

---

<div class="post-metadata">

**Author:** ![pmccoy3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pmccoy3/32/57038_2.png) [@pmccoy3](https://forum.nachi.org/u/pmccoy3)\
**Post date:** [November 10, 2020, 5:42pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/5 "2020-11-10T17:42:04Z")

</div>

Okay thanks, makes sense.

---

<div class="post-metadata">

**Author:** ![slord](https://avatars.discourse-cdn.com/v4/letter/s/f19dbf/32.png) [@slord](https://forum.nachi.org/u/slord)\
**Post date:** [November 10, 2020, 5:43pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/6 "2020-11-10T17:43:18Z")

</div>

Someone else might say different but that’s just my opinion

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 10, 2020, 6:57pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/7 "2020-11-10T18:57:30Z")

</div>

Manufactured homes are covered under the HUD rules. Very rarely do I see a water supply valve at the water heater. On manufactured homes.

---

<div class="post-metadata">

**Author:** ![pmccoy3](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pmccoy3/32/57038_2.png) [@pmccoy3](https://forum.nachi.org/u/pmccoy3)\
**Post date:** [November 10, 2020, 6:59pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/8 "2020-11-10T18:59:18Z")

</div>

Do you call it out ?

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 10, 2020, 11:16pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/11 "2020-11-10T23:16:07Z")

</div>

Are you talkin to me?

---

<div class="post-metadata">

**Author:** ![dbowers](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dbowers/32/59651_2.png) [@dbowers](https://forum.nachi.org/u/dbowers)\
**Post date:** [November 11, 2020, 7:23am UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/12 "2020-11-11T07:23:59Z")

</div>

With OR Without one, YES recommend one. Whether they do it or not is of no concern AFTER you’ve said it

---

<div class="post-metadata">

**Author:** ![ryoung7](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ryoung7/32/188798_2.png) [@ryoung7](https://forum.nachi.org/u/ryoung7)\
**Post date:** [November 11, 2020, 10:53am UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/13 "2020-11-11T10:53:00Z")

</div>

> [@pmccoy3](#):
>
> However, there is one approximately 7 feet from the water heater located on the wall that’s labeled “main shut off”.

Morning, Paul.  
Hope this post finds you well.

Paul. Why should the main domestic potable water supply be situated upstream the cold water heater feed?  
Personally, I would report what I saw.

If you feel uncomfortable reporting the reported main water shutoff is not the main domestic potable water supply shut off valve, refer to the vender agent or vender for disclosure.

Best regards.  
Robert Young

---

<div class="post-metadata">

**Author:** ![ddagostino](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ddagostino/32/60136_2.png) [@ddagostino](https://forum.nachi.org/u/ddagostino)\
**Post date:** [November 11, 2020, 12:48pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/14 "2020-11-11T12:48:15Z")

</div>

> [@pmccoy3](#):
>
> a 2006 model manufactured home that does not have a cold water shut off valve at the water heater.

I would guess that it’s about to have one installed anyway, as the tank is nearing replacement age. When the plumber installs the new appliance, he’ll likely add one during the install.

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [November 11, 2020, 1:39pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/15 "2020-11-11T13:39:11Z")

</div>

> **[bradwhite-install-manual.pdf](https://www.eagle-mt.com/downloads/Bradfordwhite/bradwhite-install-manual.pdf)**
>
> 434.43 KB

If there is a question about whether or not a shut off valve should be installed with the water heater, it is best to check the manufacturers installation instructions. Please see page 26 of this Bradford White water heater installation manual which states a valve should be installed on the cold water supply. Earlier in the instructions the installer was informed to turn off the main water to the home. Codes usually have requirements for water heaters but also require installation according to manufactures instructions.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 11, 2020, 1:44pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/16 "2020-11-11T13:44:22Z")

</div>

I agree, but it is different for manufactured home.  
I have the HUD codes and I can’t seem to find anything about a valve on a water heater on a manufactured home.  
Here they are see if you can find it.  
[ManFac Home HUD.pdf](https://forum.nachi.org/uploads/short-url/5N5fKEhVsQNuaWjHRCkBcbrsXtR.pdf) (1.4 MB)  
[ManFac Home HUD2.pdf](https://forum.nachi.org/uploads/short-url/vnhs6bWVPrPW7bkcd71ICbO9kMW.pdf) (1.6 MB)

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [November 11, 2020, 2:05pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/17 "2020-11-11T14:05:35Z")

</div>

I didn’t see it in there Roy. I just saw a requirement for a main water shut off. Does this mean shut off valves for fixtures are also not required?

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 11, 2020, 2:07pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/18 "2020-11-11T14:07:31Z")

</div>

It appears so. I hardly ever see them with the exception of high end manufactured homes. And rarely on the water heater.  
The water heaters are usually behind a screwed in access wall. Which I think is really stupid.

---

<div class="post-metadata">

**Author:** ![mwilles](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mwilles/32/181480_2.png) [@mwilles](https://forum.nachi.org/u/mwilles)\
**Post date:** [November 11, 2020, 2:09pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/19 "2020-11-11T14:09:48Z")

</div>

That’s interesting I learn something new every day. I didn’t know that I’m not familiar with HUD requirements. I don’t see much of it here. Thank you Roy.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 11, 2020, 2:10pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/20 "2020-11-11T14:10:24Z")

</div>

You are welcome.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 11, 2020, 5:44pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/22 "2020-11-11T17:44:38Z")

</div>

What are you doing? @slord That has nothing to do with this thread.  
Read the title.  
Would you please back down for a while.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [November 11, 2020, 5:50pm UTC](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469/25 "2020-11-11T17:50:41Z")

</div>

What is the title of this thread?  
You must be bi-polar… Huh?

[Next page](https://forum.nachi.org/t/water-heater-shut-off-valve-required/178469.md?page=2)