Checking out my own panel board while doing the electrical lesson. No bonding strap or screw. However is appears that the grounding bar(s) is directly attached to the box while the neutral bar(s) are insulated from the box therefore creating the needed bond with just a different approach?
Pictures would be helpful. ![]()
Is this a service panel or a distribution, aka subpanel?
It sounds like a distribution panel with this description:
Work boxes and panels are always grounded. The bond most often talked about in this forum (bonding is simply an electrical connection) is the one made in a service panel between the neutral and ground (only occurs in the service (main) panel). Your description indicates that the neutral is insulated from the ground (not bonded) as would occur in a sub-panel. The neutral buss will always be insulated from the panel enclosure. A suitable means will be provided to connect (bond) the two if that is needed (service panel). Typically this is simply a screw that starts in the neutral buss and protrudes through the insulation to connect the the enclosure.