This one has always been a nice debate…the NEC’s intent is this…
It has to be for one a “single” dwelling unit…and can’t be used lets say to size service conductors to a service for a multi-family dwelling…now it can for each individual dwelling but not in combination.
Now it is my opinion that lets say you supply to a multi-family dwelling with properly sized conductors via 310.16 as we discussed before that you can indeed go from the exterior disconnection means for that single unit to the “remote distribution panel” which is now a feeder and still be able to use 310.15(B)(6)…but only in respect to it being the " main power feeder "…simply going to a “subpanel” would not make it a "main power feeder "…
This area still needs work and we have some proposals coming for 2011 on this I have spoken to Mike Holt about it and he is on the same page and will submit them…
Generally it becomes an issue of is it a “Main Power Feeder” to the individual dwelling…going to barn, detached so on begs us to say it is not a dwelling and the allowance of this reduction says very clear…
(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. For individual dwelling units of one family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase service-entrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s).
Those words in RED have strong meaning…
just chiming in fellas…maybe I am wrong…thehehehe
Now I had to add…the 2008 change on this refers to the following:
"The reference to “lighting and appliance branch circuit panelboard” has been deleted to correlate with the changes in Article 408. Table 310.15(B)(6) has been rearranged to provide the ampacity values in the left column as a result of CMP-6 action on Proposal 6-66. The second sentence as revised NOW requires a main power feeder to supply all loads associated with the dwelling unit.
Basically…if you do size this using an example where you have an exterior disconnect and this making that the Main Disconnection means and then you feed it throught the house to a "remote distribution panel " or because of the nature of the bonding process a " subpanel " then 310.15(B)(6) would apply…but only loads associated with the dwelling itself can come out of the panel…WOW…that gets wordy…lol