doing an inspection when I took the panel cover off I noticed a 75 amp 4 pole breaker. Is this a 150A breaker??
This was fed with a 3 AWG THW copper wire. Is this under sized for this box? My mind is saying yes.
I want to hear what you guys think?
Sorry for the sideways picture
rlewis5
(Roy Lewis, CERTIFIED MASTER INSPECTOR RETIRED)
2
Looks like 75 double pole.
Jim_Port
(Jim Port)
3
The ratings on the handles do not get added. That is a 75.
sstaggs
(Shawn D. Staggs, CPI)
4
Figured but wanted to double check. This is for a 4-Point inspection.
pabernathy
(Paul Abernathy, CMI®, CMECP® Electrical Code Academy,Inc.)
5
Indeed it is a 75A rated CB. The 3 CU THW is good for 100A @ 75° C so it is fine.
Where do those leads go from the breaker?