> [@ruecker](#):
>
> I may just be a bit careful about using those readings to

I wholeheartedly agree. I am very careful about that. I even give out the name of a local mitigation company that I trust for them to use as a referral if they want a system, mainly so they see I’m not trying to sell a service.

---

<div class="post-metadata">

**Author:** ![djameson31](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/djameson31/32/277415_2.png) [@djameson31](https://forum.nachi.org/u/djameson31)\
**Post date:** [January 21, 2023, 1:04am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/42 "2023-01-21T01:04:07Z")

</div>

> [@bcawhern1](#):
>
> The consumer has no idea what you are doing.

Consumers have no idea about a lot of things we do. Yet we take the time to explain it to them. We explain what we are doing and what we are not doing.

As for conflict of interest… I can offer them information on how to fix the problem and they can do with it as they please. I even give a referral for a local mitigation company so they understand I’m not selling them anything.

Example: the 1920s house. That inspection was several months ago and I haven’t talked to them. But I think I gave them some good information that they can use while they are doing pre-planned renovations.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [January 21, 2023, 1:09am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/43 "2023-01-21T01:09:01Z")

</div>

> [@djameson31](#):
>
> Yet we take the time to explain it to them.

I doubt I am going to change your mind. But you should explain it to them if you are going down this path.

For me, only a snake oil salesman would place a CRM device atop a drain and look at the homeowner with a straight face. There, I said it.

My only reaction as a home inspector if I placed a few random machines out would be “these readings are invalid and for my use only. I recommend this house and every home be tested for radon. If you would like to have the home tested, I can begin the test today and you will have the results in 48 hours. At that point, you will be able to make an informed decision.”

---

<div class="post-metadata">

**Author:** ![djameson31](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/djameson31/32/277415_2.png) [@djameson31](https://forum.nachi.org/u/djameson31)\
**Post date:** [January 21, 2023, 1:12am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/44 "2023-01-21T01:12:39Z")

</div>

> [@bcawhern1](#):
>
> For me, only a snake oil salesman would place a CRM device atop a drain and look at the homeowner with a straight face.

Lol. The radon coming through that drain was 77 pCi/l… And I offered them nothing but advice on how to correct it on their own.

I offered no service and I gained no extra money.

I’m not quite sure I’m following the snake oil salesman part you refer to.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [January 21, 2023, 1:19am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/45 "2023-01-21T01:19:11Z")

</div>

> [@djameson31](#):
>
> The radon coming through that drain was 77 pCi/l

Invalid reading. There are reasons why there are location protocols and closed condition protocols and delay count protocols. It could be 7 or 700, doesn’t matter. I shake my head at these guys doing “snap-shot in time” testing in GA.

> [@djameson31](#):
>
> I offered no service and I gained no extra money.

But you are disseminating this information on YouTube as if it is actionable information. It might be for a mitigation contractor to seek out concentrated areas, but I would be very very clear about that. Not only on YouTube, but for my customers too.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [January 21, 2023, 1:21am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/46 "2023-01-21T01:21:22Z")

</div>

> [@djameson31](#):
>
> And I offered them nothing but advice on how to correct it on their own.

Hopefully with a recommendation for a follow-up test afterwards.

---

<div class="post-metadata">

**Author:** ![djameson31](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/djameson31/32/277415_2.png) [@djameson31](https://forum.nachi.org/u/djameson31)\
**Post date:** [January 21, 2023, 1:26am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/47 "2023-01-21T01:26:40Z")

</div>

> [@bcawhern1](#):
>
> Invalid reading

Nothing is invalid about taking readings of a hospot entry point. It’s not presented as a formal test. It’s just a singular reading. No more, no less.

> [@bcawhern1](#):
>
> But you are disseminating this information on YouTube as if it is actionable information

The YouTube video posted here was about interior drainage systems and how they completely ignored indoor IAQ issues related to radon entry and vapor intrusion.

> [@bcawhern1](#):
>
> Hopefully with a recommendation for a follow-up test afterwards.

Exactly what I said. Plug the hole and retest. The drain wasn’t connected to the main sewer lateral, so there were multiple issues in play.

---

<div class="post-metadata">

**Author:** ![ruecker](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ruecker/32/357170_2.png) [@ruecker](https://forum.nachi.org/u/ruecker)\
**Post date:** [January 21, 2023, 1:28am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/48 "2023-01-21T01:28:40Z")

</div>

> [@djameson31](#):
>
> Lol…

 ![image](https://global.discourse-cdn.com/internachi/original/4X/3/3/9/339a18c08edb8d32d67d1af63cd3d4fd5648173b.png)

Aren’t you glad you stopped by to chat Dusty? 🤣 🤣 🤣

Just kidding. Brian is asking hard questions, but it is for everyone’s education and understanding. Don’t be a stranger! I think you could have a lot to offer the forum.

---

<div class="post-metadata">

**Author:** ![djameson31](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/djameson31/32/277415_2.png) [@djameson31](https://forum.nachi.org/u/djameson31)\
**Post date:** [January 21, 2023, 1:30am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/49 "2023-01-21T01:30:27Z")

</div>

> [@ruecker](#):
>
> Aren’t you glad you stopped by to chat Dusty

😂 First time posting on the forum… And here we are!

All good! No hurt feelings here. I enjoy the topic and I ask myself these same questions all the time.

---

<div class="post-metadata">

**Author:** ![ruecker](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ruecker/32/357170_2.png) [@ruecker](https://forum.nachi.org/u/ruecker)\
**Post date:** [January 21, 2023, 1:32am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/50 "2023-01-21T01:32:15Z")

</div>

> [@djameson31](#):
>
> I enjoy the topic…

Just one question. Don’t ask why, just answer.

**Drip leg or sediment trap?**

---

<div class="post-metadata">

**Author:** ![djameson31](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/djameson31/32/277415_2.png) [@djameson31](https://forum.nachi.org/u/djameson31)\
**Post date:** [January 21, 2023, 1:32am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/51 "2023-01-21T01:32:36Z")

</div>

@bcawhern1 @ruecker I actually recorded a video in August at an inspection where I had the trackers out and the corentium pro in the middle of the basement running simultaneously. I talked about the formal short term protocol test and also showed how I was using the trackers to see if I could find a hot spot entry point. I never edited or posted the video but now this is making me want to try to dig it up.

---

<div class="post-metadata">

**Author:** ![djameson31](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/djameson31/32/277415_2.png) [@djameson31](https://forum.nachi.org/u/djameson31)\
**Post date:** [January 21, 2023, 1:33am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/52 "2023-01-21T01:33:51Z")

</div>

> [@ruecker](#):
>
> Drip leg or sediment trap?

Well… If the direction of the the gas flow changes… 🤔

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [January 21, 2023, 1:34am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/53 "2023-01-21T01:34:51Z")

</div>

> [@djameson31](#):
>
> how they completely ignored indoor IAQ issues related to radon entry and vapor intrusion.

Fair enough. And if you think that reading was validating your point then I understand. I argue it was not validating but rather confusing.

As I said, I doubt I have changed your mind. But those people who you plopped that machine down on their drain left there with a lot to think about. A lot to think about based on some very questionable processes. Glad it was an easy fix for them and not a complex situation. They may or may not have bought the house under different circumstances.

I may have the completely wrong impression, but it appears you are using this “snap-shot” in time testing data to have an effect on a buyers decision making process.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [January 21, 2023, 1:35am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/54 "2023-01-21T01:35:40Z")

</div>

> [@djameson31](#):
>
> Well… If the direction of the the gas flow changes… 🤔

And, gas pipes can be a radon entry point! 😄

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [January 21, 2023, 1:38am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/55 "2023-01-21T01:38:08Z")

</div>

> [@ruecker](#):
>
> Just kidding. Brian is asking hard questions, but it is for everyone’s education and understanding.

Nice way of saying I am being an a\*\*hole 😄

---

<div class="post-metadata">

**Author:** ![ruecker](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ruecker/32/357170_2.png) [@ruecker](https://forum.nachi.org/u/ruecker)\
**Post date:** [January 21, 2023, 1:42am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/56 "2023-01-21T01:42:02Z")

</div>

> [@bcawhern1](#):
>
> Nice way of saying I am being an a\*\*hole 😄.

Not at all. It was a good line of questioning on a very complicated topic. There is another member that is big into radon that would probably not go very easy on Dusty.

---

<div class="post-metadata">

**Author:** ![bcawhern1](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bcawhern1/32/408713_2.png) [@bcawhern1](https://forum.nachi.org/u/bcawhern1)\
**Post date:** [January 21, 2023, 1:43am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/57 "2023-01-21T01:43:49Z")

</div>

> [@ruecker](#):
>
> There is another member that is big into radon that would probably not go very easy on Dusty.

OMG, I am turning into BILL…

Dusty, I am sorry. I love you man. You do know your shit, not denying that. Thanks for going thru the motions with me.

---

<div class="post-metadata">

**Author:** ![djameson31](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/djameson31/32/277415_2.png) [@djameson31](https://forum.nachi.org/u/djameson31)\
**Post date:** [January 21, 2023, 1:45am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/58 "2023-01-21T01:45:13Z")

</div>

> [@bcawhern1](#):
>
> I may have the completely wrong impression, but it appears you are using this “snap-shot” in time testing data to have an effect on a buyers decision making process

That’s understandable because you’re not with me during the conversations to hear me repeatedly say “we have to understand this for what it is… It’s not a formal test and we can only take these readings as surface level data. We would need much more time to really understand what’s going on.”

I think we’re on the same page with advocacy for long term testing over everything else.

I just enjoy the fine details of mitigation strategies because I’m involved in it on a daily basis. And as I said, I actually enjoy this stuff for reasons other than money.

---

<div class="post-metadata">

**Author:** ![djameson31](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/djameson31/32/277415_2.png) [@djameson31](https://forum.nachi.org/u/djameson31)\
**Post date:** [January 21, 2023, 1:47am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/59 "2023-01-21T01:47:43Z")

</div>

> [@bcawhern1](#):
>
> Dusty, I am sorry. I love you man. You do know your shit, not denying that. Thanks for going thru the motions with me.

😂 Honestly, great conversation and I enjoy it. Like I said, I ask myself these same questions daily because I want to operate with honesty and transparency.

No snake oil salesman here! 😂

---

<div class="post-metadata">

**Author:** ![djameson31](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/djameson31/32/277415_2.png) [@djameson31](https://forum.nachi.org/u/djameson31)\
**Post date:** [January 21, 2023, 2:20am UTC](https://forum.nachi.org/t/water-management-system-int-drainage-systems-and-radon-gas/224674/60 "2023-01-21T02:20:30Z")

</div>

@bcawhern1 @ruecker I found that video I mentioned. I uploaded it to my drive, unedited.

For reference, the corentium pro in the middle of the basement averaged 3.3 after the 48-hour test. The clients didn’t get any data from the eco trackers, other than my recommendation to fill the gap in the slab so it would stop soil gas and vapor intrusion.

> **[New video by Dusty Jameson](https://photos.app.goo.gl/2NzF5EtCMF6Ldbpm8)**