Location of main versus sub panel & bonding of grounding & neutral conductors

You’re welcome. :sunglasses:

You are correct, with a 4-wire feeder there would be a separate bus for both the EGC’s and the neutrals and the neutral bus would be isolated from the enclosure (no green screw). A GEC would terminate on the EGC bus not the neutral bus.