# Would this be 220Amps coming in?

**URL:** <https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216>\
**Category:** Electrical Inspections\
**Created:** [October 8, 2017, 2:03pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216 "2017-10-08T14:03:09Z")\
**Posts on this page:** 16\
**Page:** 1

<div class="post-metadata">

**Author:** ![plesieur](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/plesieur/32/59455_2.png) [@plesieur](https://forum.nachi.org/u/plesieur)\
**Post date:** [October 8, 2017, 2:03pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/1 "2017-10-08T14:03:09Z")

</div>

I am finishing up a 203K write up and saved electric for last.  
1- 100 amp fuse box with 2- 60 amp fuse boxes for 1 bedroom apartments. My scope of work will mandate it all be changed to 3- 100 amp breaker panels. Maybe even a 200 amp for the main floor unit and 2- 100 amp for the 1 bedroom apartments.  
I wrote 220A coming in with 120/240 volts. The service is fed with an overhead supply.

All panels have a main shutoff.

I guess my question is would anyone else recommend a 200 amp panel for the 2 bedroom main floor and 100 amp panels for the 2 apartments. My concern is they homeowner will need new wires run to the home anyway so I propose running underground and 400 amps. Meters will go outside as part of the work.

 ![Electric.JPG](https://global.discourse-cdn.com/internachi/original/3X/b/1/b19026ba196cdf255d1b56d76deaef5a86c07765.jpeg)

---

<div class="post-metadata">

**Author:** ![Jim\_Port](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@Jim\_Port](https://forum.nachi.org/u/Jim_Port)\
**Post date:** [October 8, 2017, 2:10pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/2 "2017-10-08T14:10:28Z")

</div>

What does a demand load calculation call for?

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [October 8, 2017, 2:24pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/3 "2017-10-08T14:24:34Z")

</div>

> [@plesieur](#):
>
> My scope of work will **mandate** it all be changed to 3- 100 amp breaker panels. Maybe even a 200 amp for the main floor unit and 2- 100 amp for the 1 bedroom apartments.  
> I wrote 220A coming in with 120/240 volts. The service is fed with an overhead supply.

Since you used the word _mandate_ what’s your justification?

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [October 8, 2017, 4:15pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/4 "2017-10-08T16:15:08Z")

</div>

Paul, I defer to Jim and Robert as they are the experts, but my thought (as I see many of the same properties that you do) is… As far as the supplied Amps, 100A & 60A are/have been sufficient for the size apartments you mentioned. Seeing as an upgrade to breakers should happen, and apartment dwellers tend to like their electronics (especially “Gamers”), I would prolly suggest 100/100/100 with a higher slot capacity for the mainfloor 2 bedroom, assuming that it’s panel also serves the common areas… or… add a seperate 4th panel for the common areas and size all 3 apartments with the same panels at 100A. IMO, 200A is overkill for a “standard” apartment.

---

<div class="post-metadata">

**Author:** ![plesieur](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/plesieur/32/59455_2.png) [@plesieur](https://forum.nachi.org/u/plesieur)\
**Post date:** [October 8, 2017, 4:32pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/5 "2017-10-08T16:32:55Z")

</div>

> [@Robert\_Meier](#):
>
> Since you used the word _mandate_ what’s your justification?

Mandate for me is I have to make mandatory health and safety items. This home needs other electrical wok so a service upgrade to present code requirements would be more cost effective in the long run with a breaker panel. Neither apartments (2 apartments) has air conditioning and to install an effective energy saving install I might as well call for a 100 amp service to each unit. I will ask the electrician what makes the most sense but the fusue have to go. Unlike a regular home inspection I can call for mandatory items such as, clean the flues (chimney sweep), boiler tune up, AFCI or GFCI, smole and CO2, railings, remove torn carpet and so on.

---

<div class="post-metadata">

**Author:** ![plesieur](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/plesieur/32/59455_2.png) [@plesieur](https://forum.nachi.org/u/plesieur)\
**Post date:** [October 8, 2017, 4:43pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/6 "2017-10-08T16:43:12Z")

</div>

> [@jjonas](#):
>
> Paul, I defer to Jim and Robert as they are the experts, but my thought (as I see many of the same properties that you do) is… As far as the supplied Amps, 100A & 60A are/have been sufficient for the size apartments you mentioned. Seeing as an upgrade to breakers should happen, and apartment dwellers tend to like their electronics (especially “Gamers”), I would prolly suggest 100/100/100 with a higher slot capacity for the mainfloor 2 bedroom, assuming that it’s panel also serves the common areas… or… add a seperate 4th panel for the common areas and size all 3 apartments with the same panels at 100A. IMO, 200A is overkill for a “standard” apartment.

Thanks Jeff,

I agree with 100, 100, 100. Thought I’d ask the guys who know more about electricity than me.  
The guy buying the place is an IT professional and I will ask him what his energy needs are. For all I know he will fill the utility room with servers. Also, the upstairs apartment is over 1600 SF and is being cooled with 3 mini splits.

This is a rambler style home with a walk out in front. On the 60 amp fuse boxes, they have to go and for the same money I can get 100 amps protected by breakers. This is an insured loan so I have always asked fuses be replaced with breakers.

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [October 8, 2017, 5:02pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/7 "2017-10-08T17:02:27Z")

</div>

> [@plesieur](#):
>
> Thanks Jeff,
> 
> I agree with 100, 100, 100. Thought I’d ask the guys who know more about electricity than me.  
> The guy buying the place is an IT professional and I will ask him what his energy needs are. For all I know he will fill the utility room with servers. Also, the upstairs apartment is over 1600 SF and is being cooled with 3 mini splits.
> 
> This is a rambler style home with a walk out in front. On the 60 amp fuse boxes, they have to go and for the same money I can get 100 amps protected by breakers. This is an insured loan so I have always asked fuses be replaced with breakers.

You could always go with 125-150 for the 1600 sq. ft. apt. Which wouldn’t cost much more than 100 amp.

---

<div class="post-metadata">

**Author:** ![mcyr](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/mcyr/32/173319_2.png) [@mcyr](https://forum.nachi.org/u/mcyr)\
**Post date:** [October 8, 2017, 5:02pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/8 "2017-10-08T17:02:50Z")

</div>

I agree with Jeff’s assessment Paul. 🙂

---

<div class="post-metadata">

**Author:** ![plesieur](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/plesieur/32/59455_2.png) [@plesieur](https://forum.nachi.org/u/plesieur)\
**Post date:** [October 8, 2017, 5:13pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/9 "2017-10-08T17:13:56Z")

</div>

Hello Marcel

Jeff and Christopher’s suggestions are good. I didn’t think about 125 or 150 amps.

Electrician will chime in also but I need to deliver my report tomorrow, electrician will not be there on time.

For those who don’t know what I do, I estimate costs before the contractors show up to see if the loan is feasible.  
Yeah, I know, I know. I am not an expert in all fields.

Still, I must be doing something right though as I have been doing this for 10 years.

---

<div class="post-metadata">

**Author:** ![rlewis5](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rlewis5/32/337040_2.png) [@rlewis5](https://forum.nachi.org/u/rlewis5)\
**Post date:** [October 8, 2017, 5:48pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/10 "2017-10-08T17:48:14Z")

</div>

Would not pulling the mains and see that amps they were tell you?

---

<div class="post-metadata">

**Author:** ![lkage](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/lkage/32/347658_2.png) [@lkage](https://forum.nachi.org/u/lkage)\
**Post date:** [October 8, 2017, 7:46pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/11 "2017-10-08T19:46:51Z")

</div>

> [@plesieur](#):
>
> Hello Marcel
> 
> Jeff and Christopher’s suggestions are good. I didn’t think about 125 or 150 amps.
> 
> Electrician will chime in also but I need to deliver my report tomorrow, electrician will not be there on time.
> 
> For those who don’t know what I do, \*\*I estimate costs before the contractors show up to see if the loan is feasible. \*\*  
> Yeah, I know, I know. I am not an expert in all fields.
> 
> Still, I must be doing something right though as I have been doing this for 10 years.

It wouldn’t surprise me if the 200 amp panel was less the a 125 or 150 amp panel, what with all the 200 amp panels being installed these days.

---

<div class="post-metadata">

**Author:** ![jjonas](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/jjonas/32/301755_2.png) [@jjonas](https://forum.nachi.org/u/jjonas)\
**Post date:** [October 8, 2017, 8:14pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/12 "2017-10-08T20:14:58Z")

</div>

> [@lkage](#):
>
> It wouldn’t surprise me if the 200 amp panel was less the a 125 or 150 amp panel, what with all the 200 amp panels being installed these days.

Not in Minnesota. 100 Amp is the norm. 200A in larger homes, but 125A/150A are more common. Even Dual 100’s! Typically I see 200A on larger new builds only (and yes, there are always exceptions).

---

<div class="post-metadata">

**Author:** ![ccurrins](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/ccurrins/32/225758_2.png) [@ccurrins](https://forum.nachi.org/u/ccurrins)\
**Post date:** [October 8, 2017, 9:28pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/13 "2017-10-08T21:28:31Z")

</div>

> [@lkage](#):
>
> It wouldn’t surprise me if\*\* the 200 amp panel was less the a 125 or 150 amp panel\*\*, what with all the 200 amp panels being installed these days.

Don’t forget the SE cables.

---

<div class="post-metadata">

**Author:** ![rmeier2](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/rmeier2/32/59909_2.png) [@rmeier2](https://forum.nachi.org/u/rmeier2)\
**Post date:** [October 8, 2017, 11:35pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/14 "2017-10-08T23:35:11Z")

</div>

> [@plesieur](#):
>
> Mandate for me is I have to make mandatory health and safety items. This home needs other electrical wok so a service upgrade to present code requirements would be more cost effective in the long run with a breaker panel. Neither apartments (2 apartments) has air conditioning and to install an effective energy saving install I might as well call for a 100 amp service to each unit. I will ask the electrician what makes the most sense but the fusue have to go. Unlike a regular home inspection I can call for mandatory items such as, clean the flues (chimney sweep), boiler tune up, AFCI or GFCI, smole and CO2, railings, remove torn carpet and so on.

Fair enough. From an electrician’s or electrical inspector’s perspective simply eyeballing the service size wouldn’t be good enough. A load calculation performed according to Article 220 of the NEC would be needed but I do see where you’re coming from and if it’s acceptable to the parties that you’re dealing with then all is good. 🙂

---

<div class="post-metadata">

**Author:** ![sfetty](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/sfetty/32/331195_2.png) [@sfetty](https://forum.nachi.org/u/sfetty)\
**Post date:** [October 8, 2017, 11:41pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/15 "2017-10-08T23:41:37Z")

</div>

Great responses thanks to all that gave input, we don’t see this kind of stuff here normally.

---

<div class="post-metadata">

**Author:** ![plesieur](https://sea2.discourse-cdn.com/internachi/user_avatar/forum.nachi.org/plesieur/32/59455_2.png) [@plesieur](https://forum.nachi.org/u/plesieur)\
**Post date:** [October 9, 2017, 4:42pm UTC](https://forum.nachi.org/t/would-this-be-220amps-coming-in/119216/16 "2017-10-09T16:42:32Z")

</div>

I much appreciated the responses, as well as the suggestion of a load calculation which I have done but not for the 203K rehab loans. I think I will consider load calcs from now on though. It would make for a better report on some projects.