# what to report on old hvac equipment

**URL:** <https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801>\
**Category:** Inspecting HVAC Systems\
**Created:** [July 6, 2008, 3:34am UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801 "2008-07-06T03:34:17Z")\
**Posts on this page:** 9\
**Page:** 1

<div class="post-metadata">

**Author:** ![bking](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bking/32/624_2.png) [@bking](https://forum.nachi.org/u/bking)\
**Post date:** [July 6, 2008, 3:34am UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801/1 "2008-07-06T03:34:17Z")

</div>

I have read everything on here about what to report on old HVAC equipment but its all scattered around without much agreement on the subject so here is a new thread for this very important subject with information that many do not take into consideration. This thread is not for inspectors who cater to realtors.

Since roofs usually die a slow death where most reasonable people can spot a bad one easily, they are not so hard to deal with, but HVAC is a problem, when it quits in cold or hot weather its a real immediate problem for the occupants and this can even affect their judgement and temperment.

Forget estimated life span. average life span, service life etc. we are in business to issue our opinion as we see fit. You can use that data as a reference but nothing says you have to include it in the report when you recommend replacement.

How many of you go ahead and recommend a new HVAC system when the unit is older than about 17 years and is operating on the day of the inspection?

What about the homes with a newer heat pump airhandler and a 20 year old exterior heat pump unit? Do you inform your clients that when the exterior unit is replaced the inside half also has to be replaced due to different oils and refrigerant/design issues at a cost of 4k+?

Forget the purchase contract language such as “is it functioning as intended” etc. that only relates to how the reported issues are negotiated and is really none of our business. Our business is to inform the client of the property conditions and make good recommendations.

Actually, if something was designed to last about 17 years and is older than that, IT IS NOT functioning as intended.

Fact: Many homeowners have HVAC systems replaced when they are still operating so a recommendation to do the same is not something that is in anyway wrong.

fire away :mrgreen:

---

<div class="post-metadata">

**Author:** ![jhagarty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jhagarty/32/78584_2.png) [@jhagarty](https://forum.nachi.org/u/jhagarty)\
**Post date:** [July 6, 2008, 3:56am UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801/2 "2008-07-06T03:56:45Z")

</div>

Note the type and age of the HVAC equipment and recommend accordingly based upon your inspection of the system components.

---

<div class="post-metadata">

**Author:** ![rray](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rray/32/2162_2.png) [@rray](https://forum.nachi.org/u/rray)\
**Post date:** [July 6, 2008, 4:29am UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801/3 "2008-07-06T04:29:21Z")

</div>

> [@bking](#):
>
> This thread is not for inspectors who cater to realtors.

That’s funny, Bruce. Do we know the names of the iNACHI members who “cater to realtors [sic].” We could create a list and then give it to Chris and have him ban them from this thread.

This is in my contracts:

> [@](#):
>
> Notwithstanding anything noted by RAY concerning the roof, the heating and cooling system, fireplaces and chimneys, and wood-destroying pests and organisms, **RAY specifically and expressly recommends** that CLIENT have a complete heating and cooling system evaluation before close of escrow, a CSIA Level II inspection of the fireplace and chimney before close of escrow, a complete inspection by a qualified termite and pest control professional before close of escrow, and, annually and prior to the next rainy season, a complete roof inspection by a licensed roofing contractor.

This then goes into all my reports:

> [@](#):
>
> \*\*If it cannot be proven that furnace has had a service/maintenance inspection within the last twelve months, recommend complete system evaluation by licensed heating and cooling professional before close of escrow. \*\*Such an inspection typically involves partial dismantling of the furnace to facilitate inspection of the heat exchanger.

---

<div class="post-metadata">

**Author:** ![gbeaumont](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/gbeaumont/32/1094_2.png) [@gbeaumont](https://forum.nachi.org/u/gbeaumont)\
**Post date:** [July 6, 2008, 12:51pm UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801/4 "2008-07-06T12:51:47Z")

</div>

Hi Bruce.

> [@](#):
>
> How many of you go ahead and recommend a new HVAC system when the unit is older than about 17 years and is operating on the day of the inspection?
> 
> I would warn the buyer that the unit is approaching the end of it’s design life and recommend that they budget for a replacement, I might also point out that they may be able to extend the life of the appliance with regular servicing.
> 
> What about the homes with a newer heat pump airhandler and a 20 year old exterior heat pump unit? Do you inform your clients that when the exterior unit is replaced the inside half also has to be replaced due to different oils and refrigerant/design issues at a cost of 4k+?
> 
> Yes I would point out mismatched components, down here this is a big issues as most handlers will run around 20 years, but due to the salt air and humidity the outside coils typically last a little over 10 years. Here it is not uncommon to see a system with it’s original air handler/inside coil, but it is on its second replacement exterior coil.
> 
> Forget the purchase contract language such as “is it functioning as intended” etc. that only relates to how the reported issues are negotiated and is really none of our business. Our business is to inform the client of the property conditions and make good recommendations.
> 
> Agreed, I don’t use that language, but then again I do very little home buyer work, my clients are more interested in short to medium term opperating costs (including replacements and upgrades)
> 
> Actually, if something was designed to last about 17 years and is older than that, IT IS NOT functioning as intended.
> 
> You won’t make many friends with that statement, and I would say that you are incorrect.
> 
> Fact: Many homeowners have HVAC systems replaced when they are still operating so a recommendation to do the same is not something that is in anyway wrong.
> 
> Agreed, in most cases homeowners perform upgrades only after the existing system has started to fail, and they have been advised that ongoing costly repairs are likely to be required if they don’t replace, plus with newer units beimg more efficient there is a bigger incentive to replace to reduce operating costs.
> 
> fire away :mrgreen:

Fired 😉

Regards

Gerry

---

<div class="post-metadata">

**Author:** ![dandersen](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dandersen/32/59398_2.png) [@dandersen](https://forum.nachi.org/u/dandersen)\
**Post date:** [July 6, 2008, 2:42pm UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801/5 "2008-07-06T14:42:43Z")

</div>

I would say that the physical appearance it a good gauge. If it is rusted, deteriorated, leak signs, mold growing on it, panels don’t fit, filthy dirty coils, etc. it is quite obvious that no one cared for the equipment in the past. Regardless of the unit age, this condition is an indicator that it won’t last much longer.

If it is old, but looks like it has been cared for, it may last a long time. Service contract papers are commonly found. These units are few and far between to find though!

There is an electrical test that can be done using a megometer on the compressor electrical terminals. This tests the compressor motor wiring insulation and can detect moisture and other contaminates in the refrigerant oil (which the motor is “sitting in”.

There are oil acid tests available also.

You mentioned mismatched equipment; this is a no-go from the start. It lowers equipment efficiency and voids all equipment warranty.

> [@](#):
>
> Actually, if something was designed to last about 17 years and is older than that, IT IS NOT functioning as intended.

No, I don’t think so. I worked for a high end HVAC service company (with clients that spend a lot on maintenance) and found very old and outdated performing better than the new equipment counterpart. Actually I had to go answer why the newly installed high efficiency equipment was not performing like the old stuff on numerous occasions. Hi efficiency does not mean it works as good!

What is a high efficiency unit?  
Well, with the low end equipment it is basically a 3 ton condenser with a 2.5 ton compressor! Don’t get me wrong, you are replacing the same sized unit, just that your 3 ton is replaced with a 3t compressor in a 4 ton condenser.

One of the hardest working units from the past was the GE/Trane, climatuff compressor with a brush coil rather than a fin coil. The effective surface area of this coil was huge compared to a finned coil. There are GE’s still in service today! Trane bought out GE many years ago.

---

<div class="post-metadata">

**Author:** ![rray](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rray/32/2162_2.png) [@rray](https://forum.nachi.org/u/rray)\
**Post date:** [July 6, 2008, 3:24pm UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801/6 "2008-07-06T15:24:29Z")

</div>

> [@dandersen](#):
>
> No, I don’t think so.

I agree with you there! No doubt.

---

<div class="post-metadata">

**Author:** ![bking](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bking/32/624_2.png) [@bking](https://forum.nachi.org/u/bking)\
**Post date:** [July 6, 2008, 7:54pm UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801/7 "2008-07-06T19:54:03Z")

</div>

You can bet that a clients attorney will love the fact that a home had an old worn out hvac and the inspector did not make the client aware of the condition and consequences therein after the immenient failure occurs.

The only way to cover yourself 100% is to recommend it be replaced or at least report to this effect: When it quits, most hvac techs will recommend replacement.

---

<div class="post-metadata">

**Author:** ![dvalley](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/dvalley/32/206092_2.png) [@dvalley](https://forum.nachi.org/u/dvalley)\
**Post date:** [July 6, 2008, 8:04pm UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801/8 "2008-07-06T20:04:12Z")

</div>

When I come upon older heating units, I note the following…

_ **The heating system was paced through it’s normal sequence of operating modes, with no obvious defects noted at the time of inspection. However, due to systems age, it is clearly beyond it’s life expectancy, and replacement should be considered. Until then, I recommend service and maintenance from a licensed heating contractor now and annually.** _

---

<div class="post-metadata">

**Author:** ![bking](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/bking/32/624_2.png) [@bking](https://forum.nachi.org/u/bking)\
**Post date:** [July 6, 2008, 8:10pm UTC](https://forum.nachi.org/t/what-to-report-on-old-hvac-equipment/29801/9 "2008-07-06T20:10:09Z")

</div>

Thats pretty good but still, when it quits, here is what the homeowner might hear from the hvac tech if he cant fix it with a capacitor or relay:

“This thing was shot 2 years ago, you mean you just had this place inspected?”