Originally Posted By: wpedley This post was automatically imported from our archived forum.
Say you run oil fired boiler for twenty min and all of a sudden you notice they(homeowner) shut the water off to it…don’t know why…therefore no water in system. Gauge is maxed. What will happen once it cools and water is supplied and fired back up?
Originally Posted By: jsavino This post was automatically imported from our archived forum.
Will
It depends on the boiler, if it is cast iron or steel. If it is steel, probably nothing. Maybe the baffles melted inside and need to be replaced or the coil gasket may need to be replaced. If it is cast iron, there may be some damage. The sections in a cast iron boiler have push nipples between the sections. Weil Mclain boilers use a neoprene push nipples, ( some boilers have steel ) that after 20 minutes of running with no water, may have been damaged beyond repair. More serious would be a cracked section, probably in the upper half of the boiler. You wouldn’t know until the boiler is pressurized and ran to operating temp. Either case the boiler would have to be replaced.
In this case the burner should have been disabled from running. Either by disconnecting the power source, duct tape the switch in the off position, or something as simple as put a sign in big letters DO NOT OPERATE- NO WATER IN BOILER.
I would recommend on any boiler, a hydronic low water cut off be installed. It's good insurance for under $ 500 verses a $ 3000 + boiler install.
-- John Savino
HomeWorks Inspection Services, LLC
St. James, NY