Inspection & Writing Assignment:
The barrier EIFS and stone veneer cladding on this house have not been installed in strict accordance with any manufacturer’s installation instructions, industry standards, or good building practices. While the system appears to be in fair condition when viewed from afar, a closer look reveals many significant flaws.
The system has been installed too close to, and in some instances below grade. The bottom edge of the foam insulation boards has not been backrapped or sealed to the foundation edge. The system has not been properly spaced and sealed at dissimilar materials such as window and door frames, glass block inserts, stone veneer, utility penetrations. It has been installed in direct contact with the roof surfaces, front porch, and patio.
Kickout flashing are either undersized or have not been installed where the roof terminates in the plane of the cladding No headers flashing were observed above windows, doors, and glass block inserts.
No horizontal band has been installed between the first and second strays. The top edge of other horizontal has not been canted to promoted drainage.
The system is obviously delaminating at the east exterior of the front porch and below the window at the north side of the patio.
Elevated moisture reading was observed using a moisture meter under most of the window locations and above horizontal bands, and where the system is in contact with or below grade.
Given the vast number of repair needed and the facts that barrier EIFS is known to be an inherently defective product which cannot be made to resist moisture penetrations, it is the inspector’s considered opinion that the EIFS and stone veneer claddings should be removed from this house and replaced with a more durable and proven cladding such as Portland Cement stucco, stone or brick veneer. Removal of the existing claddings will almost certainly require the removal of the existing sheathing. At that time all moisture damage to the underlying structure must be repaired. Any insulation that has been exposed to moisture must be replaced. Prior to replacing the insulation or sheathing, it is recommended that all framing be treated with a borate solution such as Boracare.
All work should be performed by a licensed, bonded, and insured general contractor with significant experience replacing exterior claddings and in strict accordance with the cladding manufacturer’s installation instructions.