I was taking the NACHI electrical inspection online course today and under the topic “GFCIs on 2 wire circuits” it states “There is a common misconception that GFCIs only work on grounded circuits. This is not entirely the case.” My question is when would a GFCI work on a 2 wire circuit?
The GFCI does not rrequire a ground to function as it is sensing the current in both the supply and return leg is within 5 mA of each other.
If not it opesns the circut.
So it’s ok to install a GFCI on a 2 wire circuit. Thanks Michael
If the AHJ will allow it
Yes but the outlets have to be labeled as not providing a safety ground.
St. Louis County still uses 2005 NEC and does not modify this rule in their own code. All St. Louis municipalities, likewise…but get a hold of the actual code for the City of St. Louis. They write their own electrical code and this may not be allowed in it.
…and receptacles for certain applilcations are required to have a ground, so getting around the three wire requirement with a GFCI has only limited opportunity.
Where I usually find this condition is at kitchen counter outlets and bathroom sink outlets.
GFCI works fine on a 2-wire circuit, it’s just your typical tester that won’t work. The tester needs a ground to be able to simulate a leak to cause it to trip. It will still trip if there is an actual current leak or if you use the device test button which does not require a ground to work. I believe that the on-board test button uses a resistor to simulate a leak.
Most all of the GFCI outlets I have ever purchased come with two sets of labels “GFCI Protected Outlet” for downstream outlets and “No Equipment Ground” for when they are used to provide a 3-prong outlet on an ungrounded system.
NEC allows use on ungrounded systems, but local codes may not.
Replacing Receptacles to Meet the NEC
The NEC requires receptacles installed on 15 and 20 ampere branch circuits to be of the grounding-type and it requires the grounding contacts of those receptacles to be effectively grounded to the branch circuit equipment grounding conductor [210-7]. However, the Code allows the installation of any of the following installations when replacing a 2-wire nongrounding-type receptacle where no ground exists in the outlet box [210-7(d)(3)], Figure 9/10:
(a) Replace the 2-wire receptacle with another 2-wire receptacle.
(b) Replace the 2-wire receptacle with a GFCI-type receptacle and marked the receptacle with the words “No Equipment Ground.”
© Replace the 2-wire receptacle with a grounding-type receptacle where protected by a GFCI protection device (circuit breaker or receptacle). Since the grounding terminals for the receptacles are not grounded, the receptacles must be marked with the words “GFCI Protected” and “No Equipment Ground.”
Author’s Comment: The equipment grounding conductor serves no purpose in the operation of a GFCI protection device, and therefore it has no effect on the function of the GFCI test-button.
Yep, lets not forget the structure of the NEC and other documents. Even the “Codeists” like myself need to remember…USBC, IBC,IRC…then NEC…the NEC is simply a standard to which is referenced so at the end of the day…your statewide building code comes first, then the international codes and then our little NEC.
While the NEC may allow something, the IRC, IBC or the USBC may not.
When there is a change in 5mA will the GFCi pop or will it pop the breaker?
The test button does not trip the breaker. This is due to no ground being in the system. Now I could really ghetto rig it and run a wire from the ground to the the plug and “make” it work. But I just wanted to know if the GFCi should pop or the breaker when it sees a difference in 5mA.
Using 2 screw drivers is the easiest and most convenient thing to do when that is all you have to see if what you did is correct. We wired the wires correctly to the plugs everything works great when they are plugged in. But we wanted to be sure what was supposed to pop when it gets overloaded or a change in 5mA
You should not be wiring anything sir…
The test button at a GFCI breaker, or GFCI receptacle, Will, and Should, trip either, when properly wired. Even on a 2-wire system with No ground. Apparently the receptacles are improperly wired, or faulty.
The button on the GFCI receptacle is not designed to trip the breaker, it “trips” the receptacle.
Breakers trip on overloads. GFIs trip from an imbalance of current on the hot and neutrals.
Stop sticking screwdrivers into receptacles to test them. This proves that Darwin was wrong.
The test button has nothing to do with tripping the breaker. It simply shunts the current to the grounding conductor. It has nothing to do with the presence or lack of a ground. In fact adding the ground like you propose still would not trip the breaker.
If you want to test the GFI protection push the TEST button. Stop putting people at risk by doing stupid things.
Yes, you are still an idiot and should not be performing any electrical work. Once again, THIS IS NOT A SELF HELP FORUM.
Wow. 14,000 views since 2009.