Pre-drywall inspection, new construction (remodel) where some of the existing conduit and j-boxes were still being used.


I called these boxes out as in need of plugs in the missing knock-outs before hanging drywall. The contractor was a bit P-O'd and said I was being way to picky ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)

What would your call be?





Even the new installations were missing covers and knock-outs.



This is the same home where I found this http://www.nachi.org/bbsystem/viewtopic.php?t=6432


--
Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738

Originally Posted By: Bob Badger
This post was automatically imported from our archived forum.



Ask the contractor what section of the NEC allows the open KOs?


You are not being to picky, boxes should not have missing KOs, it would be acceptable if they put in KO seals.

I would guess you are hired by the future owners of this house?

If that is the case keep on doing what you are doing. ![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif)


--
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum

Originally Posted By: jpope
This post was automatically imported from our archived forum.



Bob Badger wrote:
I would guess you are hired by the future owners of this house?


That is correct!


--
Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738

Originally Posted By: Brian A. Goodman
This post was automatically imported from our archived forum.



I never ignore open knock-outs. They get noted and recommended for KO seals every time. Tell the contractor you aren’t nearly as picky as the lawyer will be if there’s a problem. Electrical is a very bad place to not dot the “i’s” and cross the “t’s”.


Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



You also need to strap that romex within 12" of the box. I can’t tell about the EMT