# What do you make of this?

**URL:** <https://forum.nachi.org/t/what-do-you-make-of-this/15455>\
**Category:** Electrical Inspections\
**Created:** [April 18, 2007, 4:50am UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455 "2007-04-18T04:50:24Z")\
**Posts on this page:** 18\
**Page:** 1

<div class="post-metadata">

**Author:** ![Scott\_Schultz](https://avatars.discourse-cdn.com/v4/letter/s/fbc32d/32.png) [@Scott\_Schultz](https://forum.nachi.org/u/Scott_Schultz)\
**Post date:** [April 18, 2007, 4:50am UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/1 "2007-04-18T04:50:24Z")

</div>

Saw a main breaker today on inspection. 200 amp breaker labeled for 1/0-4/0 copper SEC. Is 1/0 copper sufficient for a 200 amp breaker? I’ve seen it twice now and both times I’ve deferred it to an electrician to evaluate. Now, I see this breaker saying its ok to use 1/0 on this 200 amp but was always told (and taught) that 1/0 is for 100 amp and 2/0 is for 200 amp. What’s the story??

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [April 18, 2007, 5:21am UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/2 "2007-04-18T05:21:23Z")

</div>

1/0 copper can be OK up to 175a using the residential main feeder rule 310.15(B)(6) but not 200, Good call.

I doubt you will ever see a 175a panel so 1/0 is effectively 150a

---

<div class="post-metadata">

**Author:** ![Scott\_Schultz](https://avatars.discourse-cdn.com/v4/letter/s/fbc32d/32.png) [@Scott\_Schultz](https://forum.nachi.org/u/Scott_Schultz)\
**Post date:** [April 18, 2007, 5:28am UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/3 "2007-04-18T05:28:15Z")

</div>

and both times, the panel had the “approved” sticker by the electrical inspector when the house was built. I was starting to doubt myself which is why I am trying to find this out.

---

<div class="post-metadata">

**Author:** ![Scott\_Schultz](https://avatars.discourse-cdn.com/v4/letter/s/fbc32d/32.png) [@Scott\_Schultz](https://forum.nachi.org/u/Scott_Schultz)\
**Post date:** [April 18, 2007, 5:36am UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/4 "2007-04-18T05:36:42Z")

</div>

Here is a pic of the breaker

![irving 003.jpg](https://global.discourse-cdn.com/internachi/original/3X/2/6/26d55c6b49499dcc228f3fcb441d5e01db8fa649.jpeg)

---

<div class="post-metadata">

**Author:** ![Mike\_Whitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mike_whitt/32/1670_2.png) [@Mike\_Whitt](https://forum.nachi.org/u/Mike_Whitt)\
**Post date:** [April 18, 2007, 2:03pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/5 "2007-04-18T14:03:19Z")

</div>

> [@Scott Schultz](#):
>
> Saw a main breaker today on inspection. 200 amp breaker labeled for 1/0-4/0 copper SEC. Is 1/0 copper sufficient for a 200 amp breaker?

NO. 240.6 of the NEC list the size of overcurrent devices as outlined here

> [@](#):
>
> (A) Fuses and Fixed-Trip Circuit Breakers. The standard ampere ratings for fuses and inverse time circuit breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50, 60, 70, 80, 90, 100, 110, 125, 150, 175, 200,

Here we can see that a 175 is a standard size for a breaker. Using Table 310.16(B)(6) a 1/0 conductor can be used on a 175 amp service for a dwelling unit only. Being that 175 is a standard rating for an overcurrent device the rule outlined in 240.4(B) clearly states that a 175 must be used.

> [@Scott Schultz](#):
>
> but was always told (and taught) that 1/0 is for 100 amp and 2/0 is for 200 amp. What’s the story??

It would be better to look at 310.16(B)(6) as you can see that a 100 amp service can be supplied with a #4 copper or #2 aluminum conductor.

---

<div class="post-metadata">

**Author:** ![Scott\_Schultz](https://avatars.discourse-cdn.com/v4/letter/s/fbc32d/32.png) [@Scott\_Schultz](https://forum.nachi.org/u/Scott_Schultz)\
**Post date:** [April 19, 2007, 3:19pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/6 "2007-04-19T15:19:06Z")

</div>

How would the electrician go about fixing this problem? Do they replace the 1/0 SEC with 2/0 or replace part of it? Not sure how this would work. thanks

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [April 19, 2007, 6:04pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/7 "2007-04-19T18:04:58Z")

</div>

Replace the SE or replace the breaker. The tradeoff is labor vs cost. The breaker may be over $100 depending on what panel it is.

---

<div class="post-metadata">

**Author:** ![bgraham](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bgraham/32/179260_2.png) [@bgraham](https://forum.nachi.org/u/bgraham)\
**Post date:** [April 19, 2007, 7:31pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/8 "2007-04-19T19:31:44Z")

</div>

Scott, I read that breaker label as ONE 4/0 cable, I could be wrong I have been before.😃

---

<div class="post-metadata">

**Author:** ![Scott\_Schultz](https://avatars.discourse-cdn.com/v4/letter/s/fbc32d/32.png) [@Scott\_Schultz](https://forum.nachi.org/u/Scott_Schultz)\
**Post date:** [April 19, 2007, 9:32pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/9 "2007-04-19T21:32:25Z")

</div>

Bruce,

I can see how you can see it like that but that’s gotta be wrong cause there’s no way they’d say that you gotta use only a 4/0 for a measly 200 amp breaker.

---

<div class="post-metadata">

**Author:** ![bgraham](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bgraham/32/179260_2.png) [@bgraham](https://forum.nachi.org/u/bgraham)\
**Post date:** [April 19, 2007, 11:36pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/10 "2007-04-19T23:36:48Z")

</div>

so that would be a #1 up to a 4/0:D

---

<div class="post-metadata">

**Author:** ![brian\_winkle](https://avatars.discourse-cdn.com/v4/letter/b/f0a364/32.png) [@brian\_winkle](https://forum.nachi.org/u/brian_winkle)\
**Post date:** [April 20, 2007, 12:33am UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/11 "2007-04-20T00:33:58Z")

</div>

The information is for the terminal lugs, showing you what size conductors you can use in those terminals, along with the specified torque. It is not there as an indication of what wire size is acceptable for a 200 amp load, it is there to indicate what size wire is acceptable for those terminals. The correct wire size for the load is determined by referring to the applicable code.  
Any electrician who would size conductors to this label is not really an electrician.

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [April 20, 2007, 1:14pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/12 "2007-04-20T13:14:50Z")

</div>

> [@bgraham](#):
>
> Scott, I read that breaker label as ONE 4/0 cable, I could be wrong I have been before.😃

nope…it means…CU it will accept Size # 1 THRU 4/0 in AWG sizes of CU…not that it needs (1) 4/0…🙂

---

<div class="post-metadata">

**Author:** ![Mike\_Whitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mike_whitt/32/1670_2.png) [@Mike\_Whitt](https://forum.nachi.org/u/Mike_Whitt)\
**Post date:** [April 20, 2007, 6:00pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/13 "2007-04-20T18:00:18Z")

</div>

I have a 30 horse power 240 volt three phase motor.

Looking at Table 430.250 this motor is rated at 80 Full Load Amps.

Looking at 430.22 a 125% factor must be applied to the Full Load Amps of this motor in order to size the branch circuit supplying this motor. 80 times 125% equals 100 amps for the conductor.

Looking at Table 310.16 for a TW copper conductor for this motor I find that it will require at least a #1 AWG conductor.

Table 430.52 gives 250% as the multiplier for an inverse time circuit breaker and this will look a little like this 80 X 250% = 200 amps.

Now I have a 200 amp breaker that will have a #1AWG conductor and all is legal.  
Thus the listing for 1 through 4/0 on the terminals. 😉

---

<div class="post-metadata">

**Author:** ![Greg\_Fretwell](https://avatars.discourse-cdn.com/v4/letter/g/f1d935/32.png) [@Greg\_Fretwell](https://forum.nachi.org/u/Greg_Fretwell)\
**Post date:** [April 20, 2007, 6:43pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/14 "2007-04-20T18:43:35Z")

</div>

Hey Mike, how you been?

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [April 20, 2007, 9:55pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/15 "2007-04-20T21:55:30Z")

</div>

> [@Mike Whitt](#):
>
> I have a 30 horse power 240 volt three phase motor.
> 
> Looking at Table 430.250 this motor is rated at 80 Full Load Amps.
> 
> Looking at 430.22 a 125% factor must be applied to the Full Load Amps of this motor in order to size the branch circuit supplying this motor. 80 times 125% equals 100 amps for the conductor.
> 
> Looking at Table 310.16 for a TW copper conductor for this motor I find that it will require at least a #1 AWG conductor.
> 
> Table 430.52 gives 250% as the multiplier for an inverse time circuit breaker and this will look a little like this 80 X 250% = 200 amps.
> 
> Now I have a 200 amp breaker that will have a #1AWG conductor and all is legal.  
> Thus the listing for 1 through 4/0 on the terminals. 😉

lol…very nice…but I hope these guys don’t actually see a 30HP 3-phase motor in a normal dwelling anytime soon…tehehehe…

---

<div class="post-metadata">

**Author:** ![Mike\_Whitt](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mike_whitt/32/1670_2.png) [@Mike\_Whitt](https://forum.nachi.org/u/Mike_Whitt)\
**Post date:** [April 20, 2007, 10:22pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/16 "2007-04-20T22:22:35Z")

</div>

> [@Greg Fretwell](#):
>
> Hey Mike, how you been?

The good Lord keeps blessing me more and more, thank you kindly for asking and giving me a chance to praise his name again

> [@pabernathy](#):
>
> lol…very nice…but I hope these guys don’t actually see a 30HP 3-phase motor in a normal dwelling anytime soon…tehehehe…

Just wanted to explain one way that a #1 AWG conductor could land under a 200 amp breaker as there seem to be some question raised in an earlier post about the #1 AWG conductor.

Looking to get me another one of them boxes like you got.

---

<div class="post-metadata">

**Author:** ![brian\_winkle](https://avatars.discourse-cdn.com/v4/letter/b/f0a364/32.png) [@brian\_winkle](https://forum.nachi.org/u/brian_winkle)\
**Post date:** [April 20, 2007, 11:19pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/17 "2007-04-20T23:19:50Z")

</div>

> [@pabernathy](#):
>
> lol…very nice…but I hope these guys don’t actually see a 30HP 3-phase motor in a normal dwelling anytime soon…tehehehe…

They might see one if Tool Time Tim sells his place.

---

<div class="post-metadata">

**Author:** ![pabernathy](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/pabernathy/32/178230_2.png) [@pabernathy](https://forum.nachi.org/u/pabernathy)\
**Post date:** [April 22, 2007, 2:10pm UTC](https://forum.nachi.org/t/what-do-you-make-of-this/15455/18 "2007-04-22T14:10:38Z")

</div>

lol…I hear ya Brian…Mike…I got ya brother and I will give ya one of them green boxes…🙂