How difficult is it to go back and install fireblocking?
I was able to look down fron the attic all the way to the basement where the furnace vent comes up. Doesn't appear to be any fireblocking the entire way.
![](upload://7VolHIYXJ9VUPIKbgBbwf4oAHQr.jpeg)
It's a townhouse. So is that an association problem? Or a buyer problem?
Originally Posted By: scieslewicz This post was automatically imported from our archived forum.
Jeffrey,
There should have been firestopping (the metal plate that is flush) placed at each story penetration. Also, there should be at least a one inch clearance to combustibles for the vent (so seeing the tape measure vent to framing is an issue.)
Chances are all the THs are the same way and it is a definite problem especially in a multi family dwelling. The fire burn time is severly compromised!!
Originally Posted By: dbroad This post was automatically imported from our archived forum.
Fire blocking is required at ceiling line. All gaps or air chaises are required to be sealed off from main living area so nothing can get into the atic. I know this for I am building a house now and the County inspector called the framer on it, for he didnt believe me. Know the framer knows this as well.