Floor joists set into concrete
Does the Alberta building code allow joists to be EMBEDDED in concrete that is in direct contact with the ground? The IRC distinguishes between contact < 8" and contact by being embedded.
Take your pick, there are many, and has been going on for a while. :neutral:
No, as I said, just be 8" above grade
Just for the sake of interest it is 6 inches in OBC 2006.
(3) Structural wood elements shall be pressure-treated with a preservative to resist decay,
(a) where the vertical clearance between structural wood elements and the finished
ground level is less than 150 mm, or
(b) where,
(i) the wood elements are not protected from exposure to precipitation, and
(ii) the configuration is conducive to moisture accumulation.
The problem is different areas have different weather and different codes.
Nobody here thinks porous concrete in direct contact with wood is a good thing I am sure.
Just take a look at Will Deckers sight showing rotted wood joists embedded in split block as an example.
Right from the provincial code…
Splitting hairs Joe.
Wood Resting on concrete. Like sill plates or ledger boards for decks.
Those are in the concrete.
Jeffrey is right.
Need to be treated or an opening of 1/2"
The lumber should be pressure treated and or separated by a Barrier.IE: Wrapped in Blue skin, Real Dry or .Waterproof Membrane. OR an air gap of 1/2 or 5/8 " I could be wrong on the gap or opening.Then its good to go.
Then there are the fasteners for treated wood [treated wood](ASTM B-695, Class 55, minimum.)so the do not degrade.ASTM B-695, Class 55, minimum.
Most is in the link.
[quote=“clawrenson, post:26, topic:71884”]
Alberta Building Code - reg 9.3.2.9 Termite and Decay Protection
  1. Structural wood elements shall be pressure treated with a preservative to resist decay where
    a) the structural wood elements are in contact with the ground, or
    b) the vertical clearance between structural wood elements and the ground is less than 150 mm - see also 9.23.2.2 and 9.23.2.3
Generally Alberta is considered free of termites* and rats HA HA HA
9.23.2.2 Protection from Decay (notes)
  1. Ends of wood joists, beams and other members framing into masonry or concrete shall be treated to prevent decay where the bottom of the member is at or below ground level, or a 12 mm air space shall be provided at the end and sides of the member.
Best practices - wood exposed to moisture for long periods - will eventually decay.
9.23.2.3 Protection from Dampness
  1. Except as permitted in sentence 2, wood framing members that are not pressure treated with a wood preservative and which are supported on concrete in contact with the ground or fill shall be separated from the concrete by not less than 0.05 mm polyethylene film, or Typs S roll roofing.
  2. Dampproofing material referred to in sentence 1 is not required where the wood member is at least 150 mkm above the ground. (approximately 6 inches)/QUOTE
    Jus a bit of jocularity.
That’s right - ignore - my post…because yours make much more sense!
You makes sense.
Claude in view of the amount of posts you make it is probably a good idea for you to check your grammar.
Hope this helps.
Just reading it now.Protection Against decay R3 19.1 LOCATION REQUIRED
2006 IRC.
PROTECTION AGAINST DECAY R3 19.1](http://www.conradlumberco.com/pdfs/TreatedWood2006IRC.pdf)Location Required.
Protection from decay shall be provided in the following locations by the use of naturally durable wood or
wood that is preservative-treated i n accordance with American Wood-Preservers’ Association (AWPA) U1 for
the species, product, preservative and end use. Preservatives shall be listed i n Section 4 of AWPA U1.
ICC
2304.11.4.1 Posts or columns. Posts and columns supporting permanent structures that are embedded in concrete that is in direct contact with the earth, embedded in concrete that is exposed to the weather or in direct contact with the earth shall be of preservative-treated wood.
2304.11.4.2 Wood structural members. Wood structural members that support moisture-permeable floors or roofs that are exposed to the weather, such as concrete or masonry slabs, shall be of naturally durable or preservative-treated wood unless separated from such floors or roofs by an impervious moisture barrier.
Robert Alberta has there own Building Code so this cannot be used.
Greg’s is the correct one to use.
I also tell my clients that it is OK to have it 6 inches from grade as a minimum but is it smart to do so.
Code in Alberta is probably the same as Ontario
9.23.2.2. Protection from Decay
(1) Ends of wood joists, beams and other members framing into masonry or concrete shall be treated to prevent decay
the member.
the wood will rot away, treated or not. concrete contains moisture. local codes may allow it but that doesnt make it a good idea.
Jerrod, it’s not OK.
Wood beams can rest in beam pockets formed into concrete foundation walls, but they need to have an air space around them so that if they get wet they can dry. Floor joists, pressure treated or not, should not be cast into a wall like that. Even with beams in pockets, the pockets don’t extend through the wall.
The proper way to build that would have been to:
  1. Bolt a ledger to the inside of the foundation wall and rest the joists in hangers nailed to the ledger so that the wall height doesn’t matter… or
  2. Build the foundation wall low enough so that the joists rest on a plate bolted to the top of the foundation so that the top of the bolted plate is bottom of joists, … 0r
  3. Use top-flange hangers that nail to a plate anchor-bolted to the top of the wall, so that the top of the top of the bolted plate is top of joist.
There are long-established methods for constructing a framed floor that butts the inside of a concrete foundation wall and what’s shown in that photo is not one of them. It’s simply bad practice.
Look in any framing book or Architectural Graphic Standards for proper methods.
There have been millions of homes built with wall bottom plates of pressure-treated hemlock (hem-fir) that are anchor-bolted to a concrete slab, so pressure-treated contact with concrete is OK, as long as there’s drying space.
Thanks for the great feed back. Ken, I like the discription you provided it was explained really well.
Thanks again everyone.
:):slight_smile:
I concure with kenton. An airspace is needed. Direct contact is not proper building practices.
The project will see as time evolves.
From the pictures, it appears that these are not floor joists extended through the foundation but is inset 1"x4" strapping to which a downward extension of the OSB sheathing will eventually be installed and then the weather resistive barrier and siding. The wood appears to be at least 15- 18" above the finished grade so soil moisture will not be a problem.
To all others, wood in contact with concrete is not a problem in and of itself. It **could **be a rot problem when untreated wood in the concrete or in contact with the concrete is within 6"(Canadian NBC) / 8" (CMHC) of a moisture source such as the soil.
It is obviously not floor joists HI.
It is not treated, or I should say it does not appear to be treated wood from where I sit.
I see 2" x…material. It is vertical installed to accept some form of sheathing or skirting. If it is not mechanically fastened and flashed properly I see issues before long.
So why do deck ledger have to be flashed, countered and lagged bolted into the wall. Live load right ?
1" by x … or 3/4 actually when dressed would be cupped by now.
2" by x… is 1.75 x…