Originally Posted By: jonofrey This post was automatically imported from our archived forum.
Some time ago, I called out a 40 amp breaker connected to 10 AWG copper. The electrician that installed the panel called me to say that depending on what the circuit is serving, he could bump up the breaker size.
That's news to me? When I check conductor size I've always referenced NEC 310-16.
What's up with that?
BTW - please look me in the eyes and quit staring at my breasts.
Originally Posted By: dhadler This post was automatically imported from our archived forum.
John, I’m trying not to look but I just can’t help it
It seems to be OK on certain items such as Electric motors and the like. Such as AC condensers for example. They only have a significant load at start up and after that it drops dramatically once the fan/load is spinning.
They are allowed to use the larger breaker to avoid nuisance tripping under the start-up phase. It does have some type of formula to find out what and how large that is, but I don't know it, I'm just a HI.
Some of the other guy's with the electrical background will probably be able to fill you in on the details.
-- Darrell Hadler
Five Star Home Inspections
Medicine Hat, Alberta CANADA
Originally Posted By: jmyers This post was automatically imported from our archived forum.
John,
It would depend on what the circuit was serving. Units such as HVAC have to be installed using the nameplate ratings on the unit. Other than HVAC equipment, I have never heard of bumping up a rating, although a nameplate rating would supercede the code requirements.
Quote:
The concept that you need to grasp is that for motors and HVAC equipment, the overload devices for the circuit are in the unit itself, not in the overcurrent device that is protecting the circuit. The device that is protecting the circuit is providing short circuit and ground fault protection, not overload protection.
It is possible to have a #12 Cu. NM protected by a 40 ampere short circuit and ground fault protective device.
This is the link if you care to read it for yourself.
Originally Posted By: dhartke This post was automatically imported from our archived forum.
We’ve had this discussion before and if my memory serves me someone added even more information about the condensing unit having its own overcurrent protection. I still have a problem with the “safety first” NEC or UL allowing for inadequate protection of the wire between the panel and the condensing unit disconnect. What happens if an accident along the way causes the #12 hot to contact the neutral or grounding wire and it is protected by a 40 amp breaker without a GFCI? I’m not doubting the interpretation of the NEC codes. I’m doubting the NEC safety continuity. Pun intended.
Originally Posted By: Joey D’Adamo This post was automatically imported from our archived forum.
The breaker should still trip. My understanding is that the short circuit/ground fault tolerance barely, if at all, changes between breaker sizes.
dhartke wrote:
How hot will a #12 wire get carrying 40 amps?
For continuous loads, it would get pretty warm and likely damage the insulation. Of course that's not what we're talking about...
But I remember one time I had a bad lamp socket that would short out if you put a regular light in it (tri-light socket) and flipped the switch a certain way. When this happened, the breaker immediately tripped and the 18 gauge lamp cord was very very warm. But it wasn't damaged because the breaker tripped in time, despite the fact that the wire was pretty damn warm.
If the same thing happens with a short of 12 ga on a 40 A feeding a motor, I don't personally see a problem with it.
I'm only defending this issue for motor loads, though. Otherwise I never think it would be okay.
Joey
I think I'm getting closer to understanding. The key terminology is perhaps "continuous load", and a dead short rapidly spikes an amperage that is much, much greater than 40 amps, tripping the breaker in a flash.
That sparks my memory (another silly pun intended) of a stunt I pulled when I was a kid trying to hot wire a car like they do in the movies. I was under the hood, near the battery and starter relay with a coat hanger wire. Wow, burned a groove in all 10 fingers and the palms of both hands before I could let go of the wire.
I'm pretty sure that's the idea behind it, yes. I know there are cases where breakers don't trip properly, such as the whole Federal Pacific/Federal Pioneer and Zinsco mess. However, I think in those cases even if the wire was properly sized it may be damaged during a short.
With that aside, assuming a working breaker for shorts and ground faults, the only issue left is overload protection. Assuming, once again, that some type of overload protection exists, the wires will never be put in a position where they draw excess current for very long. Motors usually do have their own form of protection, and would usually only draw extra current for a few seconds during startup.
Quote:
Thanks for your patience.
I wouldn't worry about that... we're all friends here and just trying to learn. I don't even know that i'm entirely correct either. I just go after what makes sense to me and see what other people say in response.