Originally Posted By: bking This post was automatically imported from our archived forum.
I have an older GE breaker with the white stuff on it that has been discussed on here before. I scraped it off and found a phillips screw head underneath, must be a tamper proof/indication thing.
–www.BAKingHomeInspections.com
system
(system)
November 17, 2005, 12:00am
2
Originally Posted By: bbadger This post was automatically imported from our archived forum.
Well that breaker is now junk.
What you found was the calibration screw used during the manufacturing process.
All small molded case breakers have a spot on them for this screw, many manufacturers use black for this so they are not as obvious.
-- Bob Badger
Electrical Construction & Maintenance
Moderator at ECN
system
(system)
November 17, 2005, 12:00am
3
Originally Posted By: whandley This post was automatically imported from our archived forum.
Hey Bob;
Have you checked your website home page lately? Template and or text appears to be all over the place.
![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)
-- I travel the globe to protect my clients!
Orange County Home Inspections
California Home Inspectors
www.progressiveinspection.com
system
(system)
November 18, 2005, 12:00am
4
Originally Posted By: bbadger This post was automatically imported from our archived forum.
whandley wrote:
Hey Bob;
Have you checked your website home page lately? Template and or text appears to be all over the place.
![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)
What web page?
I do not have a web page, that I am awhere of.
-- Bob Badger
Electrical Construction & Maintenance
Moderator at ECN